- H3C WX3000 Series Unified Switches Switching Engine Configuration Guide-6W103
- 01-CLI Configuration
- 02-Login Configuration
- 03-Configuration File Management Configuration
- 04-VLAN Configuration
- 05-Auto Detect Configuration
- 06-Voice VLAN Configuration
- 07-GVRP Configuration
- 08-Basic Port Configuration
- 09-Link Aggregation Configuration
- 10-Port Isolation Configuration
- 11-Port Security-Port Binding Configuration
- 12-DLDP Configuration
- 13-MAC Address Table Management Configuration
- 14-MSTP Configuration
- 15-802.1x and System Guard Configuration
- 16-AAA Configuration
- 17-MAC Address Authentication Configuration
- 18-IP Address and Performance Configuration
- 19-DHCP Configuration
- 20-ACL Configuration
- 21-QoS-QoS Profile Configuration
- 22-Mirroring Configuration
- 23-ARP Configuration
- 24-SNMP-RMON Configuration
- 25-Multicast Configuration
- 26-NTP Configuration
- 27-SSH Configuration
- 28-File System Management Configuration
- 29-FTP-SFTP-TFTP Configuration
- 30-Information Center Configuration
- 31-System Maintenance and Debugging Configuration
- 32-VLAN-VPN Configuration
- 33-HWPing Configuration
- 34-DNS Configuration
- 35-Smart Link-Monitor Link Configuration
- 36-PoE-PoE Profile Configuration
- 37-Routing Protocol Configuration
- 38-UDP Helper Configuration
- 39-Acronyms
- 40-Index
09-Link Aggregation Configuration | 101.32 KB |
Table of Contents
1 Link Aggregation Configuration
Introduction to Link Aggregation
Dynamic LACP Aggregation Group
Configuring a Manual Aggregation Group
Configuring a Static LACP Aggregation Group
Configuring a Dynamic LACP Aggregation Group
Displaying and Maintaining Link Aggregation
Link Aggregation Configuration Example
l The term switch used throughout this chapter refers to a switching device in a generic sense or the switching engine of a unified switch in the WX3000 series.
l The sample output information in this manual was created on the WX3024. The output information on your device may vary.
Overview
Link aggregation means aggregating several ports together to form an aggregation group, so as to implement outgoing/incoming load sharing among the member ports in the group and to enhance the connection reliability.
Depending on different aggregation modes, link aggregation falls into three types: manual, static LACP, and dynamic LACP aggregations. Depending on whether or not load sharing is implemented, aggregation groups can be load-sharing or non-load-sharing aggregation groups.
For the member ports in an aggregation group, their basic configuration must be the same. The basic configuration includes STP, QoS, VLAN, port attributes and other associated settings.
l STP configuration, including STP status (enabled or disabled), link attribute (point-to-point or not), STP priority, path cost, standard packet format, maximum packet transmission speed, loop prevention status, root protection status, edge port or not.
l QoS configuration, including traffic limit, priority remarking, default 802.1p priority, bandwidth assurance, congestion avoidance, traffic redirection, traffic statistics, and so on.
l VLAN configuration, including permitted VLANs, and default VLAN ID.
l Port attribute configuration, including port rate, duplex mode, and link type (trunk, hybrid, or access).
Introduction to LACP
The purpose of link aggregation control protocol (LACP) is to implement dynamic link aggregation and deaggregation. This protocol is based on IEEE802.3ad and uses LACPDUs (link aggregation control protocol data unit) to interact with its peer.
After LACP is enabled on a port, LACP notifies the following information of the port to its peer by sending LACPDUs: priority and MAC address of this system, priority, number and operation key of the port. Upon receiving the information, the peer compares the information with the information of other ports on the peer device to determine the ports that can be aggregated. In this way, the two parties can reach an agreement in adding/removing the port to/from a dynamic aggregation group.
Operation Key
An operation key of an aggregation port is a configuration combination generated by system depending on the configurations of the port (rate, duplex mode, other basic configuration, and management key) when the port is aggregated.
1) The selected ports in a manual/static aggregation group have the same operation key.
2) The management key of an LACP-enabled static aggregation port is equal to its aggregation group ID.
3) The management key of an LACP-enabled dynamic aggregation port is zero by default.
4) The member ports in a dynamic aggregation group must have the same operation key.
Introduction to manual aggregation group
A manual aggregation group is manually created. All its member ports are manually added and can be manually removed (it inhibits the system from automatically adding/removing ports to/from it). Each manual aggregation group must contain at least one port. When a manual aggregation group contains only one port, you cannot remove the port unless you remove the whole aggregation group.
LACP is disabled on the member ports of manual aggregation groups, and enabling LACP on such a port will not take effect.
Port status in manual aggregation group
The selected port with the smallest port number serves as the master port of the group, and other selected ports serve as member ports of the group.
There is a limit on the number of selected ports in an aggregation group. Therefore, if the number of the member ports serving as selected ports in an aggregation group exceeds the maximum number supported by the device, the system will choose the ports with lower port numbers as the selected ports, and set others as unselected ports.
In a manual aggregation group, the system sets the ports to selected or unselected state by the following rules:
l Among the ports in an aggregation group that are in up state, the system determines the mater port with one of the following settings being the highest (in descending order) as the master port: full duplex/high speed, full duplex/low speed, half duplex/high speed, half duplex/low speed. The ports with their rate, duplex mode and link type being the same as that of the master port are selected ports, and the rest are unselected ports.
l The system sets the ports unable to aggregate with the master port (due to some hardware limit) to unselected state.
Requirements on ports for manual aggregation
Generally, there is no limit on the rate and duplex mode of the ports (also including initially DOWN port) you want to add to a manual aggregation group. After aggregation, the smallest-numbered selected port is the master port of the aggregation group and the other selected ports are the member ports of the aggregation group.
For an aggregation group:
l When the rate or duplex mode of a port in the aggregation group changes, packet loss may occur on this port;
l When the rate of a port decreases, if the port belongs to a manual or static LACP aggregation group, the port will be switched to the unselected state; if the port belongs to a dynamic LACP aggregation group, deaggregation will occur on the port.
Introduction to static LACP aggregation
A static LACP aggregation group is also manually created. All its member ports are manually added and can be manually removed (it inhibits the system from automatically adding/removing ports to/from it). Each static aggregation group must contain at least one port. When a static aggregation group contains only one port, you cannot remove the port unless you remove the whole aggregation group.
LACP is enabled on the member ports of static aggregation groups. When you remove a static aggregation group, all the member ports in up state form one or multiple dynamic aggregations with LACP enabled. LACP cannot be disabled on static aggregation ports.
Port status of static aggregation group
A port in a static aggregation group can be in one of the two states: selected or unselected.
l Both the selected and the unselected ports can transceive LACP protocol packets.
l Only the selected ports can transceive service packets; the unselected ports cannot.
In a static aggregation group, the system sets the ports to selected or unselected state according to the following rules.
l The system determines the master port with one of the following settings being the highest (in descending order) as the master port: full duplex/high speed, full duplex/low speed, half duplex/high speed, half duplex/low speed. The ports with their rate, duplex mode and link type being the same as that of the master port are selected port.
l The ports connected to a peer device different from the one the master port is connected to or those connected to the same peer device as the master port but to a peer port that is not in the same aggregation group as the peer port of the master port are unselected ports.
l The ports unable to aggregate with the master port (due to some hardware limit) are unselected ports.
l The system sets the ports with basic port configuration different from that of the master port to unselected state.
There is a limit on the number of selected ports in an aggregation group. Therefore, if the number of the selected ports in an aggregation group exceeds the maximum number supported by the device, those with lower port numbers operate as the selected ports, and others as unselected ports.
Introduction to dynamic LACP aggregation group
A dynamic LACP aggregation group is automatically created and removed by the system. Users cannot add/remove ports to/from it. A port can participate in dynamic link aggregation only when it is LACP-enabled. Ports can be aggregated into a dynamic aggregation group only when they are connected to the same peer device and have the same basic configuration (such as rate and duplex mode).
Besides multiple-port aggregation groups, the system is also able to create single-port aggregation groups, each of which contains only one port. LACP is enabled on the member ports of dynamic aggregation groups.
Port status of dynamic aggregation group
A port in a dynamic aggregation group can be in one of the two states: selected or unselected. In a dynamic aggregation group, both the selected and the unselected ports can transceive LACP protocol packets; the selected ports can transceive user service packets, but the unselected ports cannot.
In an aggregation group, the selected port with the smallest port number serves as the master port of the group, and other selected ports serve as member ports of the group.
There is a limit on the number of selected ports in an aggregation group. Therefore, if the number of the member ports that can be set as selected ports in an aggregation group exceeds the maximum number supported by the device, the system will negotiate with its peer end, to determine the states of the member ports according to the port IDs of the preferred device (that is, the device with smaller system ID). The following is the negotiation procedure:
1) Compare device IDs (system priority + system MAC address) between the two parties. First compare the two system priorities, then the two system MAC addresses if the system priorities are equal. The device with smaller device ID will be considered as the preferred one.
2) Compare port IDs (port priority + port number) on the preferred device. The comparison between two port IDs is as follows: First compare the two port priorities, then the two port numbers if the two port priorities are equal; the port with the smallest port ID is the selected port and the left ports are unselected ports.
Configuring system priority
LACP determines the selected and unselected states of the dynamic aggregation group members according to the priority of the port ID on the end with the preferred device ID.
The device ID consists of two-byte system priority and six-byte system MAC address, that is, device ID = system priority + system MAC address.
When two device IDs are compared, the system priorities are compared first, and the system MAC addresses are compared when the system priorities are the same. The device with smaller device ID will be considered as the preferred one.
Changing the system priority of a device may change the preferred device between the two parties, and may further change the states (selected or unselected) of the member ports of dynamic aggregation groups.
Configuring port priority
LACP determines the selected and unselected states of the dynamic aggregation group members according to the port IDs on the device with the preferred device ID. When the number of members in an aggregation group exceeds the number of selected ports supported by the device in each group, LACP determines the selected and unselected states of the ports according to the port IDs. The ports with superior port IDs will be set to selected state and the ports with inferior port IDs will be set to unselected state.
The port ID consists of two-byte port priority and two-byte port number, that is, port ID = port priority + port number. When two port IDs are compared, the port priorities are compared first, and the port numbers are compared if the port priorities are the same.
Aggregation Group Categories
Depending on whether or not load sharing is implemented, aggregation groups can be load-sharing or non-load-sharing aggregation groups. When load sharing is implemented,
l For IP packets, the system will implement load-sharing based on source IP address and destination IP address;
l For non-IP packets, the system will implement load-sharing based on source MAC address and destination MAC address.
In general, the system only provides limited load-sharing aggregation resources, so the system needs to reasonably allocate the resources among different aggregation groups.
The system always allocates hardware aggregation resources to the aggregation groups with higher priorities. When load-sharing aggregation resources are used up by existing aggregation groups, newly-created aggregation groups will be non-load-sharing ones.
Load-sharing aggregation resources are allocated to aggregation groups in the following order:
l An aggregation group containing special ports (such as 10GE port) which require hardware aggregation resources has higher priority than any aggregation group containing no special port.
l A manual or static aggregation group has higher priority than a dynamic aggregation group (unless the latter contains special ports while the former does not).
l For aggregation groups, the one that might gain higher speed if resources were allocated to it has higher priority than others. If the groups can gain the same speed, the one with smallest master port number has higher priority than other groups.
When an aggregation group of higher priority appears, the aggregation groups of lower priorities release their hardware resources. For single-port aggregation groups, they can transceive packets normally without occupying aggregation resources
A load-sharing aggregation group contains at least two selected ports, but a non-load-sharing aggregation group can only have one selected port at most, while others are unselected ports.
l The commands of link aggregation cannot be configured with the commands of port loopback detection feature at the same time.
l The ports where the mac-address max-mac-count command is configured cannot be added to an aggregation group. Contrarily, the mac-address max-mac-count command cannot be configured on a port that has already been added to an aggregation group.
l MAC-authentication-enabled ports and 802.1x-enabled ports cannot be added to an aggregation group.
l Mirroring destination ports and mirroring reflector ports cannot be added to an aggregation group.
l Ports configured with blackhole MAC addresses, static MAC addresses or the static ARP protocol cannot be added to the aggregation group.
l Ports where the IP-MAC address binding is configured cannot be added to an aggregation group.
l Port-security-enabled ports cannot be added to an aggregation group.
l The port with Voice VLAN enabled cannot be added to an aggregation group.
l Do not add ports with IP filtering enabled to an aggregation group.
l Do not add ports with ARP intrusion detection enabled to an aggregation group.
l Do not add ports with source IP addresses/source MAC addresses statically bound to them to an aggregation group.
l A port belonging to a port group cannot be added to an aggregation group. Conversely, a port belonging to an aggregation group cannot be added to a port group.
For a manual aggregation group, a port can only be manually added/removed to/from the manual aggregation group.
Follow these steps to configure a manual aggregation group:
To do… |
Use the command… |
Remarks |
Enter system view |
system-view |
Create a manual aggregation group |
link-aggregation group agg-id mode manual |
Required |
Configure a description for the aggregation group |
link-aggregation group agg-id description agg-name |
Optional By default, an aggregation group has no description. |
Enter Ethernet port view |
Add the Ethernet port to the aggregation group |
port link-aggregation group agg-id |
Required |
Note that:
1) When creating an aggregation group:
l If the aggregation group you are creating already exists but contains no port, its type will change to the type you set.
l If the aggregation group you are creating already exists and contains ports, the possible type changes may be: changing from dynamic or static to manual, and changing from dynamic to static; and no other kinds of type change can occur.
l When you change a dynamic/static group to a manual group, the system will automatically disable LACP on the member ports. When you change a dynamic group to a static group, the system will remain the member ports LACP-enabled.
2) When a manual or static aggregation group contains only one port, you cannot remove the port unless you remove the whole aggregation group.
You can create a static LACP aggregation group, or remove an existing static aggregation group (after that, the system will re-aggregate the original member ports in the group to form one or more dynamic aggregation groups.).
For a static aggregation group, a port can only be manually added/removed to/from the static aggregation group.
When you add an LACP-enabled port to a manual aggregation group, the system will automatically disable LACP on the port. Similarly, when you add an LACP-disabled port to a static aggregation group, the system will automatically enable LACP on the port.
Follow these steps to configure a static LACP aggregation group:
To do… |
Use the command… |
Remarks |
Enter system view |
system-view |
Create a static aggregation group |
link-aggregation group agg-id mode static |
Required |
Add the port to the aggregation group |
Required |
For a static LACP aggregation group or a manual aggregation group, you are recommended not to cross cables between the two devices at the two ends of the aggregation group. For example, suppose port 1 of the local device is connected to port 2 of the peer device. To avoid cross-connecting cables, do not connect port 2 of the local device to port 1 of the peer device. Otherwise, packets may be lost.
A dynamic LACP aggregation group is automatically created by the system based on LACP-enabled ports. The adding and removing of ports to/from a dynamic aggregation group are automatically accomplished by LACP.
You need to enable LACP on the ports which you want to participate in dynamic aggregation of the system, because, only when LACP is enabled on those ports at both ends, can the two parties reach agreement in adding/removing ports to/from dynamic aggregation groups.
You cannot enable LACP on a port which is already in a manual aggregation group.
Follow these steps to configure a dynamic LACP aggregation group:
To do… |
Use the command… |
Remarks |
Enter system view |
system-view |
Configure a description for an aggregation group |
Configure the system priority |
lacp system-priority system-priority |
Optional By default, the system priority is 32,768. |
Enable LACP on the port |
lacp enable |
Required By default, LACP is disabled on a port. |
Configure the port priority |
lacp port-priority port-priority |
Optional By default, the port priority is 32,768. |
Use the command… |
Remarks |
Display summary information of all aggregation groups |
display link-aggregation summary |
You can execute the display command in any view. |
Display detailed information of a specific aggregation group or all aggregation groups |
display link-aggregation verbose [ agg-id ] |
Display link aggregation details of a specified port or port range |
display link-aggregation interface interface-type interface-number [ to interface-type interface-number ] |
Display local device ID |
display lacp system-id |
Clear LACP statistics about a specified port or port range |
reset lacp statistics [ interface interface-type interface-number [ to interface-type interface-number ] ] |
Execute the reset command in user view. |
Network requirements
As shown in Figure 1-1:
l Switch A connects to Switch B with three ports GigabitEthernet 1/0/1 to GigabitEthernet 1/0/3. It is required that incoming/outgoing load between the two switches can be shared among the three ports.
l Adopt three different aggregation modes to implement link aggregation on the three ports between switch A and B.
Figure 1-1 Network diagram for link aggregation configuration
Configuration procedure
1) Adopting manual aggregation mode
# Create manual aggregation group 1.
<device> system-view
[device] link-aggregation group 1 mode manual
# Add GigabitEthernet 1/0/1 through GigabitEthernet 1/0/3 to aggregation group 1.
[device] interface GigabitEthernet1/0/1
[device-GigabitEthernet1/0/1] port link-aggregation group 1
[device-GigabitEthernet1/0/1] interface GigabitEthernet1/0/2
[device-GigabitEthernet1/0/2] port link-aggregation group 1
[device-GigabitEthernet1/0/2] interface GigabitEthernet1/0/3
[device-GigabitEthernet1/0/3] port link-aggregation group 1
2) Adopting static LACP aggregation mode
# Create static aggregation group 1.
[device] link-aggregation group 1 mode static
3) Adopting dynamic LACP aggregation mode
# Enable LACP on GigabitEthernet 1/0/1 through GigabitEthernet 1/0/3.
[device-GigabitEthernet1/0/1] lacp enable
[device-GigabitEthernet1/0/2] lacp enable
[device-GigabitEthernet1/0/3] lacp enable
Note that, the three LACP-enabled ports can be aggregated into a dynamic aggregation group to implement load sharing only when they have the same basic configuration (such as rate and duplex mode and so on).