Example: Configuring multi-tier M-LAG+spine gateways+ECMP paths to the external network
As shown in Figure 1, configure the network as follows:
·     Set up an M-LAG system at the spine tier to offer gateway services.
·     Set up two M-LAG systems at the leaf tier to offer access services to the servers.
·     Attach each server to a leaf M-LAG system by using two links or a single link.
·     Attach each leaf device to the spine devices by using M-LAG interfaces.
·     Configure the router to provide access to the external network.
Figure 1 Network diagram
Device
IP address
Interface description and peer device and interface
Spine 1
HGE2/0/1
N/A
Peer-link interface
Spine 2: HGE2/0/1
HGE2/0/2
2.0.0.1/30
Keepalive interface
Spine 2: HGE2/0/2
HGE1/0/5
25.1.1.1/24
Router: HGE1/0/25
FGE3/0/1
N/A
Leaf 1: FGE1/0/50
FGE3/0/2
N/A
Leaf 2: FGE1/0/50
FGE3/0/3
N/A
Leaf 3: FGE1/0/50
FGE3/0/4
N/A
Leaf 4: FGE1/0/50
Vlan-interface21
21.1.1.1/24
Leaf 1 and Leaf 2
Service VLAN
Vlan-interface31
31.1.1.1/24
Leaf 3 and Leaf 4
Service VLAN
Vlan-interface2000
192.168.2.1/30
East-west failover VLAN
Spine 2
HGE2/0/1
N/A
Peer-link interface
Spine 1: HGE2/0/1
HGE2/0/2
2.0.0.2/30
Keepalive interface
Spine 1: HGE2/0/2
HGE2/0/3
23.1.1.1/24
Router: HGE1/0/26
FGE3/0/1
N/A
Leaf 1: FGE1/0/49
FGE3/0/2
N/A
Leaf 2: FGE1/0/49
FGE3/0/3
N/A
Leaf 3: FGE1/0/49
FGE3/0/4
N/A
Leaf 4: FGE1/0/49
Vlan-interface21
21.1.1.1/24
Leaf 1 and Leaf 2
Service VLAN
Vlan-interface31
31.1.1.1/24
Leaf 3 and Leaf 4
Service VLAN
Vlan-interface2000
192.168.2.2/30
Leaf 1
XGE1/0/1
N/A
Member port of an M-LAG system interface
Server A
FGE1/0/49
N/A
Spine 2: FGE3/0/1
FGE1/0/50
N/A
Spine 1: FGE3/0/1
FGE1/0/51
N/A
Peer-link interface
Leaf 2: FGE1/0/51
FGE1/0/52
1.0.0.1/30
Keepalive interface
Leaf 2: FGE1/0/52
FGE1/0/53
N/A
Single-homed link
Server C
Leaf 2
XGE1/0/1
N/A
Server A
FGE1/0/49
N/A
Spine 2: FGE3/0/2
FGE1/0/50
N/A
Spine 1: FGE3/0/2
FGE1/0/51
N/A
Peer-link interface
Leaf 1: FGE1/0/51
FGE1/0/52
1.0.0.2/30
Keepalive interface
Leaf 1: FGE1/0/52
Leaf 3
XGE1/0/1
N/A
Server B
FGE1/0/49
N/A
Spine 2: FGE3/0/3
FGE1/0/50
N/A
Spine 1: FGE3/0/3
FGE1/0/51
N/A
Peer-link interface
Leaf 4: FGE1/0/51
FGE1/0/52
1.0.0.5/30
Keepalive interface
Leaf 4: FGE1/0/52
Leaf 4
XGE1/0/1
N/A
Server B
FGE1/0/49
N/A
Spine 2: FGE3/0/4
FGE1/0/50
N/A
Spine 1: FGE3/0/4
FGE1/0/51
N/A
Peer-link interface
Leaf 3: FGE1/0/51
FGE1/0/52
1.0.0.6/30
Keepalive interface
Leaf 3: FGE1/0/52
Router
HGE1/0/25
25.1.1.2
Spine 1: HGE2/0/3
HGE1/0/26
23.1.1.2
Spine 2: HGE2/0/3
Applicable product matrix
IMPORTANT
IMPORTANT:
In addition to running an applicable software version, you must also install the most recent patch, if any.
Role
Device
Software version
Spine
S12500X-AF
R2825
S12500G-AF
R7625
Border or leaf
S6800, S6860
R6710
S6805, S6825, S6850, S9850, S9820-64H, S9820-8C
R6710
S6890
R2825
S6812, S6813
F6628P22 and higher
·     The member devices in an M-LAG system system must use the same M-LAG system MAC address. Different M-LAG systems must each have a unique M-LAG system MAC address on the network.
·     As a best practice, run a dynamic routing protocol between the spine devices and the external network. If you use static routing, traffic interruption might occur upon the reboot of a spine device. This issue typically occurs if the service module accommodating a peer-link interface, keepalive interface, or M-LAG interface requires longer time to reboot than other service modules. To resolve the traffic interruption issue, use one of the following methods:
¡     Select an interface operating at the same speed from each service module and assign the interfaces to the aggregation group of the peer-link interface. This method ensures that the peer-link interface recovers prior to other interfaces. If you select interfaces operating at different speeds, execute the link-aggregation ignore speed command on the peer-link interface. This method might result in traffic congestion or uneven traffic distribution on aggregate links as the number of selected ports might be insufficient.
¡     Create a monitor link group on the spine devices. Configure the router-facing interfaces as uplink interfaces for the monitor link group, and the member interfaces of leaf-facing M-LAG interfaces as downlink interfaces. This method ensures that the uplink interfaces come up prior to the downlink M-LAG interfaces. If you use this method, you must manually change the downlink interfaces in the monitor link group in response to deletion or addition of M-LAG groups and membership changes of M-LAG groups.
Configuring the leaf nodes
Procedure summary
·     Configuring M-LAG
·     Configuring the links towards the servers
·     Configuring the interfaces facing single-homed downstream devices
·     Configuring the links towards the spine tier
The configuration of Leaf 3 and Leaf 4 is similar to that of Leaf 1 and Leaf 2. This configuration example provides only configuration tasks for Leaf 1 and Leaf 2.
Configuring M-LAG
Leaf 1 (S6800)
Leaf 2 (S6800)
Configuration method
Remarks
interface FortyGigE1/0/52
Manual
Enter the interface view for the keepalive link.
N/A
port link-mode route
Manual
Configure the interface for keepalive detection to operate in route mode as a Layer 3 interface.
N/A
ip address 1.0.0.1 255.255.255.252
ip address 1.0.0.2 255.255.255.252
Manual
Assign an IP address to the keepalive interface.
N/A
Manual
Return to system view.
N/A
m-lag system-mac 00e0-fc00-5800
Manual
Set the MAC address of the M-LAG system.
You must assign the same M-LAG system MAC address to the member devices in an M-LAG system system.
m-lag system-number 1
m-lag system-number 2
Manual
Set the M-LAG system number.
You must assign different M-LAG system numbers to the member devices in an M-LAG system system.
m-lag system-priority 100
Manual
(Optional.) Set the M-LAG system priority.
You must set the same M-LAG system priority on the member devices in an M-LAG system system.
The default M-LAG system priority is 32768. The smaller the value, the higher the priority.
m-lag standalone enable
Manual
Enable M-LAG standalone mode.
N/A
m-lag keepalive ip destination 1.0.0.2 source 1.0.0.1
m-lag keepalive ip destination 1.0.0.1 source 1.0.0.2
Manual
Configure the destination and source IP addresses of keepalive packets.
Exclude the interfaces providing the source and destination IP addresses from the shutdown action by M-LAG MAD.
m-lag mad exclude interface FortyGigE1/0/52
Manual
Exclude the keepalive interface from the shutdown action by M-LAG MAD.
N/A
m-lag restore-delay 300
Manual
Set the data restoration interval.
This parameter ensures that forwarding entry synchronization finishes before interfaces are brought up.
interface Bridge-Aggregation1
Manual
Create a Layer 2 aggregate interface and enter its view.
N/A
port link-type trunk
Manual
Set the link type of the interface to trunk.
N/A
port trunk permit vlan all
Manual
Configure the trunk interface to permit all VLANs.
N/A
interface FortyGigE1/0/51
Manual
Enter interface view.
N/A
Manual
N/A
Manual
N/A
port link-aggregation group 1
Manual
Assign the interface to aggregation group 1.
N/A
Manual
Enter Layer 2 aggregate interface view.
N/A
link-aggregation mode dynamic
Manual
Configure the aggregate interface to operate in dynamic mode.
N/A
port m-lag peer-link 1
Manual
Specify the aggregate interface as a peer-link interface.
N/A
undo mac-address static source-check enable
Manual
Disable static source check.
Disable static source check on the peer-link interface and spine-facing uplink interfaces.
Leaf 1 (S6800)
Leaf 2 (S6800)
Remarks
VLAN 21
VLAN 21
Manual
Create VLAN 21.
N/A
Manual
Return to the previous view.
N/A
interface Bridge-Aggregation101
Manual
Create an aggregate interface and enter its view. This interface will be assigned to a server-facing M-LAG group.
N/A
Manual
N/A
port trunk permit vlan 21
Manual
Assign the trunk interface to VLAN 21.
N/A
Manual
N/A
port m-lag group 1
port m-lag group 1
Manual
Assign the aggregate interface to M-LAG group 1.
N/A
port lacp system-priority 101
port lacp system-priority 100
Manual
Set the LACP priority.
Set different LACP priorities for different M-LAG member devices, so that only member ports with a higher priority are selected upon brain split.
Manual
N/A
interface Ten-GigabitEthernet 1/0/1
Manual
Enter the view of an M-LAG aggregation member port.
N/A
Manual
N/A
Manual
N/A
port link-aggregation group 101
Manual
Assign the interface to aggregation group 101.
N/A
Manual
N/A
Leaf 1 (S6800)
Leaf 2 (S6800)
interface FortyGigE1/0/53
Manual
Manual
Manual
IMPORTANT
IMPORTANT:
To prevent a peer link down event from triggering the M-LAG MAD DOWN action on the secondary M-LAG device, attach a single-homed downstream device to the primary M-LAG device.
Leaf 1 (S6800)
Leaf 2 (S6800)
Remarks
interface Bridge-Aggregation102
Manual
Create an aggregate interface to be assigned to an M-LAG system group and enter aggregate interface view.
N/A
Manual
N/A
Manual
N/A
Manual
N/A
port m-lag group 2
port m-lag group 2
Manual
Assign the aggregate interface to M-LAG group 2.
N/A
Manual
Manual
N/A
interface FortyGigE1/0/49
Manual
N/A
Manual
N/A
Manual
N/A
port link-aggregation group 102
Manual
Assign the interface to aggregation group 102.
N/A
interface FortyGigE1/0/50
Manual
N/A
Manual
N/A
Manual
N/A
Manual
N/A
Manual
N/A
Configuring the spine nodes
Procedure summary
·     Configuring M-LAG
·     Configuring the links towards the leaf tier
·     Configuring the dual-active VLAN gateways
·     Configuring the interfaces connected to the external network
Configuring M-LAG
Spine 1
Spine 2
Remarks
interface HundredGigE2/0/2
Manual
N/A
Manual
N/A
ip address 2.0.0.1 255.255.255.252
ip address 2.0.0.2 255.255.255.252
Manual
Assign an IP address to the interface.
N/A
Manual
N/A
Manual
Set this parameter to 200 on a fixed-port device.
m-lag role priority 100
m-lag role priority 101
Manual
Set M-LAG role priority.
The M-LAG member devices negotiate their M-LAG roles based on the M-LAG role priority. The smaller the value, the higher the priority to be the primary M-LAG devices.
m-lag system-mac 542b-de0c-0300
Manual
Manual
Manual
Manual
N/A
m-lag keepalive ip destination 2.0.0.2 source 2.0.0.1
m-lag keepalive ip destination 2.0.0.1 source 2.0.0.2
Manual
Specify a VPN instance according to the network environment.
For the interfaces that will be shut down by M-LAG MAD, exclude them from the M-LAG MAD DOWN action as needed.
m-lag mad exclude interface HundredGigE2/0/2
Manual
N/A
interface Bridge-Aggregation 1
Manual
Create Bridge-Aggregation 1.
N/A
Manual
N/A
interface HundredGigE2/0/1
Manual
Enter the view of a member port of the peer-link interface.
N/A
Manual
N/A
Manual
N/A
Manual
Enter the view of Bridge-Aggregation 1.
N/A
Manual
N/A
Manual
N/A
Manual
N/A
Manual
N/A
port trunk pvid vlan 4094
Manual
Set the PVID to 4094 for the trunk interface.
N/A
Spine 1
Spine 2
Remarks
Vlan 21 31
Vlan 21 31
Manual
Create VLANs.
N/A
Manual
N/A
Manual
Enter the view of the M-LAG group member aggregate interface connected to Leaf 1 and Leaf 2.
N/A
Manual
N/A
Manual
N/A
Manual
N/A
Manual
port m-lag group 2
port m-lag group 2
Manual
N/A
interface FortyGigE 3/0/1
Manual
N/A
Manual
N/A
Manual
N/A
Manual
Assign the interface to aggregation group 1.02
N/A
interface FortyGigE 3/0/2
Manual
N/A
Manual
N/A
Manual
N/A
Manual
N/A
Manual
N/A
interface Bridge-Aggregation103
Manual
Enter the view of the M-LAG group member aggregate interface connected to Leaf 3 and Leaf 4.
N/A
Manual
N/A
port trunk permit vlan 31
Manual
Assign the trunk interface to VLAN 31.
N/A
Manual
N/A
Manual
port m-lag group 3
port m-lag group 3
Manual
N/A
interface FortyGigE 3/0/3
Manual
N/A
Manual
N/A
Manual
N/A
port link-aggregation group 103
Manual
Assign the interface to aggregation group 1.03
N/A
interface FortyGigE3/0/4
Manual
N/A
Manual
N/A
Manual
N/A
Manual
N/A
Manual
N/A
Spine 1
Spine 2
Remarks
routing-interface base-mac 3c8c-4003-8ba5
routing-interface base-mac 3c8c-4003-8b41
Manual
Configure the base MAC address.
The base MAC address of Spine 2 is equal to that of Spine 1 + 0X64.
This step only applies to S12500X-AF and S6890 switches.
interface Vlan-interface21
Manual
Create the VLAN interface of VLAN 21, the service VLAN on Leaf 1 and Leaf 2.
N/A
ip address 21.1.1.1 255.255.255.0
Manual
N/A
mac-address 3c8c-4003-8c08
Manual
Assign a MAC address to the interface.
N/A
Manual
N/A
m-lag mad exclude interface Vlan-interface21
Manual
Exclude the VLAN interface from the M-LAG MAD DOWN action.
N/A
interface Vlan-interface31
Manual
Create the VLAN interface of VLAN 31, the service VLAN on Leaf 3 and Leaf 4.
N/A
ip address 31.1.1.1 255.255.255.0
Manual
N/A
mac-address 3c8c-4003-8c09
Manual
N/A
Manual
N/A
m-lag mad exclude interface Vlan-interface31
Manual
N/A
IMPORTANT
IMPORTANT:
·     On the S12500X-AF and S6890 switches, make sure the base MAC address plus the number of reserved MAC addresses produces a MAC address that has the same higher 36 bits as the base MAC address.
·     You cannot edit or delete the base MAC address within 30 seconds after you configure it.
·     When you assign a MAC address to a Layer 3 interface after the base MAC address configuration, make sure the following requirements are met:
¡     The MAC address must have the same higher 36 bits as the base MAC address.
¡     The MAC address must be no lower than the base MAC address plus the number of reserved MAC addresses
Spine 1
Spine 2
ospf 1 router-id 2.1.1.1
ospf 1 router-id 2.1.1.2
Manual
Start an OSPF process.
import-route direct
import-route direct
Manual
Redistribute direct routes.
area 0.0.0.0
area 0.0.0.0
Manual
Create an OSPF area.
interface HundredGigE1/0/5
interface HundredGigE2/0/3
Manual
Enter the view of the router-facing interface.
Manual
ip address 25.1.1.1 255.255.255.0
ip address 23.1.1.1 255.255.255.0
Manual
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
Manual
Enable OSPF on the interface.
Manual
Vlan 2000
Vlan 2000
Manual
Create the east-west failover VLAN.
Manual
interface Vlan-interface2000
Manual
Create the VLAN interface of the east-west failover VLAN.
ip address 192.168.2.1 255.255.255.252
ip address 192.168.2.2 255.255.255.252
Manual
ospf 1 area 0.0.0.0
ospf 1 area 0.0.0.0
Manual
Enable OSPF on the VLAN interface.
Configuring the router
Router
ospf 1 router-id 3.1.1.1
Manual
area 0.0.0.0
Manual
interface HundredGigE1/0/25
Manual
Enter the view of the interface connected to Spine 1.
Manual
ip address 25.1.1.2 24
Manual
Assign an IP address to the interface connected to Spine 1.
ospf 1 area 0.0.0.0
Manual
Manual
N/A
interface HundredGigE1/0/26
Manual
Enter the view of the interface connected to Spine 2.
Manual
ip address 23.1.1.2 24
Manual
Assign an IP address to the interface connected to Spine 2.
ospf 1 area 0.0.0.0
Manual
Traffic forwarding models
The forwarding model matrix provides the following characteristics of traffic:
·     No.—Traffic number in the U-X-XXX format:
¡     U—Underlay traffic.
¡     X—Protocol number, which can be 4 (IPv4).
¡     XXX—Traffic sequence number, starting from 201.
·     Traffic type—Type of underlay traffic, which can be IPv4 known unicast.
·     Direction—Direction of underlay traffic, which can be south-north or east-west across leaf M-LAG systems.
·     Forwarding path—Nodes that underlay traffic traverses.
·     Traffic simulation—Traffic simulation method. Typically, a tester is used to simulate server traffic.
·     Load—Traffic size, which can be light (less than 1000 flows) and heavy (more than 1000 flows).
Table 1 Traffic forwarding models
No.
Traffic type
Direction
Forwarding path
Traffic simulation
Load
Remarks
U-4-201
IPv4 known unicast
East-west across leaf M-LAG systems
Server A > Leaf 1 & Leaf 2 > Spine 1 & Spine 2 > Leaf 3 & Leaf 4 > Server B
Bond4+ tester
Light
Layer 3 forwarding between PMs.
U-4-202
IPv4 known unicast
Server B > Leaf 1 & Leaf 2 > Spine 1 & Spine 2 > Leaf 1 & Leaf 2 > Server A
Bond4+ tester
Light
U-4-203
IPv4 known unicast
South-north
Server A > Leaf 1 & Leaf 2 > Spine 1 & Spine 2 > Router
Bond4+ tester
Light
Layer 3 forwarding between PMs and the external network.
U-4-204
IPv4 known unicast
South-north
Router > Spine 1 & Spine 2 > Leaf 1 & Leaf 2 > Server A
Bond4+ tester
Light
U-4-205
IPv4 known unicast
Server C > Leaf 1 > Spine 1 & Spine 2 > Leaf 3 & Leaf 4 > Server B
Bond4+ tester
Light
U-4-206
IPv4 known unicast
Server B > Leaf 3 & Leaf 4 > Spine 1 & Spine 2 > Leaf 1 > Server C
Bond4+ tester
Light
U-4-207
IPv4 known unicast
South-north
Server C > Leaf 1 > Spine 1 & Spine 2 > Router
Bond4+ tester
Light
U-4-208
IPv4 known unicast
South-north
Router > Spine 1 & Spine 2 > Leaf 1 > Server C
Bond4+ tester
Light
Testing network convergence upon single points of failure
Table 2 Network convergence upon single points of failure
Device
Failure type
Traffic interruption time
M-LAG system at the spine or leaf tier
Single point of failure on M-LAG member links
≤ 500 ms
Single point of failure restored on M-LAG member links
0 ms
Peer link failure
For M-LAG member links: ≤ 500 ms
For a link attached to a single-homed device:
·     If the M-LAG MAD DOWN action is not triggered on the attached M-LAG member device, east-west traffic resumes after the peer link recovers.
·     If the M-LAG MAD DOWN action has been triggered on the attached M-LAG member device, traffic resumes after the peer link and the single-homed link recover.
Peer link failure restored
0 ms
Keepalive link failure
0 ms
Keepalive link failure restored
0 ms
Keepalive link and peer link failure
≤ 5000 ms
Keepalive link and peer link restored
≤ 1000 ms
Upgrading the devices
≤ 500 ms (legacy method, in which two M-LAG member devices are separately upgraded)
Expanding the network
0 ms
Replacing hardware
Fixed-port device: ≤ 500 ms
Modular device:
·     Device replacement: ≤ 1000 ms.
·     Switching fabric module replacement: 0 ms.
·     Service module replacement: ≤ 500 ms.
Upgrading the leaf devices
Checking the environment
Execute the commands in "Verifying the configuration" and the following commands to verify that a device is available for an upgrade.
Leaf 1
Leaf 2
display device
display device
Displays device information.
display boot-loader
display boot-loader
Displays current software images and startup software images.
display version
display version
Displays system version information.
See H3C Switches M-LAG System Upgrade & Replacement & Expansion Guide.
Verifying the traffic interruption time during the upgrade
Verify that the traffic interruption time is shorter than 500 ms during a switchover and shorter than 150 ms during fallback when the traffic load is light. For more information, see "Testing network convergence upon single points of failure."
Verifying the upgrade result
Execute the commands in "Verifying the configuration" and the following commands to verify that the device is upgraded successfully.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Upgrading the spine nodes
Spine 1
Spine 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
An expansion operation adds two leaf devices.
Execute the commands in "Verifying the configuration" and the following commands to verify that a device is available for an expansion.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
1.     Disconnect the device from network management systems.
2.     Upgrade the software of the device as needed.
3.     Preconfigure the device.
4.     Connect the device to network management systems.
5.     Incorporate the device on the controller.
Verifying the expansion result
Execute the following commands to verify that the device is added successfully.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Replacing hardware
Replacing a service module
Execute the commands in "Verifying the configuration" and the following commands to verify that the target device is available for a replacement.
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Replacing hardware
Switch service and management traffic on the target service module to other service modules.
Power off the device and replace the service module, or replace the service module when the device is running. For more information, see the installation guides for the service module.
For details, see H3C Switches M-LAG System Upgrade & Replacement & Expansion Guide.
Verifying the replacement result
Execute the commands in "Checking the environment."
Replacing a switching fabric module
Leaf 1
Leaf 2
display device
display device
display boot-loader
display boot-loader
display version
display version
Replacing hardware
Power off the device and replace the switching fabric module, or replace the switching fabric module when the device is running. For more information, see the installation guides for the switching fabric module.
Commands used for verifying the configuration
Leaf 1
Leaf 2
display m-lag summary
Displays summary information about the peer-link interface and M-LAG interfaces.
display m-lag system
Displays the M-LAG system settings.
display m-lag keepalive
Displays M-LAG keepalive packet statistics.
display m-lag role
display m-lag role
Displays M-LAG role information.
display m-lag consistency { type1 | type2 }
Displays information about the configuration consistency check done by M-LAG.
display m-lag consistency-check status
Displays the configuration consistency check status.
display interface Bridge-Aggregation [ brief ]
Displays information about Layer 2 aggregate interfaces.
display stp brief
display stp brief
Displays brief spanning tree status and statistics.
Verifying the status of an M-LAG system system
Verify that M-LAG is working correctly on Spine 1 and Spine 2. Use Spine 1 as an example.
# Display summary information about the peer-link interface and M-LAG interfaces.
<Spine1>dis m-lag summary
Flags: A -- Aggregate interface down, B -- No peer M-LAG interface configured
       C -- Configuration consistency check failed
Peer-link interface: BAGG1
Peer-link interface state (cause): UP
Keepalive link state (cause): UP
                     M-LAG interface information
M-LAG IF    M-LAG group  Local state (cause)  Peer state  Remaining down time(s)
BAGG102     2              UP                       UP            -
BAGG103     3              UP                       UP            -
# Verify that the M-LAG system settings are correct.
<Spine1>dis m-lag system
                     System information
Local system number: 1                      Peer system number: 2
Local system MAC: 542b-de0c-0300            Peer system MAC: 542b-de0c-0300
Local system priority: 100                  Peer system priority: 100
Local bridge MAC: 5098-b8d3-7e00            Peer bridge MAC: 3c8c-4003-8b41
Local effective role: Primary               Peer effective role: Secondary
Health level: 0
Standalone mode on split: Enabled
In standalone mode: No
                     System timer information
Timer                      State       Value (s)    Remaining time (s)
Auto recovery              Disabled    -            -
Restore delay              Disabled    60           -
Consistency-check delay    Disabled    30           -
Standalone delay           Disabled    0            -
Role to None delay         Disabled    60           -
# Verify that the keepalive link is working correctly.
<Spine1>dis m-lag keepalive
Neighbor keepalive link status (cause): Up
Neighbor is alive for: 95299 s 891 ms
Keepalive packet transmission status:
  Sent: Successful
  Received: Successful
Last received keepalive packet information:
  Source IP address: 2.0.0.2
  Time: 2022/05/31 14:07:47
  Action: Accept
M-LAG keepalive parameters:
Destination IP address: 2.0.0.2
Source IP address: 2.0.0.1
Keepalive UDP port : 6400
Keepalive VPN name : N/A
Keepalive interval : 1000 ms
Keepalive timeout  : 5 sec
Keepalive hold time: 3 sec
# Verify that Spine 1 is the primary M-LAG device.
<Spine1> display m-lag role
                    Effective role information
Factors                  Local                    Peer
Effective role           Primary                  Secondary
Initial role             Primary                  Secondary
MAD DOWN state           No                       No
Health level             0                        0
Role priority            100                      101
Bridge MAC               5098-b8d3-7e00           3c8c-4003-8b41
Effective role trigger: Peer link calculation
Effective role reason: MAD status
                    Configured role information
Factors                  Local                    Peer
Configured role          Primary                  Secondary
# Verify that Spine 1 and Spine 2 have consistent configurations.
<Spine1>dis m-lag consistency-check status
                 Global Consistency Check Configuration
Local status     : Enabled           Peer status     : Enabled
Local check mode : Strict            Peer check mode : Strict
                 Consistency Check on Modules
Module           Type1           Type2
LAGG             Check           Not Check
VLAN             Check           Check
STP              Check           Not Check
                 Type1 Consistency Check Result
Global consistency check result: SUCCESS
Inconsistent global modules: -
M-LAG IF         M-LAG group ID     Check Result      Inconsistency modules
BAGG102          2                     SUCCESS            -
BAGG103          3                     SUCCESS            -