H3C Fixed Port Campus Switches Configuration Examples-6W103
HomeSupportConfigure & DeployConfiguration ExamplesH3C Fixed Port Campus Switches Configuration Examples-6W103
Table of Contents
Related Documents
60-PTP Configuration Examples
60-PTP Configuration Examples 264.04 KB
Introduction· 1
Prerequisites· 1
Example: Configuring Layer 2 IEEE 1588v2 PTP·· 1
Network configuration· 1
Applicable hardware and software versions· 1
Procedures· 3
Configuring Device A· 3
Configuring Device B· 4
Configuring Device C· 4
Verifying the configuration· 5
Configuration files· 6
Example: Configuring Layer 3 IEEE 1588v2 PTP in multicast mode· 7
Network configuration· 7
Applicable hardware and software versions· 8
Procedures· 10
Configuring Device A· 10
Configuring Device B· 10
Configuring Device C· 11
Verifying the configuration· 11
Configuration files· 13
Example: Configuring Layer 3 IEEE 1588v2 PTP in unicast mode· 14
Network configuration· 14
Applicable hardware and software versions· 15
Procedures· 17
Configuring Device A· 17
Configuring Device B· 17
Configuring Device C· 18
Configuring the base station· 19
Verifying the configuration· 19
Configuration files· 21
Example: Configuring IEEE 802.1AS PTP·· 22
Network configuration· 22
Applicable hardware and software versions· 22
Procedures· 24
Configuring Device A· 24
Configuring Device B· 25
Configuring Device C· 25
Verifying the configuration· 26
Configuration files· 27
Example: Configuring SMPTE ST 2059-2 PTP in multicast mode· 28
Network configuration· 28
Applicable hardware and software versions· 29
Procedures· 31
Configuring Device A· 31
Configuring Device B· 31
Configuring Device C· 32
Verifying the configuration· 32
Configuration files· 34
Example: Configuring PTP (SMPTE ST 2059-2, IPv4 UDP transport, unicast transmission) 35
Applicable hardware and software versions· 36
Procedures· 37
Configuring Device A· 38
Configuring Device B· 38
Configuring Device C· 39
Configuring the base station· 39
Verifying the configuration· 40
Configuration files· 42
Introduction
This document provides PTP configuration examples.
This document is not restricted to specific software or hardware versions.
This document assumes that you have basic knowledge of PTP.
As shown in Figure 1, a PTP domain contains Device A, Device B, and Device C. Configure Layer 2 IEEE 1588v2 PTP as follows for time synchronization:
·     Specify the IEEE 1588v2 PTP profile for the devices.
·     Specify the OC clock node type for Device A and Device C, and E2ETC clock node type for Device B. These clock nodes elect a GM through BMC based on their respective default GM attributes.
·     Use the default Request-Response delay measurement mechanism for Device A and Device C.
Figure 1 Network diagram
Hardware
Software version
S6812 switch series
S6813 switch series
Release 66xx
S6550XE-HI switch series
Release 6008 and later
S6525XE-HI switch series
S5850 switch series
Not supported
S5570S-EI switch series
Not supported
S5560X-EI switch series
Not supported
S5560X-HI switch series
Release 66xx
S5500V2-EI switch series
Not supported
MS4520V2-30F switch
Not supported
MS4520V2-30C switch
MS4520V2-54C switch
Not supported
MS4520V2-28S switch
MS4520V2-24TP switch
Not supported
ES5500 switch series
Not supported
S6520X-HI switch series
S6520X-EI switch series
Release 66xx
S6520X-SI switch series
S6520-SI switch series
Release 66xx
S5000-EI switch series
Release 66xx
MS4600 switch series
Release 66xx
S5560S-EI switch series
S5560S-SI switch series
Not supported
S5500V3-24P-SI
S5500V3-48P-SI
Not supported
S5500V3-SI switch series (except the S5500V3-24P-SI and S5500V3-48P-SI)
Not supported
S5170-EI switch series
Not supported
S5130S-HI switch series
S5130S-EI switch series
S5130S-SI switch series
S5130S-LI switch series
Not supported
S5120V2-SI switch series
S5120V2-LI switch series
Not supported
S5120V3-EI switch series
Not supported
S5120V3-36F-SI
S5120V3-28P-HPWR-SI
S5120V3-54P-PWR-SI
Not supported
S5120V3-SI switch series (except the S5120V3-36F-SI, S5120V3-28P-HPWR-SI, and S5120V3-54P-PWR-SI)
Not supported
S5120V3-LI switch series
Not supported
S3600V3-EI switch series
Not supported
S3600V3-SI switch series
Not supported
S3100V3-EI switch series
S3100V3-SI switch series
Not supported
S5110V2 switch series
Not supported
S5110V2-SI switch series
Not supported
S5000V3-EI switch series
S5000V5-EI switch series
Not supported
S5000E-X switch series
S5000X-EI switch series
Not supported
E128C switch
E152C switch
E500C switch series
E500D switch series
Not supported
MS4320V2 switch series
MS4320V3 switch series
MS4300V2 switch series
MS4320 switch series
MS4200 switch series
Not supported
WS5850-WiNet switch series
Not supported
WS5820-WiNet switch series
WS5810-WiNet switch series
Not supported
WAS6000 switch series
Not supported
IE4300-12P-AC switch
IE4300-12P-PWR switch
IE4300-M switch series (except the IE4300-28P-M)
IE4320 switch series (except the IE4320-28P)
Not supported
IE4300-28P-M switch
IE4320-28P switch
Release 63xx
Procedures
# Specify the IEEE 1588v2 PTP profile.
[DeviceA] ptp profile 1588v2
# Specify the OC clock node type.
[DeviceA] ptp mode oc
# Enable PTP globally.
[DeviceA] ptp global enable
# Specify a PTP domain.
[DeviceA] ptp domain 0
# Specify PTP for obtaining the time.
[DeviceA] clock protocol ptp
# Enable PTP on GigabitEthernet 1/0/1.
[DeviceA-GigabitEthernet1/0/1] ptp enable
[DeviceB] ptp profile 1588v2
# Specify the E2ETC clock node type.
[DeviceB] ptp mode e2etc
[DeviceB] ptp domain 0
[DeviceB] ptp global enable
[DeviceB] clock protocol ptp
[DeviceB-GigabitEthernet1/0/1] ptp enable
# Enable PTP on GigabitEthernet 1/0/2.
[DeviceB-GigabitEthernet1/0/2] ptp enable
<DeviceC> system-view
[DeviceC] ptp profile 1588v2
[DeviceC] ptp mode oc
[DeviceC] ptp domain 0
[DeviceC] ptp global enable
[DeviceC] clock protocol ptp
[DeviceC-GigabitEthernet1/0/1] ptp enable
IMPORTANT
IMPORTANT:
·     The Lock status field in the output from the display ptp clock command is available only for the S6550XE-HI switch series and S6525XE-HI switch series.
·     The InstID field in the output from the display ptp interface brief command is available only for the S6550XE-HI switch series and S6525XE-HI switch series.
When the network topology is stable, perform the following tasks to verify the PTP configuration:
·     Use the display ptp clock command to display PTP clock information.
·     Use the display ptp interface brief command to display brief information about PTP interfaces.
# Display PTP clock information on Device A.
[DeviceA] display ptp clock
PTP global state    : Enabled
PTP profile         : IEEE 1588 Version 2
PTP mode            : OC
Slave only          : No
Lock status         : Unlocked
Clock ID            : 000FE2-FFFE-FF0000
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 1
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 65535
Offset from master : 0 (ns)
Mean path delay    : 0 (ns)
Steps removed      : 0
Local clock time   : Sun Jan 15 20:57:29 2019
# Display brief information about PTP interfaces on Device A.
[DeviceA] display ptp interface brief
Name       InstID    State         Delay mechanism  Clock step  Asymmetry correction
GE1/0/1    0         Master        E2E              Two         0
# Display PTP clock information on Device B.
[DeviceB] display ptp clock
PTP mode            : E2ETC
Slave only          : No
Clock ID            : 000FE2-FFFE-FF0001
Clock type          : Local
Clock domain        : 0
Number of PTP ports : 2
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master : N/A
Mean path delay    : N/A
Steps removed      : N/A
# Display brief information about PTP interfaces on Device B.
[DeviceB] display ptp interface brief
GE1/0/1  0         N/A           E2E              Two         0
GE1/0/2  0         N/A           E2E              Two         0
# Display PTP clock information on Device C.
[DeviceC] display ptp clock
PTP mode            : OC
Slave only          : No
Lock status         : Locked
Clock ID            : 000FE2-FFFE-FF0002
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master : 25
Mean path delay    : 323
Steps removed      : 2
# Display brief information about PTP interfaces on Device C.
[DeviceC] display ptp interface brief
GE1/0/1  0         Slave         E2E              Two         0
The command outputs show that Device A is elected as the GM and GigabitEthernet1/0/1 on Device A is the master port.
Configuration files
·     Device A and Device C:
 clock protocol ptp
 ptp profile 1588v2
 ptp mode oc
interface GigabitEthernet 1/0/1
 ptp enable
·     Device B:
 clock protocol ptp
 ptp profile 1588v2
 ptp mode e2etc
 ptp enable
interface GigabitEthernet 1/0/2
 ptp enable
As shown in Figure 2, a PTP domain contains Device A, Device B, and Device C. Configure Layer 3 IEEE 1588v2 PTP in multicast mode as follows for time synchronization:
·     Specify the OC clock node type for Device A and Device C, and the P2PTC clock node type for Device B. These clock nodes elect a GM through BMC based on their respective default GM attributes.
·     Configure the multicast PTP transport mode and UDP (IPv4) transport protocol for the devices.
·     Configure the peer delay measurement mechanism (p2p) for Device A and Device C.
Figure 2 Network diagram
Hardware
Software version
S6812 switch series
S6813 switch series
Release 66xx
S5850 switch series
Not supported
Not supported
Release 66xx
Not supported
Not supported
MS4520V2-30F switch
Not supported
MS4520V2-30C switch
MS4520V2-54C switch
Not supported
MS4520V2-28S switch
Not supported
Not supported
Release 66xx
Release 66xx
Release 66xx
Release 66xx
Not supported
S5500V3-24P-SI
S5500V3-48P-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
S5120V3-36F-SI
S5120V3-28P-HPWR-SI
S5120V3-54P-PWR-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
E128C switch
E152C switch
E500C switch series
E500D switch series
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
IE4300-28P-M switch
IE4320-28P switch
Release 63xx
Procedures
# Configure the source IP address for multicast PTP transport.
[DeviceA] ptp source 10.10.10.1
# On GigabitEthernet 1/0/1, specify the UDP (IPv4) transport protocol and the peer delay measurement mechanism (p2p) and enable PTP.
[DeviceA-GigabitEthernet1/0/1] ptp transport-protocol udp [DeviceA-GigabitEthernet1/0/1] ptp delay-mechanism p2p
# Specify the P2PTC clock node type.
[DeviceB] ptp mode p2ptc
[DeviceB] ptp source 10.10.10.2
# On GigabitEthernet 1/0/1, specify the UDP (IPv4) transport protocol and enable PTP.
DeviceB-GigabitEthernet1/0/1] ptp transport-protocol udp
# On GigabitEthernet 1/0/2, specify the UDP transport protocol and enable PTP.
[DeviceB-GigabitEthernet1/0/2] ptp transport-protocol udp
[DeviceC] ptp source 11.10.10.1
[DeviceC-GigabitEthernet1/0/1] ptp transport-protocol udp [DeviceC-GigabitEthernet1/0/1] ptp delay-mechanism p2p
IMPORTANT
IMPORTANT:
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
GE1/0/1    0         Master        P2P              Two         0
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : N/A
GE1/0/1  0         N/A           P2P              Two         0
GE1/0/2  0         N/A           P2P              Two         0
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
GE1/0/1  0         Slave         P2P              Two         0
Configuration files
·     Device A:
 clock protocol ptp
 ptp profile 1588v2
 ptp mode oc
 ptp enable
·     Device B:
 clock protocol ptp
 ptp profile 1588v2
 ptp mode p2ptc
 ptp enable
 ptp enable
·     Device C:
 clock protocol ptp
 ptp profile 1588v2
 ptp mode oc
 ptp enable
As shown in Figure 3, configure PTP (IEEE 1588 version 2, IPv4 UDP transport, unicast transmission) to enable Device A, Device B, Device C, and the base station to synchronize the time with the ToD clock source.
·     Specify the IEEE 1588 version 2 PTP profile and unicast IPv4 UDP transport of PTP messages for Device A, Device B, and Device C.
·     Assign Device A, Device B, Device C, and the base station to PTP domain 0. Specify the BC clock node type for Device A, Device B, and Device C.
·     Connect Device A to the ToD clock source and Device C to the base station.
·     Use the default Request_Response delay measurement mechanism on all clock nodes in the PTP domain.
Figure 3 Network diagram
Hardware
Software version
S6812 switch series
S6813 switch series
Release 66xx
S5850 switch series
Not supported
Not supported
Not supported
Release 66xx
Not supported
MS4520V2-30F
Not supported
MS4520V2-30C
MS4520V2-54C
Not supported
MS4520V2-28S
MS4520V2-24TP
Not supported
Not supported
Release 66xx
Release 66xx
Release 66xx
Release 66xx
Not supported
S5500V3-24P-SI
S5500V3-48P-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
S5120V3-36F-SI
S5120V3-28P-HPWR-SI
S5120V3-54P-PWR-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
E128C
E152C
E500C switch series
E500D switch series
Not supported
Not supported
Not supported
Not supported
Not supported
IE4300-12P-AC & IE4300-12P-PWR
Not supported
IE4300-28P-M
IE4320-28P
Not supported
Procedures
IMPORTANT
IMPORTANT:
The device does not provide ToD interfaces. It can be deployed as Device B or Device C but not Device A.
Before configuration, assign IP addresses to the interfaces, and make sure the devices can reach each other. (Details not shown.)
# Specify the IEEE 1588 version 2 PTP profile.
# Specify the BC clock node type.
[DeviceA] ptp mode bc
# Create a PTP domain.
# Configure the device to use ToD 0 to receive clock signals and set the receive delay correction to 1000 nanoseconds.
[DeviceA] ptp tod0 input delay 1000
# Set priority 1 to 0 for the ToD 0 clock.
[DeviceA] ptp priority clock-source tod0 priority1 0
# On GigabitEthernet 1/0/1, specify IPv4 UDP transport of PTP messages, configure the destination IP address for unicast PTP messages, and enable PTP.
[DeviceA-GigabitEthernet1/0/1] ptp unicast-destination 10.10.10.2
[DeviceB] ptp mode bc
[DeviceB-GigabitEthernet1/0/1] ptp transport-protocol udp
[DeviceB-GigabitEthernet1/0/1] ptp unicast-destination 10.10.10.1
# On GigabitEthernet 1/0/2, specify IPv4 UDP transport of PTP messages, configure the destination IP address for unicast PTP messages, and enable PTP.
[DeviceB-GigabitEthernet1/0/2] ptp unicast-destination 11.10.10.1
[DeviceC] ptp mode bc
[DeviceC-GigabitEthernet1/0/1] ptp unicast-destination 11.10.10.2
# On GigabitEthernet1/0/2, specify IPv4 UDP transport of PTP messages, configure the destination IP address for unicast PTP messages, and enable PTP.
[DeviceC-GigabitEthernet1/0/2] ptp transport-protocol udp
[DeviceC-GigabitEthernet1/0/2] ptp unicast-destination 12.10.10.1
[DeviceC-GigabitEthernet1/0/2] ptp enable
# Specify PTP domain 0.
# Specify IPv4 UDP transport of PTP messages.
# Set the destination IP address of unicast PTP messages to 12.10.10.2.
# Specify the Request_Response delay measurement mechanism.
For more information, see the configuration guide for the base station.
IMPORTANT
IMPORTANT:
When the network is stable, perform the following tasks:
·     Use the display ptp interface brief command to display brief PTP running information for all PTP interfaces.
PTP mode            : BC
Slave only          : No
Clock type          : ToD0
 ToD direction  : In
 ToD delay time : 1000 (ns)
Clock domain        : 0
Priority1     : 0
Priority2     : 128
Clock quality :
 Class                 : 6
 Accuracy              : 32
Steps removed      : 0
# Display brief PTP running information for all PTP interfaces on Device A.
PTP mode            : BC
Slave only          : No
Clock type          : ToD0
 ToD direction  : In
Clock domain        : 0
Priority1     : 0
Priority2     : 128
Clock quality :
 Class                 : 6
 Accuracy              : 32
Offset from master : 12 (ns)
Mean path delay    : 323 (ns)
Steps removed      : 1
# Display brief PTP running information for all PTP interfaces on Device B.
GE1/0/2  0         Master          E2E              Two         0
PTP mode            : BC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Offset from master  : 25 (ns)
Mean path delay     : 2791000 (ns)
Steps removed       : 2
# Display brief PTP running information for all PTP interfaces on Device C.
Configuration files
·     Device A
 clock protocol ptp
 ptp profile IEEE 1588 Version 2
 ptp mode bc
 ptp domain 0
 ptp global enable
 ptp enable
·     Device B
 clock protocol ptp
 ptp mode bc
 ptp domain 0
 ptp global enable
 ptp enable
 ptp enable
·     Device C
 clock protocol ptp
 ptp mode bc
 ptp domain 0
 ptp global enable
 ptp enable
 ptp enable
As shown in Figure 1, a PTP domain contains Device A, Device B, and Device C. Configure IEEE 802.1AS PTP as follows for time synchronization:
·     Specify the IEEE 802.1AS PTP profile for Device A, Device B, and Device C.
·     Specify the OC clock node type for Device A and Device C, and P2PTC clock node type for Device B. These clock nodes elect a GM through BMC based on their respective default GM attributes.
·     Use the default peer delay measurement mechanism on all clock nodes in the PTP domain.
Figure 4 Network diagram
Hardware
Software version
S6812 switch series
S6813 switch series
Not supported
S5850 switch series
Not supported
Not supported
Not supported
Not supported
Not supported
MS4520V2-30F switch
Not supported
MS4520V2-30C switch
MS4520V2-54C switch
Not supported
MS4520V2-28S switch
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
S5500V3-24P-SI
S5500V3-48P-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
S5120V3-36F-SI
S5120V3-28P-HPWR-SI
S5120V3-54P-PWR-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
E128C switch
E152C switch
E500C switch series
E500D switch series
Not supported
Not supported
Not supported
Not supported
Not supported
IE4300-12P-AC & IE4300-12P-PWR switches
Not supported
IE4300-28P-M switch
IE4320-28P switch
Not supported
Procedures
# Specify the IEEE 802.1AS PTP profile.
[DeviceA] ptp profile 8021as
# Enable PTP on Twenty-FiveGigE 1/0/1.
[DeviceA] interface twenty-fivegige 1/0/1
[DeviceA-Twenty-FiveGigE1/0/1] ptp enable
[DeviceA-Twenty-FiveGigE1/0/1] quit
[DeviceB] ptp profile 8021as
[DeviceB] interface twenty-fivegige 1/0/1
[DeviceB-Twenty-FiveGigE1/0/1] ptp enable
[DeviceB-Twenty-FiveGigE1/0/1] quit
# Enable PTP on Twenty-FiveGigE 1/0/2.
[DeviceB] interface twenty-fivegige 1/0/2
[DeviceB-Twenty-FiveGigE1/0/2] ptp enable
[DeviceB-Twenty-FiveGigE1/0/2] quit
[DeviceC] ptp profile 8021as
[DeviceC] interface twenty-fivegige 1/0/1
[DeviceC-Twenty-FiveGigE1/0/1] ptp enable
[DeviceC-Twenty-FiveGigE1/0/1] quit
IMPORTANT
IMPORTANT:
PTP profile         : IEEE 802.1AS
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 246
Priority2     : 248
Clock quality :
 Class                 : 248
 Accuracy              : 254
 Offset (log variance) : 16640
Steps removed      : 0
Local clock time   : Sun Jan 15 20:57:29 2011
WGE1/0/1  0        Master        P2P              Two         0
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 246
Priority2     : 248
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : N/A
WGE1/0/1   0          N/A           P2P              Two         0
WGE1/0/2   0          N/A           P2P              Two         0
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 2
WGE1/0/1   0         Slave         P2P              Two         0
The command outputs show that Device A is elected as the GM and Twenty-FiveGigE 1/0/1 on Device A is the master port.
Configuration files
 ptp profile 8021as
 ptp mode oc
 ptp domain 0
 ptp global enable
interface Twenty-FiveGigE 1/0/1
 ptp enable
·     Device B
 ptp profile 8021as
 ptp mode p2ptc
 ptp domain 0
 ptp global enable
 ptp enable
interface Twenty-FiveGigE 1/0/2
 ptp enable
As shown in Figure 3, Device A, Device B, and Device C are in a PTP domain. Configure SMPTE ST 2059-2 PTP in multicast mode as follows for time synchronization:
·     Specify the SMPTE ST 2059-2 PTP profile for the devices.
·     Configure the multicast PTP transport mode for the devices.
·     Specify the OC clock node type for Device A and Device C, and the P2PTC clock node type for Device B. All clock nodes elect a GM through BMC based on their respective default GM attributes.
Figure 5 Network diagram
Hardware
Software version
S6812 switch series
S6813 switch series
Release 66xx
S5850 switch series
Not supported
Not supported
Release 66xx
Not supported
Not supported
MS4520V2-30F switch
Not supported
MS4520V2-30C switch
MS4520V2-54C switch
Not supported
MS4520V2-28S switch
Not supported
Not supported
Release 66xx
Release 66xx
Release 66xx
Release 66xx
Not supported
S5500V3-24P-SI
S5500V3-48P-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
S5120V3-36F-SI
S5120V3-28P-HPWR-SI
S5120V3-54P-PWR-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
E128C switch
E152C switch
E500C switch series
E500D switch series
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
IE4300-28P-M switch
IE4320-28P switch
Release 63xx
Procedures
# Specify the SMPTE ST 2059-2 PTP profile.
[DeviceA] ptp profile st2059-2
# On GigabitEthernet 1/0/1, specify the peer delay measurement mechanism (p2p) and enable PTP.
[DeviceB] ptp profile st2059-2
[DeviceC] ptp profile st2059-2
IMPORTANT
IMPORTANT:
PTP profile         : SMPTE ST 2059-2
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 0
PTP mode            : P2PTC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : N/A
PTP mode            : OC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed      : 2
The output shows that Device A is elected as the GM and GigabitEthernet1/0/1 on Device A is the master port.
Configuration files
·     Device A:
 clock protocol ptp
 ptp mode oc
 ptp domain 0
 ptp global enable
 ptp enable
·     Device B:
 clock protocol ptp
 ptp mode p2ptc
 ptp domain 0
 ptp global enable
 ptp enable
 ptp enable
·     Device C:
 clock protocol ptp
 ptp mode oc
 ptp domain 0
 ptp global enable
 ptp enable
As shown in Figure 10, configure PTP (SMPTE ST 2059-2, IPv4 UDP transport, unicast transmission) to enable Device A, Device B, Device C, and the base station to synchronize time with the ToD clock source.
·     Specify the SMPTE ST 2059-2 PTP profile and unicast IPv4 UDP transport of PTP messages for Device A, Device B, and Device C.
Figure 6 Network diagram
Hardware
Software version
S6812 switch series
S6813 switch series
Release 66xx
S5850 switch series
Not supported
Not supported
Not supported
Release 66xx
Not supported
MS4520V2-30F
Not supported
MS4520V2-30C
MS4520V2-54C
Not supported
MS4520V2-28S
MS4520V2-24TP
Not supported
Not supported
Release 66xx
Release 66xx
Release 66xx
Release 66xx
Not supported
S5500V3-24P-SI
S5500V3-48P-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
S5120V3-36F-SI
S5120V3-28P-HPWR-SI
S5120V3-54P-PWR-SI
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
E128C
E152C
E500C switch series
E500D switch series
Not supported
Not supported
Not supported
Not supported
Not supported
Not supported
IE4300-28P-M
IE4320-28P
Not supported
Procedures
IMPORTANT
IMPORTANT:
The SMPTE ST 2059-2 PTP profile supports IPv4 UDP transport rather than IEEE 802.3/Ethernet transport of PTP messages. It supports both multicast and unicast transmission of PTP messages.
IMPORTANT
IMPORTANT:
# On GigabitEthernet 1/0/1, configure the destination IP address for unicast PTP messages and enable PTP. (The SMPTE ST 2059-2 PTP profile transports PTP messages over IPv4 UDP by default.)
# On GigabitEthernet 1/0/2, configure the destination IP address for unicast PTP messages and enable PTP. (The SMPTE ST 2059-2 PTP profile transports PTP messages over IPv4 UDP by default.)
# On GigabitEthernet1/0/2, configure the destination IP address for unicast PTP messages and enable PTP. (The SMPTE ST 2059-2 PTP profile transports PTP messages over IPv4 UDP by default.)
IMPORTANT
IMPORTANT:
When the network is stable, perform the following tasks to verify the PTP configuration:
·     Use the display ptp interface brief command to display brief PTP running information.
PTP mode            : BC
Slave only          : No
Clock type          : ToD0
 ToD direction  : In
Clock domain        : 0
Priority1     : 0
Priority2     : 128
Clock quality :
 Class                 : 6
 Accuracy              : 32
Steps removed      : 0
# Display brief PTP running information on Device A.
PTP mode            : BC
Slave only          : No
Clock type          : ToD0
 ToD direction  : In
Clock domain        : 0
Priority1     : 0
Priority2     : 128
Clock quality :
 Class                 : 6
 Accuracy              : 32
Steps removed      : 1
# Display brief PTP running information on Device B.
PTP mode            : BC
Slave only          : No
Clock type          : Local
Clock domain        : 0
Priority1     : 128
Priority2     : 128
Clock quality :
 Class                 : 248
 Accuracy              : 254
Steps removed       : 2
# Display brief PTP running information on Device C.
Configuration files
·     Device A
 clock protocol ptp
 ptp mode bc
 ptp domain 0
 ptp global enable
 ptp enable
·     Device B
 clock protocol ptp
 ptp mode bc
 ptp domain 0
 ptp global enable
 ptp enable
 ptp enable
·     Device C
 clock protocol ptp
 ptp mode bc
 ptp domain 0
 ptp global enable
 ptp enable
 ptp enable
