01-Installation Guide | 4.81 MB |
Examining the installation site
Installing the switch in a 19-inch rack
Rack-mounting the switch by using front mounting brackets
Rack-mounting the switch by using front and rear mounting brackets
Mounting the switch on a workbench
Grounding the switch with a grounding strip
Grounding the switch with a grounding conductor buried in the earth ground
Installing and removing a fan tray
Installing and removing a power supply
Installing and removing a PSR75-12A, PSR150-A1, or PSR150-D1
Installing and removing a PSR360-56A, PSR560-56D, PSR720-56A, or PSR1110-56A
Connecting the power cord for a built-in AC power supply
Connecting the power cord for a PSR75-12A/PSR150-A1 power supply
Connecting the power cord for a PSR150-D1/PSR560-56D power supply
Connecting the power cord for a PSR360-56A/PSR720-56A/PSR1110-56A power supply
Installing and removing an expansion module
Installing an expansion module
3 Accessing the switch for the first time
Connecting the switch to a configuration terminal
Connecting a DB9-to-RJ45 console cable
Connecting a USB-to-RJ45 console cable
Connecting a micro USB console cable
Planning IRF fabric size and the installation site
Identifying the master switch and planning IRF member IDs
Planning IRF topology and connections
Identifying physical IRF ports on the member switches
Configuring basic IRF settings
Connecting the physical IRF ports
Verifying the IRF fabric setup
5 Maintenance and troubleshooting
Removable power supply failure
1 Preparing for installation
H3C S6520X-SI switch series includes the following models:
· S6520X-16ST-SI
· S6520X-24ST-SI
· S6520X-10XT-SI
· S6520X-16XT-SI
· S6520X-18C-SI
· S6520X-26C-SI
· S6520X-26MC-SI
· S6520X-26MC-UPWR-SI
· S6520X-26XC-UPWR-SI
· S6520X-54XC-UPWR-SI
Safety recommendations
To avoid any equipment damage or bodily injury caused by improper use, read the following safety recommendations before installation. Note that the recommendations do not cover every possible hazardous condition.
· Before cleaning the switch, remove all power cords from the switch. Do not clean the switch with wet cloth or liquid.
· Do not place the switch near water or in a damp environment. Prevent water or moisture from entering the switch chassis.
· Do not place the switch on an unstable case or desk. The switch might be severely damaged in case of a fall.
· Ensure good ventilation of the equipment room and keep the air inlet and outlet vents of the switch free of obstruction.
· Connect the yellow-green protection grounding cable before powering on the switch.
· Make sure the power input voltage is as required by the power supply.
· To avoid electrical shocks, do not open the chassis while the switch is operating or when the switch is just powered off.
· During switch installation, wear an ESD wrist strap. Make sure the strap makes good skin contact and is reliably grounded.
The switch must be used indoors. You can mount your switch in a rack or on a workbench. Make sure the following requirements are met:
· Adequate clearance is reserved at the air inlet and outlet vents for ventilation.
· The rack or workbench has a good ventilation system.
· Identify the hot aisle and cold aisle at the installation site, and make sure ambient air flows into the switch from the cold aisle and exhausts to the hot aisle.
· Identify the airflow designs of neighboring devices, and prevent hot air flowing out of the neighboring device from entering the device.
· The rack is sturdy enough to support the switch and its accessories.
· The rack or workbench is reliably grounded.
To ensure correct operation and long service life of your switch, install it in an environment that meets the requirements described in the following subsections.
Temperature/humidity
Maintain temperature and humidity in the equipment room at acceptable ranges.
· Lasting high relative humidity can cause poor insulation, electricity leakage, mechanical property change of materials, and metal corrosion.
· Lasting low relative humidity can cause washer contraction and ESD and cause problems including loose mounting screws and circuit failure.
· High temperature can accelerate the aging of insulation materials and significantly lower the reliability and lifespan of the switch.
For the temperature and humidity requirements of different switch models, see technical specifications in Hardware Information and Specifications.
Cleanliness
Dust buildup on the chassis might cause electrostatic adsorption and dust corrosion, resulting in poor contact of metal connectors and contact points. This might shorten the device's lifetime and even cause device failure in the worst case. Table1-1 describes the dust concentration limits in the equipment room.
Table1-1 Dust concentration limits in the equipment room
Substance |
Particle diameter |
Concentration limit |
Dust particles |
≥ 0.5 µm |
≤ 3.5 × 106 particles/m3 |
Dust particles |
≥ 5 µm |
≤ 3 × 104 particles/m3 |
Dust (suspension) |
≤ 75 µm |
≤ 0.2 mg/m3 |
Dust (sedimentation) |
75 µm to 150 µm |
≤ 1.5 mg/(m2h) |
To maintain cleanliness in the equipment room, follow these guidelines:
· Keep the equipment room away from pollution sources. Do not smoke, eat, or drink in the equipment room.
· Use double-layer glass in windows and seal doors and windows with dust-proof rubber strips. Use screen doors and window screens for doors and windows open to the outside and make sure the external windows are air tight.
· Use dustproof materials for floors, walls, and ceilings and use wallpaper or matt paint that does not produce powders.
· Clean the equipment room regularly and clean the air filters of the rack each month.
· Wear ESD clothing and shoe covers before entering the equipment room, keep the ESD clothing and shoe covers clean, and change them frequently.
Corrosive gas limit
Corrosive gases can accelerate corrosion and aging of metal components. Make sure the corrosive gases in the equipment room do not exceed the concentration limits as shown in Table1-2.
Table1-2 Corrosive gas concentration limits in the equipment room
Gas |
Average concentration (mg/m3) |
Maximum concentration (mg/m3) |
SO2 |
0.3 |
1.0 |
H2S |
0.1 |
0.5 |
Cl2 |
0.1 |
0.3 |
HCI |
0.1 |
0.5 |
HF |
0.01 |
0.03 |
NH3 |
1.0 |
3.0 |
O3 |
0.05 |
0.1 |
NOX |
0.5 |
1.0 |
CAUTION: As a best practice, control the corrosive gas concentrations in the equipment room at their average values. Make sure the corrosive gas concentrations do not exceed 30 minutes per day at their maximum values. |
To control corrosive gases, use the following guidelines:
· As a best practice, do not build the equipment room in a place with a high concentration of corrosive gases.
· Make sure the equipment room is not connected to sewer, vertical shaft, or septic tank pipelines and keep it far away from these pipelines. The air inlet of the equipment room must be away from such pollution sources.
· Use environmentally friendly materials to decorate the equipment room. Avoid using organic materials that contains harmful gases, such as sulfur or chlorine-containing insulation cottons, rubber mats, sound-proof cottons, and avoid using plasterboards with high sulfur concentration.
· Place fuel (diesel or gasoline) engines separately. Do not place them in the same equipment room with the device. Make sure the exhausted air of the engines will not flow into the equipment room or towards the air inlet of the air conditioners.
· Place batteries separately. Do not place them in the same room with the device.
· Employ a professional company to monitor and control corrosive gases in the equipment room regularly.
EMI
All electromagnetic interference (EMI) sources, from outside or inside of the switch and application system, adversely affect the switch in the following ways:
· A conduction pattern of capacitance coupling.
· Inductance coupling.
· Electromagnetic wave radiation.
· Common impedance (including the grounding system) coupling.
To prevent EMI, use the following guidelines:
· If AC power is used, use a single-phase three-wire power receptacle with protection earth (PE) to filter interference from the power grid.
· Keep the switch far away from radio transmitting stations, radar stations, and high-frequency devices.
· Use electromagnetic shielding, for example, shielded interface cables, when necessary.
· To prevent signal ports from getting damaged by overvoltage or overcurrent caused by lightning strikes, route interface cables only indoors.
Laser safety
WARNING! The switch is a class 1 laser device. Disconnected optical fibers or transceiver modules might emit invisible laser light. Do not stare into beams or view directly with optical instruments when the switch is operating. |
Installation tools
No installation tools are provided with the switch. Prepare the following tools yourself as required:
· ESD wrist strap
· Flat-blade screwdriver
· Phillips screwdriver
· Needle-nose pliers
· Diagonal pliers
· Marker
2 Installing the switch
CAUTION: Keep the tamper-proof seal on a mounting screw on the chassis cover intact, and if you want to open the chassis, contact H3C for permission. Otherwise, H3C shall not be liable for any consequence. |
Figure2-1 Hardware installation flow
Installation method
Table2-2 Installation method
Switch model |
Installation method |
S6520X-16ST-SI S6520X-24ST-SI S6520X-10XT-SI S6520X-16XT-SI S6520X-18C-SI S6520X-26C-SI S6520X-26MC-SI |
Using front mounting brackets |
Attach the front mounting brackets to the sides of the chassis, on a position near the port side or power supply side as needed. |
S6520X-26MC-UPWR-SI S6520X-26XC-UPWR-SI S6520X-54XC-UPWR-SI |
Using front and rear mounting brackets |
· Attach the front mounting brackets to the sides of the chassis, on a position near the port side or power supply side as needed. · Install the rear mounting brackets based on the rack depth. ¡ If the rack depth is in the range of 429 to 595 mm (15.89 to 23.43 in), orient the brackets with the wide flange inside the rack. ¡ If the rack depth is in the range of 274 to 440 mm (10.79 to 17.32 in) and the distance from the rear rack posts to the inner surface of the cabinet door is larger than 153 mm (6.02 in), orient the brackets with the wide flange outside the rack. · If you are to install the PSR1110-56A power supplies for the switch, make sure the rack depth is greater than 600 mm (23.62 in). |
Figure2-2 Procedure for rack-mounting the switch by using the front mounting brackets
Figure2-3 Procedure for rack-mounting the switch by using the front and rear mounting brackets
NOTE: If a rack shelf is available, you can put the switch on the rack shelf, slide the switch to an appropriate location, and attach the switch to the rack by using the mounting brackets. |
Mounting brackets
Table2-3 Mounting brackets available for the switch
Switch model |
Front mounting brackets (Figure2-4) |
Rear mounting bracket and shoulder screw (Figure2-5) |
Provided |
N/A |
Provided |
Provided |
Figure2-4 Front mounting bracket
(1) Screw hole for attaching the bracket to the switch |
(2) Screw hole for attaching the bracket to the rack |
(3) M4 screw |
Figure2-5 Rear mounting bracket and shoulder screw
(1) Screw hole for attaching the bracket to the rack |
(2) Shoulder screw |
The S6520X-16ST-SI, S6520X-24ST-SI, S6520X-10XT-SI, S6520X-16XT-SI, S6520X-18C-SI, S6520X-26C-SI, and S6520X-26MC-SI switches support rack mounting by using front mounting brackets. The following procedure rack-mounts an S6520X-26C-SI switch.
Attaching the front mounting brackets to the switch
1. Select an installation position for the mounting brackets as required: near the power supply side or port side.
2. Attach the front mounting brackets to the chassis:
a. Align the round holes in the wide flange of one front mounting bracket with the screw holes in the chassis. See Figure2-6 and Figure2-7.
b. Use M4 screws (provided with the switch) to attach the front mounting bracket to the chassis.
c. Repeat the preceding two steps to attach the other front mounting bracket to the chassis.
Figure2-6 Attaching the front mounting bracket to the installation position near the port side
Figure2-7 Attaching the front mounting bracket to the installation position near the power supply side
Mounting the chassis in the rack
1. Wear an ESD wrist strap. Make sure the strap makes good skin contact and is reliably grounded.
2. Install cage nuts (user-supplied) in the mounting holes in the rack posts. Make sure the corresponding cage nuts on the left and right front rack posts are at the same height.
3. One person holds the switch chassis and aligns the installation holes on the mounting brackets with the cage nuts on the rack posts.
4. The other person uses M6 screws (user supplied) to attach the mounting brackets to the rack.
Figure2-8 Mounting the switch in the rack (front mounting brackets near the port side)
Figure2-9 Mounting the switch in the rack (front mounting brackets near the power supply side)
The S6520X-26MC-UPWR-SI, S6520X-26XC-UPWR-SI, and S6520X-54XC-UPWR-SI switches support rack mounting by using front and rear mounting brackets. The following procedure rack-mounts an S6520X-26MC-UPWR-SI switch.
Attaching the front mounting brackets and shoulder screws to the switch
The switch provides two installation positions on its side for the front mounting brackets. One is near the power supply side and the other is near the port side. The following procedure attaches the front mounting brackets to the installation position near the port side. The power supply side mounting is similar.
To attach the front mounting brackets and shoulder screws to the switch:
1. Align the round holes in the wide flange of one front mounting bracket with the screw holes in the chassis. See Figure2-10.
2. Use M4 screws (supplied with the switch) to attach the front mounting bracket to the chassis.
3. Repeat the preceding two steps to attach the other front mounting bracket to the chassis.
4. Unpack the shoulder screws and attach them to the chassis.
Two installation positions as red-marked in Figure2-10 are available for shoulder screws. Select one as required.
Figure2-10 Attaching the front mounting brackets and shoulder screws to the chassis
Attaching the rear mounting brackets to the rack
1. Determine the switch installation position in the rack.
2. Install cage nuts in the rear rack posts. Make sure the corresponding cage nuts on the left and right front rack posts are at the same height.
3. Orient the rear mounting brackets with the wide flange inside or outside the rack as required.
4. Use M6 screws to attach the rear mounting brackets to the rear posts, as shown in Figure2-11.
Do not fully tighten the M6 screws before mounting the switch in the rack.
Figure2-11 Attaching the rear mounting brackets to the rack with the wide flange inside the rack
Figure2-12 Attaching the rear mounting brackets to the rack with the wide flange outside the rack
2. Make sure the front mounting brackets and shoulder screws are securely attached to the two sides of the switch.
3. Attach cage nuts (user supplied) to the front rack posts. Make sure the corresponding cage nuts on the left and right rear rack posts are at the same height.
4. One person supports the chassis bottom with one hand, holds the front part of the chassis with the other, and pushes the chassis into the rack gently. Make sure the shoulder screws rest firmly on the upper edge of the rear mounting brackets. See Figure2-13 and Figure2-14.
5. The other person attaches the front mounting brackets with M6 screws (user-supplied) to the front rack posts. Make sure the switch is installed securely in the rack. See Figure2-13 and Figure2-14.
Figure2-13 Mounting the switch in the rack (with the wide flange of the rear mounting brackets inside the rack)
IMPORTANT: · Reserve a minimum clearance of 10 cm (3.9 in) around the chassis for heat dissipation. · Do not place heavy objects on the switch. |
To mount the switch on a workbench:
1. Verify that the workbench is sturdy and reliably grounded.
2. Place the switch with bottom up, and clean the round holes in the chassis bottom with dry cloth.
3. Attach the rubber feet to the four round holes in the chassis bottom.
4. Place the switch with upside up on the workbench.
CAUTION: Correctly connecting the grounding cable is crucial to lightning protection and EMI protection. |
The power input end of the switch has a noise filter, whose central ground is directly connected to the chassis to form the chassis ground (commonly known as PGND). You must securely connect this chassis ground to the earth to minimize the potential for system damage, maximize the safety at the site, and minimize EMI susceptibility of the system.
NOTE: The power and grounding terminals in this section are for illustration only. |
CAUTION: · Connect the grounding cable to the grounding strip in the equipment room. Do not connect it to a fire main or lightning rod. · To guarantee the grounding effect and avoid switch damage, use the grounding cable provided with the switch to connect the switch to a grounding strip in the equipment room. |
If a grounding strip is available at the installation site, use the grounding cable provided with the switch to connect the switch to the grounding strip.
Connecting the grounding cable to the chassis
Two types of grounding cables are available for the switch, as shown in Figure2-15 and Figure2-16.
To connect the grounding cable to the chassis:
1. Remove the grounding screw from the grounding hole in the rear panel of the chassis.
2. Use the grounding screw to attach the ring terminal of the grounding cable to the grounding screw hole. Fasten the screw.
Figure2-15 Connecting the grounding cable to the chassis (1)
(1) Grounding screw |
(2) Ring terminal |
(3) Grounding sign |
(4) Grounding hole |
(5) Grounding cable |
Figure2-16 Connecting the grounding cable to the chassis (2)
(1) Grounding cable |
(2) Grounding sign |
(3) Grounding hole |
(4) Ring terminal |
(5) Grounding screw |
Connecting the grounding cable to a grounding strip
1. Cut the grounding cable to a length required for connecting to the grounding strip.
2. Use diagonal pliers to strip 20 mm (0.79 in) of insulation off the end of the grounding cable. Then use needle-nose pliers to bend the bare metal part to the shape as shown in Figure2-17. Make sure the bended part can securely attached to the grounding post on the grounding strip.
3. Attach the bended part of the grounding cable to the grounding post and use the hex nut to fasten the bended part to the post.
Figure2-17 Connecting the grounding cable to a grounding strip
(1) Grounding post |
(2) Grounding strip |
(3) Grounding cable |
(4) Hex nut |
If the installation site does not have any grounding strips, but earth ground is available, hammer a 0.5 m (1.64 ft) or longer angle iron or steel tube into the earth ground to serve as a grounding conductor.
The dimensions of the angle iron must be a minimum of 50 × 50 × 5 mm (1.97 × 1.97 × 0.20 in). The steel tube must be zinc-coated and its wall thickness must be a minimum of 3.5 mm (0.14 in).
Weld the yellow-green grounding cable to the angel iron or steel tube and treat the joint for corrosion protection.
Figure2-18 Grounding the switch by burying the grounding conductor into the earth ground
(2) Chassis rear panel |
(4) Welding point |
(5) Grounding conductor |
(6) Earth |
The S6520X-26XC-UPWR-SI and S6520X-54XC-UPWR-SI switches each comes with empty fan tray slots and supports the LSPM1FANSB fan trays.
To ensure good ventilation of the switch, follow these guidelines to install and remove fan trays:
· The LSPM1FANSB fan tray provides port-side intake and power supply-side exhaust airflows. The fan tray handle is red. Select the LSPM1FANSB fan trays for the switch based on the ventilation requirements at the installation site.
· Before powering on the switch, make sure all fan tray slots have fan trays installed and the fan trays are the same model.
· Make sure all slots have a module or filler panel installed when the switch is operating.
· For an S6520X-26XC-UPWR-SI switch, if both fan trays fail during the switch operation, replace them within two minutes.
· For an S6520X-54XC-UPWR-SI switch, if more than one fan tray fail during the switch operation, replace the faulty fan trays one by one and finish replacing a fan tray within three minutes.
· If one fan tray fails while the switch is operating, perform either of the following tasks:
¡ If the ambient temperature is not higher than 27°C (80.6°F), replace the fan tray within 24 hours and make sure the failed fan tray is in position before the replacement.
¡ If the ambient temperature is higher than 27°C (80.6°F), replace the fan tray immediately.
Installing a fan tray
2. Unpack the fan tray and verify that the fan tray model is as required.
3. Orient the fan tray with the TOP mark facing up.
4. Align the fan tray with the fan tray slot. Holding the fan tray handles, slide the fan tray into the slot along the guide rails. Make sure the fan tray is fully seated in the slot and has a firm contact with the backplane.
To prevent damage to the fan tray or the connectors in the chassis, insert the fan tray gently. If you encounter a hard resistance while inserting the fan tray, pull out the fan tray and insert it again.
Figure2-19 Installing a fan tray
Removing a fan tray
WARNING! · Do not touch bare wires or terminals on the fan trays. · Do not place the fan tray in moist place. Prevent liquid from entering the fan tray. · Contact H3C Support if the circuits or components on a fan tray are faulty. Do not remove any fan tray components. |
To remove a fan tray:
2. Holding the fan tray handles, pull the fan tray slowly out of the slot along the guide rails.
3. Put the removed fan tray in an antistatic bag.
Figure2-20 Removing a fan tray
WARNING! · To avoid bodily injury or switch damage, strictly follow the procedures in Figure2-21 and Figure2-22 to install and remove a power supply. · You must provide a circuit breaker for each power supply. |
Figure2-21 Installation procedure
The S6520X-SI switches (except the S6520X-10XT-SI and S6520X-16XT-SI) each provide two power supply slots. It comes with power supply slot 1 empty and power supply slot 2 installed with a filler panel. You can install one or two power supplies for the switch as required. For the power supplies available for the switch and their specifications, see power supplies in Hardware Information and Specifications.
IMPORTANT: · An S6520X-18C-SI switch can only use PSR150-A1 or PSR150-D1 power supplies for power supply when it is installed with an LSPM6FWD firewall module. · An S6520X-26C-SI switch can only use PSR150-A1 or PSR150-D1 power supplies for power supply when it is installed with an LSWM2SP8P, LSWM4SP8PM, LSWM2MGT8P or LSWM2XMGT8P interface module, or an LSPM6FWD firewall module. |
The installation and removal procedures are the same for the PSR75-12A, PSR150-A1, and PSR150-D1 power supplies. The following procedure installs and removes a PSR75-12A power supply.
Installing a power supply
2. Remove the filler panel, if any, from the target power supply slot.
Use a Phillips screwdriver to remove the screws on the filler panel and then remove the filler panel.
Figure2-23 Removing the filler panel from the target power supply slot
3. Unpack the power supply and verify that the power supply model is correct.
4. Correctly orient the power supply. Make sure the lettering on the power supply is upward.
5. Align the power supply with the power supply slot. Grasping the handle of the power supply with one hand and supporting its bottom with the other, slide the power supply slowly into the slot along the guide rails. See callout 1 in Figure2-24.
To prevent damage to the power supply or the connectors on the backplane, insert the power supply gently. If you encounter a hard resistance when inserting the power supply, pull out the power supply and insert it again.
6. Use a Phillips screwdriver to fasten the captive screws on the power supply to secure the power supply in place. See callout 2 in Figure2-24.
If the captive screw cannot be tightly fastened, verify the installation of the power supply.
Figure2-24 Installing a power supply
Removing a power supply
2. Disconnect the power cord.
3. Use a Phillips screwdriver to completely loosen the captive screws on the power supply.
4. Grasping the handle of the power supply with one hand, pull the power supply part way out of the slot. Supporting the module bottom with the other, pull the power supply slowly out of the slot along the guide rails.
Put away the removed power supply in an antistatic bag or the power supply package bag for future use.
5. If you are not to install a new power supply in the slot, install a filler panel in the slot to prevent dust and ensure good ventilation.
The installation and removal procedures are the same for the PSR360-56A, PSR560-56D, PSR720-56A, and PSR1110-56A power supplies. The following procedure installs and removes a PSR720-56A power supply.
Hold the round hole on the filler panel and pull the filler panel out of the slot gently along the guide rails.
Figure2-25 Removing the filler panel from the target power supply slot
3. Unpack the power supply. Make sure the power supply model is as required.
Keep the packaging box and packaging bag for the power supply secure for future use.
5. Align the power supply with the power supply slot. Grasping the handle of the power supply with one hand and supporting its bottom with the other, slide the power supply slowly into the slot along the guide rails until the latch of the power supply clicks into the slot.
Figure2-26 Installing a power supply
Figure2-27 PSR1110-56A power supply installed in the switch
NOTE: The PSR1110-56A power supply, including the handle, adds 64 mm (2.52 in) to the chassis depth. |
3. Press the latch on the power supply towards the handle side, and pull the power supply part way out of the slot along the guide rails.
4. Grasping the handle of the power supply with one hand and supporting module bottom with the other, pull the power supply slowly out of the slot along the guide rails.
Figure2-28 Removing a power supply
WARNING! Provide a circuit breaker for each power input. Make sure the circuit breaker is off before connecting the power cord. |
Table2-4 Power source options and power cord connection procedures for the power supplies
Power supply model |
Power source option |
Power cord connection procedure |
Built-in power supply |
AC power source |
PSR75-12A/PSR150-A1 |
AC power source |
PSR150-D1 |
–48 VDC power source |
H3C RPS: RPS800-A or RPS1600-A |
PSR560-56D |
H3C RPS: RPS1600-A |
PSR360-56A/PSR720-56A/PSR1110-56A |
AC power source |
Connecting the power cord for a PSR360-56A/PSR720-56A/PSR1110-56A |
The power cord for a PSR75-12A or PSR150-A1 power supply is a C13 power cord. The power cord for a PSR360-56A, PSR720-56A, or PSR1110-56A power supply is a C15 power cord (for high-temperature equipment).
2. Attach the two ends of the power cord retainer clip into the two holders at the two sides of the power receptacle, and pull the power cord retainer clip upwards. See Figure2-29.
3. Connect the female connector of the AC power cord supplied with the power supply to the power receptacle. See callout 1 in Figure2-30.
4. Pull the power cord retainer clip downwards to secure the connector to the power receptacle. See callout 2 in Figure2-30.
5. Connect the other end of the power cord to an AC power source.
Figure2-29 Connecting the power cord for a built-in AC power supply (1)
Figure2-30 Connecting the power cord for a built-in AC power supply (2)
The power cord connection procedure is the same for the PSR75-12A and PSR150-A1 power supplies. The following procedure connects the power cord for a PSR75-12A power supply.
To connect the power cord for a PSR75-12A power supply:
2. Attach two ends of the power cord retainer clip into the two holes next to the power receptacle on the power supply, and pull the power cord retainer clip leftwards. See Figure2-31.
3. Connect the female connector of the AC power cord supplied with the power supply to the power receptacle. See callout 1 in Figure2-32.
4. Pull the power cord retainer clip rightwards to secure the connector to the power receptacle. See callout 2 in Figure2-32.
5. Connect the other end of the power cord to an AC power source. For a PSR75-12A power supply, you can also connect the power cord to a high-voltage DC power supply source.
Figure2-31 Connecting the power cord for a PSR75-12A power supply (1)
Figure2-32 Connecting the power cord for a PSR75-12A power supply (2)
CAUTION: · To connect a –48 VDC power source in the equipment room for power supply, use the DC power cord provided with the power supply. To connect an RPS for power supply, use an RPS power cord compatible with the RPS. · Before connecting the power cord to a –48 VDC power source, identify the positive and negative labels on the power cord to ensure correct connections. |
The power cord connection procedure is the same for the PSR150-D1 and PSR560-56D power supplies. The following procedure connects the power cord for a PSR150-D1 power supply.
To connect the power cord for a PSR150-D1 power supply:
2. Correctly orient the female connector of the DC power cord, and insert the connector into the power receptacle. See callout 1 in Figure2-33.
The DC power receptacle and DC power cord connector form a disorientation rejection structure. If you cannot insert the connector easily into the receptacle, the orientation might be wrong. Remove and reorient the connector.
3. Use a flat-blade screwdriver to fasten the screws on the connector to secure the connector to the power receptacle. See callout 2 in Figure2-33.
4. Connect the other end of the power cord to a –48 VDC power source or an RPS.
Figure2-33 Connecting the power cord for a PSR150-D1 power supply
The power cord connection procedure is the same for the PSR360-56A, PSR720-56A, and PSR1110-56A power supplies. The following procedure connects the power cord for a PSR720-56A power supply.
To connect the power cord for a PSR720-56A power supply:
2. Plug the female connector of the power cord into the power receptacle on the power supply, as shown by callout 1 in Figure2-34.
3. Use a cable tie to secure the power cord to the handle of the power supply, as shown by callout 2 and callout 3 in Figure2-34.
4. Connect the other end of the power cord to an AC power source.
Figure2-34 Connecting the power cord for a PSR720-56A power supply
CAUTION: · Do not touch the surface-mounted components on an expansion module directly with your hands. · Do not use excessive force when you install or remove an expansion module. · The expansion modules are hot swappable. However, do not install or remove an expansion module while the switch is starting up. |
IMPORTANT: · An S6520X-18C-SI switch must use PSR150-A1 or PSR150-D1 power supplies for power supply when it is installed with an LSPM6FWD firewall module. · An S6520X-26C-SI switch must use PSR150-A1 or PSR150-D1 power supplies for power supply when it is installed with an LSWM2SP8P, LSWM4SP8PM, LSWM2MGT8P or LSWM2XMGT8P interface module, or an LSPM6FWD firewall module. |
The S6520X-18C-SI, S6520X-26C-SI, S6520X-26MC-SI, S6520X-26MC-UPWR-SI, S6520X-26XC-UPWR-SI, and S6520X-54XC-UPWR-SI switches each provide an expansion slot on the rear panel. For the expansion modules available for the switches, see expansion modules in Hardware Information and Specifications.
The installation and removal procedures are similar for expansion modules. The following procedures install and remove LSWM2QP2P (with an ejector lever) and LSPM6FWD (without an ejector lever) expansion modules.
2. Use a Phillips screwdriver to remove the screw on the filler panel in the target expansion slot. Then remove the filler panel.
Keep the filler panel secure for future use.
Figure2-35 Removing the filler panel from the target expansion slot
3. Unpack the expansion module.
4. If the expansion module has an ejector lever, follow these steps to install it:
a. Fully open the ejector lever, as shown by callout 1 in Figure2-36.
b. Gently push the expansion module into the slot along the guide rails until the expansion module has good contact with the chassis. See callout 2 in Figure2-36.
c. Close the ejector lever, as shown by callout 3 in Figure2-36.
d. Use a Phillips screwdriver to fasten the captive screw on the expansion module to secure the module in the slot. See callout 4 in Figure2-36.
5. If the expansion module does not have an ejector lever, follow these steps to install it:
a. Gently push the expansion module into the slot along the guide rails until the expansion module has good contact with the chassis. See callout 1 Figure2-37.
b. Use a Phillips screwdriver to fasten the captive screw on the expansion module to secure the module in the slot. See callout 2 Figure2-37.
Figure2-36 Installing an expansion module with an ejector lever (LSWM2QP2P)
Figure2-37 Installing an expansion module without an ejector lever (LSPM6FWD)
Figure2-38 LSPM6FWD firewall module installed in the switch
NOTE: The LSPM6FWD firewall module, including the handle, adds 75 mm (2.95 in) to the chassis depth. |
Removing an expansion module
2. Use a Phillips screwdriver to remove the captive screw on the expansion module.
3. (Optional.) If the expansion module has an ejector lever, fully open the ejector lever.
Skip this step if the expansion module does not have an ejector lever.
4. Gently pull the expansion module out of the chassis along the guide rails.
5. If you are not to install a new expansion module, install a filler panel in the slot to prevent dust and ensure good ventilation in the switch.
Verifying the installation
Before powering on the switch, verify the following items:
· There is enough space around the switch for heat dissipation.
· The rack or workbench on which the switch is mounted is stable.
· The grounding cable is securely connected.
· The power source specifications are as required by the device.
· The power cords are correctly connected.
· If part of the network cable for a port is routed outdoors, verify that a network port lightning protector is used for the port.
· If a power line is routed from outdoors, verify that a surge protected power strip is used for the switch.
You can connect the switch to a configuration terminal by using the serial console port or the micro USB console port. Only the micro USB console port takes effect if you connect both the serial console port and micro USB console port.
In Figure3-1, the switch is connected to a configuration terminal (PC as an example) from the serial console port.
Figure3-1 Connecting the switch to a configuration terminal
As shown in Table3-1, three types of console cables can be used for connecting the switch to a configuration terminal. As a best practice, use a serial console cable for connection. The switch is not provided with a serial console cable or a micro USB console cable. Prepare an H3C console cable or prepare a micro USB console cable yourself.
Table3-1 Connection methods and console cables
Connection method |
Console cable type |
Configuration terminal-side connector |
Switch-side connector |
Using the serial console port for connection |
DB9-to-RJ45 console cable |
DB-9 female connector |
RJ-45 connector |
USB-to-RJ45 console cable |
USB connector |
RJ-45 connector |
Using the micro USB console port for connection |
Micro USB console cable |
USB connector |
Micro USB connector |
CAUTION: Follow these guidelines when you connect a DB9-to-RJ45 console cable: · Identify the mark on the serial console port and make sure you are connecting to the correct port. · The serial ports on PCs do not support hot swapping. To connect a PC to an operating switch, first connect the PC end. To disconnect a PC from an operating switch, first disconnect the switch end. |
A DB9-to-RJ45 serial console cable is an 8-core shielded cable, with a crimped RJ-45 connector at one end for connecting to the serial console port of the switch, and a DB-9 female connector at the other end for connecting to the serial port on a configuration terminal.
Figure3-2 DB9-to-RJ45 console cable
Table3-2 DB9-to-RJ45 console cable signal pinout
RJ-45 |
Signal |
DB-9 |
Signal |
1 |
RTS |
8 |
CTS |
2 |
DTR |
6 |
DSR |
3 |
TXD |
2 |
RXD |
4 |
SG |
5 |
SG |
5 |
SG |
5 |
SG |
6 |
RXD |
3 |
TXD |
7 |
DSR |
4 |
DTR |
8 |
CTS |
7 |
RTS |
To connect the switch to a configuration terminal (for example, a PC) by using a DB9-to-RJ45 console cable:
1. Plug the DB-9 female connector of the DB9-to-RJ45 console cable to the serial port on the PC.
2. Connect the RJ-45 connector to the serial console port on the switch.
IMPORTANT: · To use a USB-to-RJ45 console cable to connect the switch to a configuration terminal, first download and install the USB-to-RJ45 console driver on the configuration terminal and then connect the USB-to-RJ45 console cable to the configuration terminal. · If you have connected a USB-to-RJ45 console cable to the configuration terminal before installing the driver, remove and reconnect the USB-to-RJ45 console cable to the configuration terminal after driver installation. |
Figure3-3 USB-to-RJ45 console cable
The following installs the driver on the Windows system. To install the driver on other operating systems, see the installation guide in the driver compression package named by using the corresponding operating system.
To connect the switch to a configuration terminal by using a USB-to-RJ45 console cable:
1. Click the following link, or copy it to the address bar on your browser and download the USB-to-RJ45 console driver.
http://www.h3c.com/en/home/USB_to_RJ45_Console/
2. View the TXT file Read me in the Windows folder to check whether the Windows system of the configuration terminal supports the driver.
3. If the Windows system supports the driver, install PL23XX-M_LogoDriver_Setup_v200_20190815.exe.
4. Click Next on the welcome page of the driver installation wizard.
Figure3-4 Driver installation wizard
5. Click Finish after the drive installation is completed.
Figure3-5 Finishing the driver installation
6. Connect the standard USB connector of the cable to the USB port of the configuration terminal.
7. Connect the RJ-45 connector of the cable to the console port of the switch.
A micro USB console cable has a micro USB connector at one end to connect to the micro USB console port of the switch, and a standard USB connector at the other end to connect to the USB port on the configuration terminal.
Figure3-6 Micro USB console cable
To connect the switch to a configuration terminal, for example a PC, by using a micro USB console cable:
1. Connect the standard USB connector to the USB port of the PC.
2. Connect the micro USB connector to the micro USB console port of the switch.
3. Click the following link, or copy it to the address bar on the browser to log in to download and install the USB console driver on the configuration terminal.
http://www.h3c.com/en/home/USB_Console/
4. Select a driver program according to the operating system you use:
¡ XR21V1410_XR21B1411_Windows_Ver1840_x86_Installer.EXE—32-bit operating system.
¡ XR21V1410_XR21B1411_Windows_Ver1840_x64_Installer.EXE—64-bit operating system.
5. Click Next on the installation wizard.
Figure3-7 Device Driver Installation Wizard
6. Click Continue Anyway.
Figure3-8 Software Installation
7. Click Finish.
Figure3-9 Completing the device driver installation wizard
Setting terminal parameters
To configure and manage the switch through the console port, you must run a terminal emulator program, such as TeraTermPro, on your configuration terminal. You can use the emulator program to connect a network device, a Telnet site, or an SSH site. For more information about the terminal emulator programs, see the user guides for these programs.
Configure the terminal parameters as follows:
· Bits per second—9600.
· Data bits—8.
· Parity—None.
· Stop bits—1.
· Flow control—None.
Starting the switch
Pre-start checklist
· The power cord is correctly connected.
· The input power voltage is as required by the switch.
· The console cable is correctly connected.
· The PC has started, and the terminal parameters have been correctly configured.
Power on the switch
During the startup process, you can access Boot ROM menus to perform tasks such as software upgrade and file management. The Boot ROM interface and menu options differ with software versions. For more information about Boot ROM menu options, see the software-matching release notes for the device.
After the startup process is completed, you can access the CLI to configure the switch.
For more information about the configuration commands and CLI, see H3C S6520X-SI Switch Series Configuration Guides and H3C S6520X-SI Switch Series Command References.
4 Setting up an IRF fabric
You can use H3C IRF technology to connect and virtualize S6520X-SI switches into a large virtual switch called an "IRF fabric" for flattened network topology, and high availability, scalability, and manageability.
An S6520X-SI switch can set up an IRF fabric only with switches from the same switch series.
IRF fabric setup flowchart
Figure4-1 IRF fabric setup flowchart
To set up an IRF fabric:
Step |
1. Plan IRF fabric setup |
Plan the installation site and IRF fabric setup parameters: · Planning IRF fabric size and the installation site · Identifying the master switch and planning IRF member IDs · Planning IRF topology and connections |
2. Install IRF member switches |
See "Installing the switch in a 19-inch rack" or "Mounting the switch on a workbench." |
3. Connect ground wires and power cords |
See "Grounding the switch" and "Connecting the power cord." |
4. Power on the switches |
N/A |
5. Configure basic IRF settings |
See H3C S6520X-SI Switch Series IRF Configuration Guide or H3C S6520X-SI Switch Series Virtual Technologies Configuration Guide, depending on the software version. |
6. Connect the physical IRF ports |
Connect physical IRF ports on switches. All switches except the master switch automatically reboot, and the IRF fabric is established. |
Planning IRF fabric setup
This section describes issues that an IRF fabric setup plan must cover.
Choose switch models and identify the number of required IRF member switches, depending on the user density and upstream bandwidth requirements. The switching capacity of an IRF fabric equals the total switching capacities of all member switches.
Plan the installation site depending on your network solution, as follows:
· Place all IRF member switches in one rack for centralized high-density access.
· Distribute the IRF member switches in different racks to implement the ToR access solution for a data center.
NOTE: For the maximum IRF member devices supported by the switch, see the release notes that come with the switch. |
Determine which switch you want to use as the master for managing all member switches in the IRF fabric.
An IRF fabric has only one master switch. You configure and manage all member switches in the IRF fabric at the CLI of the master switch. IRF member switches automatically elect a master.
You can affect the election result by assigning a high member priority to the intended master switch. For more information about master election, see H3C S6520X-SI Switch Series IRF Configuration Guide or H3C S6520X-SI Switch Series Virtual Technologies Configuration Guide, depending on the software version.
Prepare an IRF member ID assignment scheme. An IRF fabric uses member IDs to uniquely identify and manage its members, and you must assign each IRF member switch a unique member ID.
You can create an IRF fabric in daisy chain topology or more reliable ring topology. In ring topology, the failure of one IRF link does not cause the IRF fabric to split as in daisy chain topology. Instead, the IRF fabric changes to a daisy chain topology without interrupting network services.
You connect the IRF member switches through IRF ports, the logical interfaces for the connections between IRF member switches. Each IRF member switch has two IRF ports: IRF-port 1 and IRF-port 2. To use an IRF port, you must bind a minimum of one physical port to it.
When connecting two neighboring IRF member switches, you must connect the physical ports of IRF-port 1 on one switch to the physical ports of IRF-port 2 on the other switch.
Multiple types of ports (see Table4-1 for the port types) on the S6520X-SI switches can be used for IRF connections. You can bind several IRF physical ports to an IRF port for increased bandwidth and availability.
Figure4-2 and Figure4-3 show the topologies of an IRF fabric made up of three S6520X-26C-SI switches. The IRF port connections in the two figures are for illustration only, and more connection methods are available.
Figure4-2 IRF fabric in daisy chain topology
Figure4-3 IRF fabric in ring topology
Identify the physical IRF ports on the member switches according to your topology and connection scheme.
Table4-1 shows the physical ports that can be used for IRF connection and the port use restrictions.
Table4-1 Candidate physical IRF ports and their use restrictions
Chassis |
Candidate physical IRF ports |
Use restrictions |
S6520X-16ST-SI |
The following ports on the front panel: · 16 × SFP+ ports · 2 × 1/10GBASE-T autosensing Ethernet ports |
· All physical ports to be bound to an IRF port must have the same data rate. · Physical ports on interface modules and the front panel can be bound to the same IRF port. · If a QSFP+ port is split into four virtual SFP+ ports, the QSFP+ port cannot be used as a physical IRF port. · The physical ports must operate at their maximum rate. · The ports on an LSPM4G4T6P interface module cannot be used as IRF physical ports. |
S6520X-24ST-SI |
The following ports on the front panel: · 24 × SFP+ ports · 2 × 1/10GBASE-T autosensing Ethernet ports on the front panel |
S6520X-10XT-SI |
The following ports on the front panel: · 2 × SFP+ ports · 8 × 10/5G/2.5G/1000BASE-T autosensing Ethernet ports |
S6520X-16XT-SI |
The following ports on the front panel: · 2 × SFP+ ports · 14 × 10/5G/2.5G/1000BASE-T autosensing Ethernet ports |
S6520X-18C-SI |
· 16 × SFP+ ports on the front panel · 1/10GBASE-T autosensing Ethernet ports, 5G/2.5G/1000BASE-T autosensing Ethernet ports, 10G/5G/2.5G/1000BASE-T autosensing Ethernet ports, SFP+ ports, SFP28 ports, or QSFP+ ports on the expansion module |
S6520X-26C-SI |
· 24 × SFP+ ports on the front panel · 1/10GBASE-T autosensing Ethernet ports, 5G/2.5G/1000BASE-T autosensing Ethernet ports, 10G/5G/2.5G/1000BASE-T autosensing Ethernet ports, SFP+ ports, SFP28 ports, or QSFP+ ports on the expansion module |
S6520X-26MC-SI |
· 24 × 5G/2.5G/1000/100BASE-T autosensing Ethernet ports on the front panel · 1/10GBASE-T autosensing Ethernet ports, 5G/2.5G/1000BASE-T autosensing Ethernet ports, 10G/5G/2.5G/1000BASE-T autosensing Ethernet ports, SFP+ ports, SFP28 ports, or QSFP+ ports on the expansion module |
S6520X-26MC-UPWR-SI |
S6520X-26XC-UPWR-SI |
· 24 × 10G/5G/2.5G/1000/100BASE-T autosensing Ethernet ports on the front panel · 1/10GBASE-T autosensing Ethernet ports, 5G/2.5G/1000BASE-T autosensing Ethernet ports, 10G/5G/2.5G/1000BASE-T autosensing Ethernet ports, SFP+ ports, SFP28 ports, or QSFP+ ports on the expansion module |
· 48 × 10G/5G/2.5G/1000/100BASE-T autosensing Ethernet ports on the front panel · 4 × QSFP+ ports on the front panel · 5G/2.5G/1000BASE-T autosensing Ethernet ports, 10G/5G/2.5G/1000BASE-T autosensing Ethernet ports, SFP+ ports, SFP28 ports, or QSFP+ ports on the expansion module |
Planning the cabling scheme
Use the following cables to connect the IRF physical ports on the switch:
· 5G/2.5G/1000BASE-T autosensing Ethernet port—Category 5e or above twisted pair cable.
· 5G/2.5G/1000/100BASE-T autosensing Ethernet port—Category 5e or above twisted pair cable.
· 10G/5G/2.5G/1000BASE-T autosensing Ethernet port—Category 5e or above twisted pair cable.
· 10G/5G/2.5G/1000/100BASE-T autosensing Ethernet port—Category 5e or above twisted pair cable.
· 1/10GBASE-T autosensing Ethernet port—Category 6 or above twisted pair cable.
· SFP+ port—SFP+ transceiver module and optical fiber or SFP+ cable. For the available transceiver module and cable types, see ports in Hardware Information and Specifications.
· SFP28 port—SFP28 transceiver module and optical fiber or SFP28 cable. For the available transceiver module and cable types, see ports in Hardware Information and Specifications.
· QSFP+ port—QSFP+ transceiver modules and optical fiber or QSFP+ cable. For the available transceiver module and cable types, see ports in Hardware Information and Specifications.
For a short-distance IRF connection in an equipment room, use a twisted-pair cable, SFP+ cable, SFP28 cable, or QSFP+ cable.
For a long-distance IRF connection, use SFP+/SFP28/QSFP+ transceiver modules and optical fibers.
The following subsections describe several H3C recommended IRF connection schemes by using SFP+ cables and SFP+ transceiver modules and fibers. All these schemes use a ring topology.
IMPORTANT: In these schemes, all physical IRF ports are located on the same side. If physical IRF ports are on different sides, you must measure the distance between them to select an appropriate cable. |
Connecting the IRF member switches in one rack
Connect the IRF member switches (9 switches in this example) in a rack as shown in Figure4-4. The switches in the ring topology (see Figure4-5) are in the same order as connected in the rack.
Figure4-4 Connecting the switches in one rack
Connecting the IRF member switches in a ToR solution
You can install IRF member switches in different racks side by side to deploy a top of rack (ToR) solution.
After you install the IRF member switches, power on the switches, and log in to each IRF member switch (see H3C S6520X-SI Switch Series Fundamentals Configuration Guide) to configure their member IDs, member priorities, and IRF port bindings.
Follow these guidelines when you configure the switches:
· Assign the master switch higher member priority than any other switch.
· Bind physical ports to IRF port 1 on one switch and to IRF port 2 on the other switch. You perform IRF port binding before or after connecting IRF physical ports depending on the software release.
· To bind the ports on an interface module to an IRF port, you must install the interface module first.
· Execute the display irf configuration command to verify the basic IRF settings.
For more information about configuring basic IRF settings, see H3C S6520X-SI Switch Series IRF Configuration Guide or H3C S6520X-SI Switch Series Virtual Technologies Configuration Guide, depending on the software version.
Use twisted pair cables, cables, or transceiver modules and fibers to connect the IRF member switches as planned.
Wear an ESD wrist strap when you connect cables or transceiver modules and fibers. For how to connect them, see H3C Transceiver Modules and Network Cables Installation Guide.
To verify the basic functionality of the IRF fabric after you finish configuring basic IRF settings and connecting IRF ports:
1. Log in to the IRF fabric through the console port of any member switch.
2. Create a Layer 3 interface, assign it an IP address, and make sure the IRF fabric and the remote network management station can reach each other.
3. Use Telnet, web, or SNMP to access the IRF fabric from the network management station. (See H3C S6520X-SI Switch Series Fundamentals Configuration Guide.)
4. Verify that you can manage all member switches as if they were one node.
5. Display the running status of the IRF fabric by using the commands in Table4-2.
Table4-2 Displaying and maintaining IRF configuration and running status
Task |
Command |
Display information about the IRF fabric. |
display irf |
Display all members’ IRF configurations that take effect at a reboot. |
display irf configuration |
Display IRF fabric topology information. |
display irf topology |
NOTE: To avoid IP address collision and network problems, configure a minimum of one multi-active detection (MAD) mechanism to detect the presence of multiple identical IRF fabrics and handle collisions. For more information about MAD detection, see H3C S6520X-SI Switch Series IRF Configuration Guide or H3C S6520X-SI Switch Series Virtual Technologies Configuration Guide, depending on the software version. |
Built-in power supply failure
The S6520X-10XT-SI and S6520X-16XT-SI switches use a built-in power supply and support only AC power input.
Symptom
The system status LED (SYS) of the switch is off.
Solution
To resolve the issue:
1. Verify that the AC power cord is connected to the switch correctly, and the AC-input power receptacle on the switch and the AC power outlet are in good condition.
2. Verify that the AC power source is operating correctly.
3. Verify that the operating temperature of the switch is in the acceptable range, and the power supply has good ventilation. Over-temperature can cause the power supply to stop working and enter self-protection mode.
4. If the issue persists, contact H3C Support.
The S6520X-SI switches (except the S6520X-10XT-SI and S6520X-16XT-SI) use removable power supplies.
To identify the operating status of a power supply on an S6520X-16ST-SI, S6520X-24ST-SI, S6520X-18C-SI, S6520X-26C-SI, or S6520X-26MC-SI switch, observe the PWR1 or PWR2 LED on the front panel. For more information about the PWR1 and PWR2 LEDs, see LEDs in Hardware Information and Specifications.
To identify the operating status of a power supply on an S6520X-26MC-UPWR-SI, S6520X-26XC-UPWR-SI, or S6520X-54XC-UPWR-SI switch, observe the PWR1 or PWR2 LED on the front panel and the LED on the power supply. For more information about the PWR1 and PWR2 LEDs, see LEDs in Hardware Information and Specifications. For more information about the LED on the power supply, see H3C PSR360-56A Power supply User Manual, H3C PSR560-56D Power supply User Manual, H3C PSR720-56A Power supply User Manual, and H3C PSR1110-56A Power supply User Manual.
Symptom
The PWR LED for a power supply is not steady green.
Solution
1. Verify that the power cord is correctly connected.
2. Verify that the power source meets the requirement.
3. Verify that the operating temperature of the switch is in an acceptable range and the power supply has good ventilation.
To replace a power supply, see "Installing and removing a ."
Fan tray failure
The S6520X-SI switches (except the S6520X-26XC-UPWR-SI and S6520X-54XC-UPWR-SI) use built-in fan trays. If a fan tray fails, contact H3C Support.
The S6520X-26XC-UPWR-SI and S6520X-54XC-UPWR-SI switches use removable fan trays. If an LSPM1FANSB fan tray fails, the fan tray Alarm LED turns on and the switch sends alarm messages. You can see "Installing and removing a fan tray" to replace the fan tray.
Configuration terminal issues
If the configuration environment setup is correct, the configuration terminal displays booting information when the switch is powered on. If the setup is incorrect, the configuration terminal displays nothing or garbled text.
No display
Symptom
The configuration terminal does not have display when the switch is powered on.
Solution
1. Verify that the power supply is supplying power to the switch correctly.
2. Verify that the console cable is correctly connected.
3. Verify that the console cable does not have any issues and the terminal settings are correct.
Garbled display
Symptom
The display on the configuration terminal is garbled.
Solution
1. Verify that the following settings are configured for the terminal:
¡ Baud rate—9600.
¡ Data bits—8.
¡ Stop bits—1.
¡ Parity—None.
¡ Flow control—None.
2. If the issue persists, contact H3C Support.
