14-Common Industrial Protocols Configuration Guide
HomeSupportConfigure & DeployConfiguration GuidesH3C IE4300[IE4300-M][IE4320] Switch Series Configuration Guides-R63xx-6W10214-Common Industrial Protocols Configuration Guide
01-EtherNet IP configuration
01-EtherNet IP configuration 421.43 KB
Configuring EtherNet/IP·· 2
About EtherNet/IP· 2
Benefits· 2
Network model 2
Communication mechanism·· 3
Restrictions: Software version compatibility with EtherNet/IP· 6
Restrictions and guidelines· 6
Enabling EtherNet/IP· 6
Display and maintenance commands for EtherNet/IP· 7
Appendix A  H3C device-specific object specifications· 7
Identity object (Class ID: 0x01) 7
Service codes· 7
Class attributes (instance=0) 8
Instance attributes (instance>0) 8
Message router object (Class ID: 0x02) 9
Service codes· 10
Class attributes (instance=0) 10
Instance attributes (instance>0) 10
Assembly object (Class ID: 0x04) 10
Service codes· 10
Class attributes (instance=0) 11
Instance attributes (instance>0) 11
Connection manager object (Class ID: 0x06) 11
Service codes· 11
Class attributes (instance=0) 12
Instance attributes (instance>0) 12
TCP/IP interface object (Class Code: 0xF5) 12
Service codes· 12
Class attributes (instance=0) 13
Instance attributes (instance>0) 13
Ethernet link object (Class Code: 0xF6) 15
Service codes· 15
Class attributes (instance=0) 15
Instance attributes (instance>0) 15
Appendix B  H3C device-specific CIP data in explicit messaging· 16
Requesting port and alarm data· 16
Port information· 17
Alarm information· 18
Requesting device status data· 18
Device information (01) 20
Port information (02) 21
RSTP information (03) 22
ERPS ring network information (04) 23
ERPS instance information (05) 24
RRPP domain information (06) 26
RRPP ring information (07) 26
Setting the device status· 28
Appendix C  H3C device-specific CIP data in implicit messaging· 29
Output message· 29
Input message· 30
Port information in the input message· 30
Alarm information in the input message· 32
About EtherNet/IP
Ethernet/Industrial Protocol (EtherNet/IP) is an industrial network control technology defined and maintained by the Open DeviceNet Vendor Association (ODVA). Built on standard Ethernet and TCP/IP technologies, EtherNet/IP uses Ethernet protocols at the physical and data link layers, TCP/IP protocol family at the network and transport layers, and Common Industrial Protocol (CIP) at the application layer. EtherNet/IP can meet the real-time and reliable communication requirements in high-load industrial networks, and it is widely used in industrial Ethernet networks.
Benefits
EtherNet/IP has the following technical benefits:
·     Open: EtherNet/IP uses the TCP/IP protocol stack. It can use existing standard Ethernet hardware and be compatible with existing industrial Ethernet networks.
·     Standardized: EtherNet/IP contains recognized standards defined by ODVA. It provides a unified communication standard for different industrial devices and systems and allows smooth communication between devices from different vendors.
·     Safe and reliable: The application layer CIP protocol of EtherNet/IP has a built-in mechanism for secure and reliable data transmission.
·     Scalable: The application layer CIP protocol of EtherNet/IP is an expandable protocol that can be extended and customized based on different application scenarios and requirements.
Network model
As shown in Table 1, EtherNet/IP uses the same physical layer, data link layer, and transport layer as standard Ethernet and adds an encapsulation layer above the transport layer. This encapsulation layer is used to package the CIP data coming from the application layer into a standard format.
Figure 1 EtherNet/IP network model
Messaging type
EtherNet/IP uses two types of messaging for communication between devices: explicit messaging and implicit messaging.
·     Explicit messaging: Data is transmitted through TCP, suitable for scenarios that require accurate message delivery and are not time critical, such as configuring device information and uploading or downloading programs.
·     Implicit messaging: Data is transmitted through UDP, suitable for transmission of time-critical data such as I/O data. A CIP connection must be established before implicit messaging. CIP connection is a CIP protocol service. After the connection is established, the two ends each hold a connection ID for subsequent information exchange.
Communication model
Explicit communication
EtherNet/IP explicit communication uses a client/server model in which the industrial control device (controller) acts as the client, and peripheral I/O sensors, valves, industrial switches, or other measuring devices (devices) act as servers. The communication is initiated by the client, which sends a request to the servers. The servers respond accordingly after receiving the request.
Figure 2 EtherNet/IP explicit communication model
Implicit communication
EtherNet/IP implicit communication uses a producer/consumer model. In this model, the devices act as data producers. They send their data onto the network all at once, allowing the controller to selectively read the data they require. This greatly enhances the communication efficiency of the entire EtherNet/IP network system.
Figure 3 EtherNet/IP implicit communication model
Message formats
Explicit communication message format
In explicit communication mode, EtherNet/IP encapsulates the CIP protocol data in the following format.
Figure 4 Explicit communication message format
The EtherNet/IP explicit encapsulation package includes an encapsulation header and encapsulation data. The encapsulation header contains the following fields:
·     Command: EtherNet/IP command that describes the function and purpose of the message, in 2 bytes.
·     Length: Length of the data following the encapsulation header, in 2 bytes.
·     Session Handle: TCP session handle, in 4 bytes.
·     Status: Execution status of the EtherNet/IP command, in 4 bytes.
·     Sender Context: Description of sender information, in 8 bytes.
·     Options: Optional field, a maximum of 4 bytes.
The encapsulating data contains the following fields:
·     Item Count: Total number of items in the packaged data.
·     Address Item: Destination address information, including the address type, address length, and specific address.
·     Data Item: CIP protocol data information, including the data type, data length, and specific data. The specific data includes the CIP command and request path.
Implicit communication message format
In implicit communication mode, EtherNet/IP encapsulates the CIP protocol data in the following format.
Figure 5 Implicit communication message format
The EtherNet/IP explicit encapsulation package includes only the encapsulation data, which contains the following fields:
·     Address Item: Destination address information, including the address type, address length, CIP connection ID, and specific address. In implicit communication mode, EtherNet/IP determines the target by the connection ID.
CIP object model
Each CIP node is a set of objects, and the targets of CIP communication are these specific objects. For EtherNet/IP communication, you can define specific components on a device as different objects.
Objects use a three-dimensional structure with classes, instances, and attributes. Multiple classes can exist on a CIP node, each class can have multiple instances, and each instance can have multiple attributes, as shown in Figure 6.
Figure 6 CIP object model diagram
EtherNet/IP is supported only in F6355P05 and later.
H3C industrial switches can act only as devices in EtherNet/IP communication. The term "device" in this configuration procedure collectively refers to H3C industrial switches.
After EtherNet/IP is enabled on a device, the device can establish a TCP or UDP connection with the controller and perform EtherNet/IP communication over this connection. The controller can read and write the data or status of the device over EtherNet/IP. The device uses port number 44818 for establishing TCP connections and port number 2222 for establishing UDP connections.
Arbitrarily changing the status of the device might pose serious security risks to the entire network when a misoperation or malicious attack is present in the network. In such scenarios, switch the EtherNet/IP operating mode on the device to read-only mode. This ensures that the controller can only read information from the device via EtherNet/IP.
The device uses VLAN 1 as the EtherNet/IP management VLAN for communication with the controller. Before enabling EtherNet/IP, first assign an IP address to VLAN interface 1.
The controller can differentiate data of ports in the total data sent by the lower-level device by the port ID displayed in the display ethernet-ip information command.
Currently, the controller can read and modify the information of 128 ports on a device simultaneously.
Some CIP commands require a specific transport layer connection for EtherNet/IP communication.
Table 1 CIP command codes and required transport layer connection
Command code
Name
Connection method
0x0000
NOP
TCP
0x0004
ListServices
TCP or UDP
0x0063
ListIdentity
TCP or UDP
0x0064
ListInterfaces
TCP or UDP
0x0065
RegisterSession
TCP
0x0066
UnRegisterSession
TCP
0x006F
SendRRData
TCP
0x0070
SendUnitData
TCP
0x0072
IndicateStatus
TCP
0x0073
Cancel
TCP
2.     Enable EtherNet/IP.
ethernet-ip enable
By default, EtherNet/IP is disabled.
3.     (Optional) Set the EtherNet/IP operating mode to read-only.
ethernet-ip working-mode read-only
By default, the EtherNet/IP operating mode is read/write. In read/write mode, the device allows read/write operations from the controller over EtherNet/IP.
Display information required for reading port information via EtherNet/IP.
display ethernet-ip information interface { interface-type interface-number | interface-name }
"instance=0" indicates a class attribute, which is shared by all objects within the same class. "instance>0" indicates an instance attribute, which is unique to an object instance.
Service codes
Service code
Need in implementation
Service name
instance=0
instance>0
0x0E
Conditional (√)
Conditional (√)
Get_Attribute_Single
Reads the specified attribute.
0x05
Optional (x)
Required (√)
Reset
Invokes the reset service for the device.
0x01
Optional (√)
Conditional (√)
Get_Attributes_All
Reads multiple attributes of the object.
Class attribute
Access rule
Attribute name
Data type
0x01
Get
Revision
USHORT
Object revision.
0x02
Get
Number of instances
USHORT
Number of object instances currently created in this class level of the device.
0x06
Get
Number of max attributes
USHORT
Maximum number of attributes in the current class.
0x07
Get
Number of max instance attributes
USHORT
Maximum number of attributes in the current instance.
Instance attribute
Access rule
Name
Data type
0x01
Get
Vendor ID
UINT
Vendor ID.
0x02
Get
Device type
UINT
Device type.
0x03
Get
Product code
UINT
Product code:
·     2465: H3C IE4320-28S
·     2463: H3C IE4320-28P
·     2464: H3C IE4320-28S-HPWR
·     2479: H3C IE4320-52S
·     2478: H3C IE4320-52P
·     2487: H3C IE4320-28S-PS1
·     2552: H3C IE4320-12P-UPWR
·     2551: H3C IE4320-28F
·     2579: H3C IE4320-6P
·     2576: H3C IE4320-12P
·     2578: H3C IE4320-20P
·     2577: H3C IE4320-6P-AC
·     2604: H3C IE4320-12P-PWRM
·     3470: H3C IE4320-28P-K
·     3469: H3C IE4320-28P-S
·     1749: H3C IE4300-28P-M
·     1974: H3C IE4300-12P-PWR-M
·     2225: H3C IE4300-12P-AC
·     2226: H3C IE4300-12P-PWR
·     25506: H3C Simware32/H3C Simware64
0x04
Get
Revision
STRUCT
Device revision, including major and minor revisions, displayed in the major.minor format.
Major revision
USINT
Major revision range: 0x 01 to 0x 7F.
Minor revision
USINT
Minor revision range: 0x01 to 0xFF.
0x05
Get
Status
WORD
Device status.
0x06
Get
Serial number
UDINT
Serial number.
0x07
Get
Product name
STRING
Product name.
The message router object strips the header of messages received from the Unconnected Message Manager (UCMM) or Transport, and parses the data. Then, it routes the service to the target class or attribute.
Service codes
Service code
Service name
Class attribute
Instance attribute
0x0E
Required (√)
Required (√)
0x01
Conditional (√)
Conditional(√)
Get_Attribute_All
Reads the value of multiple attributes of the object.
Class attribute
Access rule
Name
Data type
0x01
Get
Revision
UINT
Object revision
0x02
Get
Max instance
UINT
Maximum instance number of an object currently created in this class level of the device.
0x03
Get
Number of instances
UINT
Number of object instances currently created at this class level of the device.
No instance attributes are currently available for the message router object.
The assembly object binds attributes of multiple objects. It defines the parameters for I/O data exchange.
Service codes
Service code
Service name
Static assembly
Dynamic assembly (unsupported currently)
Class attribute
Instance attribute
Class attribute
Instance attribute
0x0E
Conditional (√)
Required (√)
Required (√)
Required (√)
0x08
N/A
N/A
Required
N/A
Create
0x10
N/A
Optional (√)
N/A
Conditional (√)
Set_Attribute_Single
Sets the specified attribute.
0x09
N/A
N/A
Conditional
Required
Delete
Deletes the assembly object and releases the resources.
Class attribute
Access rule
Name
Data type
0x01
Get
Revision
UINT
Object revision
0x02
Get
Max instance
UINT
0x03
Get
Number of instances
UINT
Instance attribute
Access rule
Name
Data type
0x03
Required (√)
Get/Set
Data
ARRAY of BYTE
I/O connection data.
The connection manager object is responsible for establishment and termination of Common Industrial Protocol (CIP) connections.
Service codes
Service code
Service name
Class attribute
Instance attribute
0x01
Optional (√)
Optional (√)
Get_Attributes_All
0x0E
Conditional (√)
Conditional (√)
0x4E
N/A
Conditional (√)
Forward_Close
Closes a CIP connection.
0x54
N/A
Conditional (√)
Forward_Open
Opens a CIP connection.
0x5A
N/A
Conditional (√)
Get_Connection_Owner
Determines the owner of a redundant connection.
Class
Attribute
Access rule
Name
Data type
0x01
Get
Revision
UINT
Object revision
0x02
Get
Max instance
UINT
0x03
Get
Number of instances
UINT
No instance attributes are available currently for the connection manager object.
The TCP/IP interface object provides the mechanism to configure TCP/IP network interfaces on a device.
Service codes
Service code
Service name
Class attribute
Instance attribute
0x01
Optional (√)
Optional (√)
Get_Attributes_All
0x0E
Conditional (√)
Required (√)
0x10
N/A
Required (√)
Class
Attribute
Access rule
Attribute name
Data type
0x01
Get
Revision
UINT
Object revision
0x02
Get
Max instance
UINT
0x03
Get
Number of instances
UINT
Class attribute
Access rule
Attribute name
Data type
Remarks
0x01
Get
Status
DWORD
IP configuration status
·     0—Not configured.
·     1—Valid configuration obtained from Bootstrap Protocol (BOOTP), Dynamic Host Configuration Protocol (DHCP), or non-volatile storage.
·     2—Configured by hardware.
0x02
Get
Configuration capability
DWORD
Configuration capability supported by the device
·     0—BOOTP client
·     1—DNS client
·     2—DHCP client
·     3—DHCP-DNS update
·     4—Configuration settable
·     5 to 31—Reserved
0x03
Get/Set
Configuration
control
DWORD
Interface IP mode
0x04
Get
Physical link object
STRUCT
of:
Path of the physical link object
The obtained attribute is a structure composed of the following members.
Path size
UINT
Path size
Path
EPATH
Specific path information
0x05
Get/Set
Interface configuration
STRUCT
of:
TCP/IP network configuration information of the device
IP address
UDINT
IP address of the device
Network mask
UDINT
Subnet mask of the device
Gateway address
UDINT
Gateway of the device
Name server
UDINT
Primary name server
Name server 2
UDINT
Secondary name server
Domain name
STRING
Default domain name
0x06
Get/Set
Host name
STRING
Device name
0x08
Get
Set is conditional
TTL value
USINT
TTL value of EtherNet/IP multicast packets
0x09
Get
Set is conditional
Mcast config
STRUCT of:
Multicast IP address configuration information
Alloc control
USINT
Multicast address allocation status
Reserved
USINT
Num Mcast
UINT
Number of allocable multicast addresses
An Ethernet link maintains link-specific counters and status information for an Ethernet interface.
Service codes
Service code
Service name
Class attribute
Instance attribute
0x01
Optional (√)
Optional (√)
Get_Attributes_All
0x0E
Conditional (√)
Required (√)
Class
Attribute
Access rule
Attribute name
Data type
0x01
Get
Revision
UINT
Object revision
0x02
Get
Max instance
UINT
0x03
Get
Number of Instances
UINT
Class attribute
Access rule
Attribute name
Data type
Remarks
0x01
Get
Interface speed
DWORD
Interface speed
10 Mbps
100 Mbps
1 G
0x02
Get
Interface flags
DWORD
Interface flags
0x03
Get
Physical address
ARRAY of 6 USINTS
MAC address
0x0A
Get
Interface label
SHORT_
STRING
Interface name
To retrieve or set the status of an H3C device, the industrial control device (controller) must first send a request carrying the set attribute single command to that device. Subsequently, the controller sends a request carrying the get attribute single command to formally request the data.
Service
Service: 16
Class: 4
Instance: 104
Attribute: 3
Get attribute single
Service: 14
Class: 4
Instance: 103
Attribute: 3
To retrieve port and alarm data of an H3C device, the controller needs to send a request that carries the set attribute single command to that device. This request populates the first two bytes of the data portion with 0x0000, and the succeeding bytes as follows:
Third byte
Fourth byte
00
01
02
03
04
05
n
Port status and alarms (00)
After receiving the request packet with the get attribute single command, the H3C device replies to the controller with a response packet. The value starting at position 05 in the response message is as follows:
Port information
Input byte offset num
Status item
Position in the data portion of the packet (byte)
Each byte represents the status of four ports. The port status occupies 32 bytes. The succeeding bytes are alarm information.
0
Status of ports 1 to 4
1
Status of ports 5 to 8
2
Status of ports 9 to 12
3
Status of ports 13 to 16
4
Status of ports 17 to 20
5
Status of ports 21 to 24
6
Status of ports 25 to 28
7
Status of ports 29 to 32
8
Status of ports 33 to 36
9
Status of ports 37 to 40
10
Status of ports 41 to 44
11
Status of ports 45 to 48
12
Status of ports 49 to 52
13
Status of ports 53 to 56
14
Status of ports 57 to 60
15
Status of ports 61 to 64
16
Status of ports 65 to 68
17
Status of ports 69 to 72
18
Status of ports 73 to 76
19
Status of ports 77 to 80
20
Status of ports 81 to 84
21
Status of ports 85 to 88
22
Status of ports 89 to 92
23
Status of ports 93 to 96
24
Status of ports 97 to 100
25
Status of ports 101 to 104
26
Status of ports 105 to 108
27
Status of ports 109 to 112
28
Status of ports 113 to 116
29
Status of ports 117 to 120
30
Status of ports 121 to 124
31
Status of ports 125 to 128
The status of each port is represented by 2 bits. The available port status in binary are:
·     00: Disabled
·     01: Up
·     10: Down
A port is considered enabled if it is in up or down state.
Alarm information
Position in the data portion of the message
(byte)
Name
Value
Data length (bytes)
32
Port 1 alarm status
0x00: disable
0x01: normal
0x02: alarm
1
33
Port 2 alarm status
0x00: disable
0x01: normal
0x02: alarm
1
34
Ports 3 to 128 alarm status
Each port occupies 1 byte
0x01: normal
0x02: alarm
62
160
Temperature alarm status
0x01: normal
0x02: alarm
1
161
CPU alarm status
0x01: normal
0x02: alarm
1
162
Memory alarm status
0x01: normal
0x02: alarm
1
163
Power supply alarm status
0x01: normal
0x02: Power supply 1 alarm
0x03: Power supply 2 alarm
1
164 to 255
Reserved
To retrieve status data of an H3C device, the controller sends a request that carries the set attribute single command to that device. This request populates the first two bytes of the data portion with 0x0000, and the succeeding bytes as follows:
Third byte
Fourth byte
Fifth byte
Data category (Table)
Data category (node)/index
Data subcategory (node)/subindex
00
01
02
03
04
05
06
n(ff)
00
01
n
01 (Device information)
Vendor name
Device type
Vendor address
Phone number
Product name
Additional information
02 (Port information)
First port
Second port
Third port
Fourth port
Fifth port
Sixth port
Nth port
03 (RSTP information)
Global info
Ring network info on the first port
Ring network info on the second port
Ring network info on the third port
Ring network info on the fourth port
Ring network info on the fifth port
Ring network info on the sixth port
Ring network info on the Nth port
04 (ERPS ring network info)
Global info
First ERPS ring info
Second ERPS ring info
Third ERPS ring info
Fourth ERPS ring info
Fifth ERPS ring info
Sixth ERPS ring info
Nth ERPS ring info
05 (ERPS ring instance info)
Global info
Nth ERPS ring info
First instance info
Nth instance info
06 (RRPP domain info)
Global info
First RRPP domain info
Second RRPP domain info
Third RRPP domain info
Fourth RRPP domain info
Fifth RRPP domain info
Sixth RRPP domain info
Nth RRPP domain info
07 (RRPP ring network info)
Global info
First RRPP ring information
Nth RRPP ring information
After receiving the request packet with the get attribute single command, the H3C device replies to the controller with a response packet. The value starting from position 05 in the response packet is as follows:
(byte)
Name
Value
Data length (bytes)
00
Whether the request is successful or failed
0x0000: Successful.
0xFFFF: Failed
2
02
Serial number
33
35
Boot ROM version
64
99
Current running software version
64
163
Device IP address
192.168.0.1
(C0 A8 00 01)
4
167
MAC address of the MPU
4
171
Device bridge MAC address
6
177
Power supply 1 status information
0x00: Power off
0x01: Power on
1
178
Power supply 2 status information
0x00: Power off
0x01: Power on
1
179
CPU usage in percentage (long term)
4
183
CPU usage in percentage (short term)
4
187
Total memory (bytes)
4
191
Free memory (bytes)
4
195
Device uptime (minutes)
8
203 to 255
Reserved
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
Port name
64
66
Port state
·     0x00: Disabled
·     0x01: Up
·     0x02: Down
1
67
Port speed
1
68
Duplex mode
·     0x01: Half
·     0x02: Full
·     0x03: Auto
1
69
Flow control enabling status
·     0x00: Off
·     0x01: On
1
70
Received packet count
8
78
Received byte count
8
86
Transmitted packet count
8
94
Transmitted byte count
8
102
Received unicast packet count
8
110
Received multicast packet count
8
118
Received broadcast packet count
8
126
Transmitted unicast packet count
8
134
Transmitted multicast packet count
8
142
Transmitted broadcast packet count
8
150
Received pause frame count
8
158
Transmitted pause frame count
8
166
Received CRC error packet count
8
174 to 255
Reserved
RSTP global information
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
RSTP global enabling status
·     0—Disabled
·     1—Enabled
2
04
Root bridge ID
8 byes
8
12
Bridge ID
8 byes
8
20
Priority
Value range: 0 to 61440
4
24
Hello time at which the root device sends BPDUs
Value range: 1 to10
4
28
Max age of BPDUs
Value range: 6 to 40
4
32
Forward delay
Value range: 4 to 30
4
RSTP port information
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
RSTP port enabling status
·     0—Disabled
·     1—Enabled
2
04
Port priority
Value range: 0 to 240
4
08
Path cost
Value range: 0 to 200000000
4
12
Port role
·     0—Disabled port
·     1—Alternate port
·     2—Backup port
·     3—Root port
·     4—Designated port
·     5—Master port
4
16
Port state
·     1—Discarding
·     2—Learning
·     3—Forwarding
4
ERPS ring network global information
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
ERPS global enabling status
0: disable
1: enable
2
ERPS ring information
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
ERPS ring ID
Value range: 1 to 8
2
04
ERPS ring member port 0
Port name
64
68
RPS ring member port 1
Port name
64
132
ERPS ring instance list
64
197-255
Reserved
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
0: disable
1: enable
2
(byte)
Name
Value
Length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
ERPS ring ID
Value range: 1 to 8
2
04
ERPS instance ID
Value range: 1 to 64
2
06
ERPS instance enabling status
0: The instance is not enabled.
1: The instance is enabled.
1
07
Control VLAN of the ERPS instance
Value range: 2 to 4094
2
09
Node role
String.
·     Owner: Owner node.
·     Neighbor: Neighbor
·     Interconnection: Interconnection node
·     Normal: Normal node
32
41
Node state
String.
·     Idle: Stable state when all non-RPL links are available
·     Protection: State when a non-RPL link is faulty. In this state, the RPL link is unblocked to forward traffic. All nodes enter the protection state after a node enters the protection state.
·     MS: State when traffic paths are manually switched.
·     FS: State when traffic paths are forcibly switched.
·     Pending: Transitional state between two states.
·     -: ERPS is disabled globally or for the instance.
32
73
Port name.
64
137
Role of ERPS ring member port 0
String.
·     RPL
·     Non-RPL
8
145
State of ERPS ring member port 0
String.
·     Blocked
·     Up
·     Down
8
153
ERPS ring member port 1
Port name.
64
217
Role of ERPS ring member port 1
Port role. String.
·     RPL
·     Non-RPL
8
225
State of ERPS ring member port 1
Port state. String.
·     Blocked
·     Up
·     Down
8
233-255
Reserved
RRPP ring network global information
Data portion
position (byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
RRPP global enabling status
0: disable
1: enable
2
Data portion
position (byte)
Name
Value
Data length (bytes)
(byte)
Data name
Data example
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
RRPP domain ID
Value range: 1 to 8
2
04
Control VLAN of the RRPP domain
2
06
Ring list of the RRPP domain
128
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
0: Disabled
1: Enabled
2
(byte)
Name
Value
Data length (bytes)
00
0x0000: Successful.
0xFFFF: Failed
2
02
RRPP domain ID
Value range: 1 to 8
2
04
RRPP ring ID
2
06
Ring level
·     0—Primary ring
·     1—subring
1
07
RRPP ring enabling status
·     0—RRPP ring is not enabled.
·     1— RRPP ring is enabled.
1
08
Node role
·     0—Transit node
·     1—Master node
·     2—Edge node
·     3—Assistant edge node
1
09
RRPP ring state
·     0—Completed
·     1—Failed
·     2—LinkUp
·     3—LinkDown
·     4—PreForward
·     5—LinkUpNotify
·     6—LinkDnNotify
·     7—PreForwardNotify
·     8—Unknown
1
10
RRPP ring primary port
Value range: 1 to 128
4
14
RRPP ring primary port status
Port status:
·     0—down.
·     1—up.
·     2—blocked.
1
15
RRPP ring secondary port
4
19
RRPP ring secondary port status
Port status:
·     0—down.
·     1—up.
·     2—blocked.
1
20
RRPP ring edge port
4
24
RRPP ring edge port status
Port status:
·     0—down.
·     1—up.
·     2—blocked.
1
To set the port status of an H3C device, the controller sends a request that carries the set attribute single command to the device. This request populates the first two bytes of the data portion with 0x0100, and the succeeding bytes as follows:
Status item
Position in the data portion of the message (byte)
3
Status for ports 1 to 4
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
21
22
23
24
25
26
27
28
29
30
31
32
33
34
The port status of each port is represented by 2 bits. The binary value 01 represents to enable the port, 10 represents to disable the port, and 00 and 11 represent to keep the port status unchanged.
A CIP connection must be established between an H3C device and the controller to initiate implicit communication. The connection parameters need to be configured as follows:
Transport type
Class ID
Instance ID
Connection point
Data size
Input
4
3
101 0x65
200 bytes
Output
102 0x66
40 bytes
The output message in implicit communication contains the desired status for each port. The Input message contains the current status and alarm information of each port.
Output message
The output message describes the desired status for each port.
Status item
Transaction number. The device will process the output message (2 bytes) only when the transaction number is updated. If the transaction number is not updated, the succeeding message portion will not be read and analyzed.
Run idle buf, which is set to 0 (4bytes). The output length set in the connection point starts counting from below. The data location is also counted from below.
0
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
21
22
23
24
25
26
27
28
29
30
31
32 to 39
Reserved
The first 32 bytes of the message indicate the desired status for the ports, with 2 bits for each port. 01 represents to enable the port, 10 represents to disable the port, 00 and 11 represent to keep the port status unchanged. The last eight bytes are reserved.
Input message
The input message describes the current status of ports.
Status item
Transaction number. The device will process the output message (2 bytes) only when the transaction number is updated. If the transaction number is not updated, the succeeding message portion will not be read and analyzed. The output length set in the connection point starts counting from below. The data location is also counted from below.
0
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
21
22
23
24
25
26
27
28
29
30
31
The status of each port is represented by 2 bits:
·     00: Disabled
·     01: Up
·     10: Down
Name
Value
Data length (bytes)
32
Port 1 alarm status
0x00: Disabled
0x01: Normal
0x02: Alarm
33
Port 2 alarm status
0x00: Disabled
0x01: Normal
0x02: Alarm
34
0x01: Normal
0x02: Alarm
160
0x01: Normal
0x02: Alarm
161
CPU alarm status
0x01: Normal
0x02: Alarm
162
Memory alarm status
0x01: Normal
0x02: Alarm
163
0x01: Normal
164 to 199
Reserved