07-Layer 3—IP Services Configuration Guide
HomeSupportConfigure & DeployConfiguration GuidesH3C MSR1000[2600][3600] Routers Configuration Guides(V9)-R9119-6W10007-Layer 3—IP Services Configuration Guide
03-DHCP configuration
03-DHCP configuration 799.02 KB
DHCP overview·· 1
DHCP network model 1
DHCP address allocation· 1
Allocation mechanisms· 1
IP address allocation process· 2
IP address lease extension· 2
DHCP message format 3
DHCP options· 4
Common DHCP options· 4
Custom DHCP options· 4
Vendor-specific option (Option 43) 5
Relay agent option (Option 82) 6
Option 184· 6
Protocols and standards· 7
Configuring the DHCP server 8
About DHCP server 8
DHCP address assignment mechanisms· 8
Principles for selecting an address pool 9
IP address allocation sequence· 10
DHCP server tasks at a glance· 10
Creating a DHCP user class· 11
Configuring an address pool on the DHCP server 11
DHCP address pool tasks at a glance· 11
Creating a DHCP address pool 12
Specifying a primary subnet and multiple address ranges in a DHCP address pool 12
Specifying a primary subnet and multiple secondary subnets in a DHCP address pool 13
Configuring a static binding in a DHCP address pool 15
Configuring dynamic subnet allocation in a DHCP address pool 15
Specifying gateways for DHCP clients· 17
Specifying a domain name suffix for DHCP clients· 18
Specifying DNS servers for DHCP clients· 18
Specifying WINS servers and NetBIOS node type for DHCP clients· 18
Specifying BIMS server for DHCP clients· 19
Specifying the configuration file for DHCP client automatic configuration· 19
Specifying a server for DHCP clients· 20
Configuring Option 184 parameters for DHCP clients· 20
Customizing DHCP options· 21
Applying a DHCP address pool to a VPN instance· 23
Configuring the DHCP user class whitelist 23
Configuring IP address reservation· 24
Enabling random IP address allocation· 24
Binding gateways to DHCP server's MAC address· 25
Advertising subnets that are assigned to clients· 26
Applying an address pool to an interface· 26
Configuring a DHCP policy for dynamic assignment 27
Allocating different IP addresses to DHCP clients with the same MAC· 28
Enabling DHCP· 28
Enabling the DHCP server on an interface· 29
Configuring IP address conflict detection· 29
Enabling handling of Option 82· 29
Configuring DHCP server compatibility· 30
Configuring the DHCP server to always broadcast responses· 30
Disabling Option 60 encapsulation in DHCP replies· 30
Enabling the DHCP server to return a DHCP-NAK message upon client notions of incorrect IP addresses  31
Configuring the DHCP server to ignore BOOTP requests· 31
Configuring the DHCP server to send BOOTP responses in RFC 1048 format 31
Setting the DSCP value for DHCP packets sent by the DHCP server 32
Configuring DHCP binding auto backup· 32
Enabling client offline detection on the DHCP server 33
Configuring SNMP notifications for the DHCP server 33
Enabling DHCP logging on the DHCP server 34
Verifying and maintaining DHCP server 34
Verifying DHCP server configuration· 34
Displaying IP address allocation information on the DHCP server 35
Clearing IP address allocation information on the DHCP server 35
Displaying and clearing DHCP server statistics· 35
DHCP server configuration examples· 36
Example: Configuring static IP address assignment 36
Example: Configuring dynamic IP address assignment 37
Example: Configuring DHCP user class· 39
Example: Configuring DHCP user class whitelist 41
Example: Configuring primary and secondary subnets· 42
Example: Customizing DHCP option· 43
Troubleshooting DHCP server configuration· 45
Failure to obtain a non-conflicting IP address· 45
Configuring the DHCP relay agent 46
About DHCP relay agent 46
DHCP relay agent operation· 46
DHCP relay agent support for Option 82· 47
DHCP relay agent support for MCE· 47
DHCP relay agent tasks at a glance· 47
Enabling DHCP· 48
Enabling the DHCP relay agent on an interface· 48
Specifying DHCP servers· 49
Specifying DHCP servers on a relay agent 49
Configuring a DHCP address pool on a DHCP relay agent 49
Specifying the DHCP server selecting algorithm·· 50
Configuring the DHCP relay agent security features· 51
Enabling the DHCP relay agent to record relay entries· 51
Enabling periodic refresh of dynamic relay entries· 52
Enabling DHCP starvation attack protection· 52
Enabling DHCP server proxy on the DHCP relay agent 53
Enabling client offline detection on the DHCP relay agent 53
Configuring the DHCP relay agent to release an IP address· 54
Configuring DHCP relay agent support for Option 82· 54
Setting the DSCP value for DHCP packets sent by the DHCP relay agent 55
Specifying the DHCP relay agent address for the giaddr field· 56
Manually specifying the DHCP relay agent address for the giaddr field· 56
Configuring smart relay to specify the DHCP relay agent address for the giaddr field· 56
Specifying the source IP address for relayed DHCP requests· 57
Discarding DHCP requests received from SRv6 tunnels· 58
Configuring support for forwarding DHCP replies based on MAC address table· 58
Configuring the DHCP relay agent to always unicast relayed DHCP responses· 59
Configuring forwarding DHCP replies based on Option 82· 59
Verifying and maintaining DHCP relay agent 60
Verifying DHCP relay agent configuration· 60
Displaying and clearing DHCP relay entries· 60
Displaying MAC address check entries on the DHCP relay agent 61
Displaying and clearing packet statistics on the DHCP relay agent 61
DHCP relay agent configuration examples· 61
Example: Configuring basic DHCP relay agent 61
Example: Configuring Option 82· 62
Example: Configuring DHCP server selection· 63
Troubleshooting DHCP relay agent configuration· 64
Failure of DHCP clients to obtain configuration parameters through the DHCP relay agent 64
Configuring the DHCP client 65
About DHCP client 65
Restrictions and guidelines: DHCP client configuration· 65
DHCP client tasks at a glance· 65
Enabling the DHCP client on an interface· 65
Configuring a DHCP client ID for an interface· 66
Enabling duplicated address detection· 66
Setting the DSCP value for DHCP packets sent by the DHCP client 67
Verifying and maintaining DHCP client 67
DHCP client configuration examples· 67
Example: Configuring DHCP client 67
DHCP client configuration examples (on an AP) 69
Example: Configuring DHCP client 69
Configuring the BOOTP client 71
About BOOTP client 71
BOOTP client application· 71
Obtaining an IP address dynamically· 71
Protocols and standards· 71
Configuring an interface to use BOOTP for IP address acquisition· 71
Verifying and maintaining BOOTP client 72
BOOTP client configuration examples· 72
Example: Configuring BOOTP client 72
DHCP overview
DHCP network model
The Dynamic Host Configuration Protocol (DHCP) provides a framework to assign configuration information to network devices.
Figure 1 shows a typical DHCP application scenario where the DHCP clients and the DHCP server reside on the same subnet. The DHCP clients can also obtain configuration parameters from a DHCP server on another subnet through a DHCP relay agent. For more information about the DHCP relay agent, see "Configuring the DHCP relay agent."
Figure 1 A typical DHCP application
DHCP supports the following allocation mechanisms:
·     Static allocation—The network administrator assigns an IP address to a client, such as a WWW server, and DHCP conveys the assigned address to the client.
·     Automatic allocation—DHCP assigns a permanent IP address to a client.
·     Dynamic allocation—DHCP assigns an IP address to a client for a limited period of time, which is called a lease. Most DHCP clients obtain their addresses in this way.
Figure 2 IP address allocation process
As shown in Figure 2, a DHCP server assigns an IP address to a DHCP client in the following process:
1.     The client broadcasts a DHCP-DISCOVER message to locate a DHCP server.
2.     Each DHCP server offers configuration parameters such as an IP address to the client in a DHCP-OFFER message. The sending mode of the DHCP-OFFER is determined by the flag field in the DHCP-DISCOVER message. For more information, see "DHCP message format."
3.     If the client receives multiple offers, it accepts the first received offer, and broadcasts it in a DHCP-REQUEST message to formally request the IP address. (IP addresses offered by other DHCP servers can be assigned to other clients.)
4.     All DHCP servers receive the DHCP-REQUEST message. However, only the server selected by the client does one of the following operations:
¡     Returns a DHCP-ACK message to confirm that the IP address has been allocated to the client.
¡     Returns a DHCP-NAK message to deny the IP address allocation.
After receiving the DHCP-ACK message, the client verifies the following details before using the assigned IP address:
·     The assigned IP address is not in use. To verify this, the client broadcasts a gratuitous ARP packet. The assigned IP address is not in use if no response is received within the specified time.
·     The assigned IP address is not on the same subnet as any IP address in use on the client.
Otherwise, the client sends a DHCP-DECLINE message to the server to request an IP address again.
A dynamically assigned IP address has a lease. When the lease expires, the IP address is reclaimed by the DHCP server. To continue using the IP address, the client must extend the lease duration.
When about half of the lease duration elapses, the DHCP client unicasts a DHCP-REQUEST to the DHCP server to extend the lease. Depending on the availability of the IP address, the DHCP server returns one of the following messages:
·     A DHCP-ACK unicast confirming that the client's lease duration has been extended.
·     A DHCP-NAK unicast denying the request.
If the client receives no reply, it broadcasts another DHCP-REQUEST message for lease extension when about seven-eighths of the lease duration elapses. Again, depending on the availability of the IP address, the DHCP server returns either a DHCP-ACK unicast or a DHCP-NAK unicast.
DHCP message format
Figure 3 shows the DHCP message format. DHCP uses some of the fields in significantly different ways. The numbers in parentheses indicate the size of each field in bytes.
Figure 3 DHCP message format
·     op—Message type defined in options field. 1 = REQUEST, 2 = REPLY
·     htype, hlen—Hardware address type and length of the DHCP client.
·     hops—Number of relay agents a request message traveled.
·     xid—Transaction ID, a random number chosen by the client to identify an IP address allocation.
·     secs—Filled in by the client, the number of seconds elapsed since the client began address acquisition or renewal process. This field is reserved and set to 0.
·     flags—The leftmost bit is defined as the BROADCAST (B) flag. If this flag is set to 0, the DHCP server sent a reply back by unicast. If this flag is set to 1, the DHCP server sent a reply back by broadcast. The remaining bits of the flags field are reserved for future use.
·     ciaddr—Client IP address if the client has an IP address that is valid and usable. Otherwise, set to zero. (The client does not use this field to request an IP address to lease.)
·     yiaddr—Your IP address. It is an IP address assigned by the DHCP server to the DHCP client.
·     siaddr—Server IP address, from which the client obtained configuration parameters.
·     giaddr—Gateway IP address. It is the IP address of the first relay agent to which a request message travels.
·     chaddr—Client hardware address.
·     sname—Server host name, from which the client obtained configuration parameters.
·     file—Boot file (also called system software image) name and path information, defined by the server to the client.
·     options—Optional parameters field that is variable in length. Optional parameters include the message type, lease duration, subnet mask, domain name server IP address, and WINS IP address.
DHCP options
DHCP extends the message format as an extension to BOOTP for compatibility. DHCP uses the options field to carry information for dynamic address allocation and provide additional configuration information for clients.
Figure 4 DHCP option format
Common DHCP options
The following are common DHCP options:
·     Option 3—Router option. It specifies the gateway address to be assigned to the clients.
·     Option 6—DNS server option. It specifies the DNS server IP address to be assigned to the clients.
·     Option 33—Static route option. It specifies a list of classful static routes (the destination addresses in these static routes are classful) that a client should add into its routing table. If both Option 33 and Option 121 exist, Option 33 is ignored.
·     Option 51—IP address lease option.
·     Option 53—DHCP message type option. It identifies the type of the DHCP message.
·     Option 55—Parameter request list option. It is used by a DHCP client to request specified configuration parameters. The option includes values that correspond to the parameters requested by the client.
·     Option 60—Vendor class identifier option. A DHCP client uses this option to identify its vendor. A DHCP server uses this option to distinguish DHCP clients, and assigns IP addresses to them.
·     Option 66—TFTP server name option. It specifies the TFTP server domain name to be assigned to the clients.
·     Option 67—Boot file name option. It specifies the boot file name to be assigned to the client.
·     Option 121—Classless route option. It specifies a list of classless static routes (the destination addresses in these static routes are classless) that a client should add into its routing table. If both Option 33 and Option 121 exist, Option 33 is ignored.
·     Option 150—TFTP server IP address option. It specifies the TFTP server IP address to be assigned to the clients.
For more information about DHCP options, see RFC 2132 and RFC 3442.
Custom DHCP options
Some options, such as Option 43, Option 82, and Option 184, have no standard definitions in RFC 2132.
Option 43 function
DHCP servers and clients use Option 43 to exchange vendor-specific configuration information.
The DHCP client can obtain the following information through Option 43:
·     ACS parameters, including the ACS URL, username, and password.
·     Service provider identifier, which is acquired by the CPE from the DHCP server and sent to the ACS for selecting vender-specific configurations and parameters. For more information about CPE and ACS, see CWMP configuration in Network Management and Monitoring Configuration Guide.
·     PXE server address, which is used to obtain the boot file or other control information from the PXE server.
·     AC address, which is used by an AP to obtain the boot file or other control information from the AC.
Option 43 format
Figure 5 Option 43 format
Network configuration parameters are carried in different sub-options of Option 43 as shown in Figure 5.
·     Sub-option type—The field value can be 0x01 (ACS parameter sub-option), 0x02 (service provider identifier sub-option), or 0x80 (PXE server address sub-option).
·     Sub-option length—Excludes the sub-option type and sub-option length fields.
·     Sub-option value—The value format varies by sub-option.
Sub-option value field format
·     ACS parameter sub-option value field—Includes the ACS URL, username, and password separated by spaces (hexadecimal number 20) as shown in Figure 6.
Figure 6 ACS parameter sub-option value field
·     Service provider identifier sub-option value field—Includes the service provider identifier.
·     PXE server address sub-option value field—Includes the PXE server type that can only be 0, the server number that indicates the number of PXE servers contained in the sub-option, and server IP addresses, as shown in Figure 7.
Figure 7 PXE server address sub-option value field
Option 82 is the relay agent option. It records the location information about the DHCP client. When a DHCP relay agent or DHCP snooping device receives a client's request, it adds Option 82 to the request and sends it to the server.
The administrator can use Option 82 to locate the DHCP client and further implement security control and accounting. The DHCP server can use Option 82 to provide individual configuration policies for the clients.
Option 82 can include a maximum of 255 sub-options and must include a minimum of one sub-option. Option 82 supports two sub-options: sub-option 1 (Circuit ID) and sub-option 2 (Remote ID). Option 82 has no standard definition. Its padding formats vary by vendor.
·     Circuit ID has the following padding modes:
¡     String padding mode—Includes a character string specified by the user.
¡     Normal padding mode—Includes the VLAN ID and interface number of the interface that receives the client's request.
¡     Verbose padding mode—Includes the access node identifier specified by the user, and the VLAN ID, interface number and interface type of the interface that receives the client's request.
·     Remote ID has the following padding modes:
¡     Normal padding mode—Includes the MAC address of the DHCP relay agent interface or the MAC address of the DHCP snooping device that receives the client's request.
¡     Sysname padding mode—Includes the name of the device. To set the device name, use the sysname command in system view.
Option 184
Option 184 is a reserved option. You can define the parameters in the option as needed. The device supports Option 184 carrying voice related parameters, so a DHCP client with voice functions can get voice parameters from the DHCP server.
Option 184 has the following sub-options:
·     Sub-option 1—Specifies the IP address of the primary network calling processor. The primary processor acts as the network calling control source and provides program download services. For Option 184, you must define sub-option 1 to make other sub-options take effect.
·     Sub-option 2—Specifies the IP address of the backup network calling processor. DHCP clients contact the backup processor when the primary one is unreachable.
·     Sub-option 3—Specifies the voice VLAN ID and the result whether the DHCP client takes this VLAN as the voice VLAN.
·     Sub-option 4—Specifies the failover route that includes the IP address and the number of the target user. A SIP VoIP user uses this IP address and number to directly establish a connection to the target SIP user when both the primary and backup calling processors are unreachable.
·     RFC 2131, Dynamic Host Configuration Protocol
·     RFC 2132, DHCP Options and BOOTP Vendor Extensions
·     RFC 1542, Clarifications and Extensions for the Bootstrap Protocol
·     RFC 3046, DHCP Relay Agent Information Option
·     RFC 3442, The Classless Static Route Option for Dynamic Host Configuration Protocol (DHCP) version 4
About DHCP server
A DHCP server manages a pool of IP addresses and client configuration parameters. It selects an IP address and configuration parameters from the address pool and allocates them to a requesting DHCP client.
Configure the following address assignment mechanisms as needed:
·     Static address allocation—Manually bind the MAC address or ID of a client to an IP address in a DHCP address pool. When the client requests an IP address, the DHCP server assigns the IP address in the static binding to the client.
·     Dynamic address allocation—Specify IP address ranges in a DHCP address pool. Upon receiving a DHCP request, the DHCP server dynamically selects an IP address from the matching IP address range in the address pool.
You can specify IP address ranges in an address pool by using either of the following methods:
·     Method 1A primary subnet being divided into multiple address ranges in an address pool
·     Method 2A primary subnet and multiple secondary subnets in an address pool
An address range includes a common IP address range and IP address ranges for DHCP user classes.
Upon receiving a DHCP request, the DHCP server finds a user class matching the client and selects an IP address in the address range of the user class for the client. A user class can include multiple matching rules, and a client matches the user class as long as it matches any of the rules. In address pool view, you can specify different address ranges for different user classes.
The DHCP server selects an IP address for a client by performing the following steps:
1.     DHCP server compares the client against DHCP user classes in the order they are configured.
2.     If the client matches a user class, the DHCP server selects an IP address from the address range of the user class.
3.     If the matching user class has no assignable addresses, the DHCP server compares the client against the next user class. If all the matching user classes have no assignable addresses, the DHCP server selects an IP address from the common address range.
4.     If the DHCP client does not match any DHCP user class, the DHCP server selects an address in the IP address range specified by the address range command. If the address range has no assignable IP addresses or it is not configured, the address allocation fails.
All address ranges must belong to the primary subnet. If an address range does not reside on the primary subnet, DHCP cannot assign the addresses in the address range.
The DHCP server selects an IP address from the primary subnet first. If there is no assignable IP address on the primary subnet, the DHCP server selects an IP address from secondary subnets in the order they are configured.
The DHCP server observes the following principles to select an address pool for a client:
1.     If there is an address pool where an IP address is statically bound to the MAC address or ID of the client, the DHCP server selects this address pool and assigns the statically bound IP address and other configuration parameters to the client.
2.     If the receiving interface has a DHCP policy and the DHCP client matches a user class, the DHCP server selects the address pool that is bound to the matching user class. If no matching user class is found, the server assigns an IP address and other parameters from the default DHCP address pool. If no default address pool is specified or the default address pool does not have assignable IP addresses, the address assignment fails.
3.     If the receiving interface has an address pool applied, the DHCP server selects an IP address and other configuration parameters from this address pool.
4.     If the above conditions are not met, the DHCP server selects an address pool depending on the client location.
¡     Client on the same subnet as the server—The DHCP server compares the IP address of the receiving interface with the primary subnets of all address pools.
-     If a match is found, the server selects the address pool with the longest-matching primary subnet.
-     If no match is found, the DHCP server compares the IP address with the secondary subnets of all address pools. The server selects the address pool with the longest-matching secondary subnet.
¡     Client on a different subnet than the server—The DHCP server compares the IP address in the giaddr field of the DHCP request with the primary subnets of all address pools.
For example, two address pools 1.1.1.0/24 and 1.1.1.0/25 are configured but not applied to any DHCP server's interfaces.
·     If the IP address of the receiving interface is 1.1.1.1/25, the DHCP server selects the address pool 1.1.1.0/25. If the address pool has no available IP addresses, the DHCP server will not select the other pool and the address allocation will fail.
·     If the IP address of the receiving interface is 1.1.1.130/25, the DHCP server selects the address pool 1.1.1.0/24.
To ensure correct address allocation, keep the IP addresses used for dynamic allocation on one of the subnets:
·     Clients on the same subnet as the server—Subnet where the DHCP server receiving interface resides.
·     Clients on a different subnet than the serverSubnet where the first DHCP relay interface that faces the clients resides.
As a best practice, configure a minimum of one matching primary subnet in your network. Otherwise, the DHCP server selects only the first matching secondary subnet for address allocation. If the network has more DHCP clients than the assignable IP addresses in the secondary subnet, not all DHCP clients can obtain IP addresses.
The DHCP server selects an IP address for a client in the following sequence:
1.     IP address statically bound to the client's MAC address or ID.
2.     IP address that was ever assigned to the client.
3.     IP address designated by the Option 50 field in the DHCP-DISCOVER message sent by the client.
Option 50 is the Requested IP Address option. The client uses this option to specify the wanted IP address in a DHCP-DISCOVER message. The content of Option 50 is user defined.
4.     First assignable IP address found in the way discussed in "DHCP address assignment mechanisms" and "Principles for selecting an address pool."
5.     IP address that was a conflict or passed its lease duration. If no IP address is assignable, the server does not respond.
·     If a client moves to another subnet, the DHCP server selects an IP address in the address pool matching the new subnet. It does not assign the IP address that was once assigned to the client.
·     Conflicted IP addresses can be assigned to other DHCP clients only after the addresses are in conflict for an hour.
To configure the DHCP server, perform the following tasks:
1.     (Optional.) Creating a DHCP user class
2.     Configuring an address pool on the DHCP server
3.     (Optional.) Modifying the address pool selection method on the DHCP server
¡     Applying an address pool to an interface
¡     Configuring a DHCP policy for dynamic assignment
4.     (Optional.) Allocating different IP addresses to DHCP clients with the same MAC
5.     Enabling DHCP
6.     Enabling the DHCP server on an interface
7.     (Optional.) Configuring advanced DHCP features
¡     Configuring IP address conflict detection
¡     Enabling handling of Option 82
¡     Configuring DHCP server compatibility
¡     Setting the DSCP value for DHCP packets sent by the DHCP server
¡     Configuring DHCP binding auto backup
¡     Enabling client offline detection on the DHCP server
8.     (Optional.) Configuring SNMP notification and logging
¡     Configuring SNMP notifications for the DHCP server
¡     Enabling DHCP logging on the DHCP server
The DHCP server classifies DHCP users into different user classes according to the hardware address, option information, or the giaddr field in the received DHCP requests. The server allocates IP addresses and configuration parameters to DHCP clients in different user classes.
2.     Create a DHCP user class and enter DHCP user class view.
dhcp class class-name
3.     Configure a match rule for the DHCP user class.
By default, no match rule is configured for a DHCP user class.
To configure a DHCP address pool, perform the following tasks:
1.     Creating a DHCP address pool
2.     Specifying IP address ranges in a DHCP address pool
In one DHCP address pool, dynamic allocation methods cannot be configured together, but static and dynamic address allocations (excluding dynamic subnet allocation) can be both implemented.
¡     Specifying a primary subnet and multiple address ranges in a DHCP address pool
¡     Specifying a primary subnet and multiple secondary subnets in a DHCP address pool
¡     Configuring a static binding in a DHCP address pool
¡     Configuring dynamic subnet allocation in a DHCP address pool
3.     Specifying other configuration parameters to be assigned to DHCP clients
¡     Specifying gateways for DHCP clients
¡     Specifying a domain name suffix for DHCP clients
¡     Specifying DNS servers for DHCP clients
¡     Specifying WINS servers and NetBIOS node type for DHCP clients
¡     Specifying BIMS server for DHCP clients
¡     Specifying the configuration file for DHCP client automatic configuration
¡     Specifying a server for DHCP clients
¡     Configuring Option 184 parameters for DHCP clients
¡     Customizing DHCP options
4.     (Optional.) Applying a DHCP address pool to a VPN instance
5.     (Optional.) Configuring the DHCP user class whitelist
6.     (Optional.) Configuring IP address reservation
7.     (Optional.) Enabling random IP address allocation
8.     (Optional.) Binding gateways to DHCP server's MAC address
9.     (Optional.) Advertising subnets that are assigned to clients
2.     Create a DHCP address pool and enter its view.
dhcp server ip-pool pool-name
Some scenarios need to classify DHCP clients on the same subnet into different address groups. To meet this need, you can configure DHCP user classes and specify different address ranges for the classes. The clients matching a user class can then get the IP addresses of an address range. In addition, you can specify a common address range for the clients that do not match any user class. If no common address range is specified, such clients fail to obtain IP addresses.
If there is no need to classify clients, you do not need to configure DHCP user classes or their address ranges.
·     If you execute the network or address range command multiple times for the same address pool, the most recent configuration takes effect.
·     You can repeat the class command to specify different address ranges for different user classes.
·     You can repeat the forbidden-ip command or the forbidden-ip-range command to exclude multiple address ranges from DHCP allocation.
·     The forbidden-ip and forbidden-ip-range commands take effect only on the IP pool for which the commands are executed, and the dhcp server forbidden-ip command takes effect on all IP pools configured for the device.
·     You can use class range to modify an existing address range, and the new address range can include IP addresses that are being used by clients. Upon receiving a lease extension request for such an IP address, the DHCP server allocates a new IP address to the requesting client. But the original lease continues aging in the address pool, and will be released when the lease duration is reached. To release such lease without waiting for its timeout, execute the reset dhcp server ip-in-use command.
2.     Enter DHCP address pool view.
3.     Specify the primary subnet in the address pool.
network network-address [ mask-length | mask mask ] [ export-route [ preference preference | tag tag ] * ]
By default, no primary subnet is specified.
4.     (Optional.) Specify the common address range.
address range start-ip-address [ end-ip-address ] [ vpn-instance vpn-instance-name ]
By default, no IP address range is specified.
5.     (Optional.) Specify an IP address range for a DHCP user class.
By default, no IP address range is specified for a user class.
The DHCP user class must already be created by using the dhcp class command.
6.     (Optional.) Set the address lease duration.
expired { allow-hint | { day day [ hour hour [ minute minute [ second second ] ] ] | unlimited } [ allow-hint ] }
The default setting is 1 day.
7.     (Optional.) Exclude the specified IP addresses in the address pool from dynamic allocation.
forbidden-ip ip-address&<1-8>
By default, except for the DHCP server IP address, all IP addresses in the IP pool are assignable.
8.     (Optional.) Exclude an IP range from DHCP allocation in the IP pool.
forbidden-ip-range start-ip-address [ end-ip-address ]
9.     (Optional.) Exclude the specified IP addresses from automatic allocation in system view.
a.     Return to system view.
b.     Exclude the specified IP addresses from automatic allocation globally.
By default, except for the IP address of the DHCP server interface, IP addresses in all address pools are assignable.
If an address pool has a primary subnet and multiple secondary subnets, the server assigns IP addresses on a secondary subnet when the primary subnet has no assignable IP addresses.
IP addresses specified by the forbidden-ip command or the forbidden-ip-range command are not assignable in the IP pool for which the command is executed, but are assignable in other address pools.
IP addresses specified by the dhcp server forbidden-ip command are not assignable in any address pool.
3.     Specify the primary subnet.
You can specify only one primary subnet in each address pool. If you execute the network command multiple times, the most recent configuration takes effect.
4.     (Optional.) Specify a secondary subnet.
network network-address [ mask-length | mask mask ] secondary
By default, no secondary subnet is specified.
You can specify a maximum of 32 secondary subnets in one address pool.
5.     (Optional.) Return to address pool view.
Setting the lease duration for dynamically allocation IP addresses
3.     Set the address lease duration.
Excluding IP addresses from dynamic allocation
3.     Exclude the specified IP addresses from dynamic allocation.
To exclude multiple address ranges from the address pool, repeat this step.
4.     (Optional.) Exclude an IP range from DHCP allocation in the address pool.
5.     (Optional.) Exclude the specified IP addresses from dynamic allocation in system view.
b.     Exclude the specified IP addresses from dynamic allocation globally.
To exclude multiple address ranges globally, repeat this step.
Some DHCP clients, such as a WWW server, need fixed IP addresses. To provide a fixed IP address for a client, you can statically bind the MAC address or ID of the client to an IP address in a DHCP address pool. When the client requests an IP address, the DHCP server assigns the IP address in the static binding to the client.
·     The IP address of a static binding cannot be the address of the DHCP server interface. Otherwise, an IP address conflict occurs and the bound client cannot obtain an IP address correctly.
·     Multiple interfaces on the same device might all use DHCP to request a static IP address. In this case, use client IDs rather than the device's MAC address to identify the interfaces. Otherwise, IP address allocation will fail.
3.     Configure a static binding.
One IP address can be bound to only one client MAC or client ID. You cannot modify bindings that have been created. To change the binding for a DHCP client, you must delete the existing binding first.
4.     (Optional.) Set the lease duration for the IP address.
By default, the lease duration is 1 day.
This feature applies to the forwarding-control separation solution. In a forwarding-control separation network, a control plane (CP) issues table entries to data planes (DPs) through OpenFlow channels and exchanges protocol messages with DPs through VXLAN tunnels. The CP performs authentication and authorization for users, and the DPs assign users to different VXLAN networks and forward traffic for users.
Figure 8 Dynamic subnet allocation
As shown in Figure 8, the CP connects to DPs through VXLAN tunnels and acts as the DHCP server. The CP subnets the primary network according to the mask length in the subnet mask-length mask-length command.
After you configure this feature, the CP performs the following operations to ensure flexible and efficient IP address allocation:
·     Allocates a subnet to a DP when a user accesses the network through the DP, and assigns IP addresses on the subnet to users on the DP. Subnet allocated to a DP is based on the DP address or the VXLAN ID.
·     Issues the subnet route to the DP to which the subnet is allocated. After the routing convergence, users form external networks can access users on the DP.
·     Reclaims an idle subnet when all users on the subnet go offline.
2.     Create a DHCP address pool for dynamic subnet allocation and enter its view.
dhcp server ip-pool pool-name subnet-alloc
3.     Specify the primary subnet for dynamic allocation.
network network-address [ mask-length | mask mask ] [ export-route ]
By default, no subnet is specified in a DHCP address pool.
4.     (Optional.) Specify the subnet allocation mode.
subnet alloc-mode { dp-address | vxlan-id }
By default, subnets are allocated based on VXLAN IDs.
5.     Specify the mask length for the dynamically allocated subnets.
By default, no mask length is specified for dynamically allocated subnets.
6.     (Optional.) Set the delay time for the DHCP server to reclaim idle subnets.
subnet idle-time time
By default, the delay time for the DHCP server to reclaim idle subnets is 1 second.
When all users on a subnet go offline, the CP reclaims the idle subnet. When the users come online again, the CP assigns them IP addresses in another subnet. To avoid assigning IP addresses of different subnets to a user that comes online and goes offline frequently, increase the delay time for the CP to reclaim idle subnets.
7.     (Optional.) Disable the DHCP server from issuing routes for an IP address pool that supports dynamic subnet allocation.
subnet export-route disable
By default, the DHCP server issues routes for IP address pools that support dynamic subnet allocation.
In a CUPS scenario, the CP acts as the DHCP server. When the CP and UP are colocated on the same device, only the network route rather than the subnet routes can be advertised to reduce the number of routes. In this case, you can disable the DHCP server from issuing routes for IP address pools that support dynamic subnet allocation. Then, execute the network export-route command to advertise the network route to the UP.
DHCP clients send packets destined for other networks to a gateway. The DHCP server can assign the gateway address to the DHCP clients.
You can specify gateway addresses in each address pool on the DHCP server. A maximum of 64 gateways can be specified in DHCP address pool view or secondary subnet view.
The DHCP server assigns gateway addresses to clients on a secondary subnet in the following ways:
·     If gateways are specified in both address pool view and secondary subnet view, DHCP assigns those specified in the secondary subnet view.
·     If gateways are specified in address pool view but not in secondary subnet view, DHCP assigns those specified in address pool view.
3.     Specify gateways.
gateway-list ip-address&<1-64>
By default, no gateway is specified.
4.     (Optional.) Specify gateways in secondary subnet view.
a.     Enter secondary subnet view.
b.     Specify gateways.
You can specify a domain name suffix in a DHCP address pool on the DHCP server. With this suffix assigned, the client only needs to input part of a domain name, and the system adds the domain name suffix for name resolution. For more information about DNS, see DNS configuration in Layer 3—IP Services Configuration Guide.
3.     Specify a domain name suffix.
domain-name domain-name
To access hosts on the Internet through domain names, a DHCP client must contact a DNS server to resolve names. You can specify up to eight DNS servers in a DHCP address pool.
3.     Specify DNS servers.
dns-list ip-address&<1-8>
By default, no DNS server is specified.
A Microsoft DHCP client using NetBIOS protocol must contact a WINS server for name resolution.
In addition, you must specify one of the following NetBIOS node types to approach name resolution:
·     b (broadcast)-node—A b-node client sends the destination name in a broadcast message. The destination returns its IP address to the client after receiving the message.
·     p (peer-to-peer)-node—A p-node client sends the destination name in a unicast message to the WINS server. The WINS server returns the destination IP address.
·     m (mixed)-node—An m-node client broadcasts the destination name. If it receives no response, it unicasts the destination name to the WINS server to get the destination IP address.
·     h (hybrid)-node—An h-node client unicasts the destination name to the WINS server. If it receives no response, it broadcasts the destination name to get the destination IP address.
By default, no DHCP address pool exists.
3.     Specify WINS servers.
nbns-list ip-address&<1-8>
By default, no WINS server is specified.
This step is optional for b-node. You can specify a maximum of eight WINS servers for such clients in one DHCP address pool.
4.     Specify the NetBIOS node type.
By default, no NetBIOS node type is specified.
Perform this task to provide the BIMS server IP address, port number, and shared key for the clients. The DHCP clients contact the BIMS server to get configuration files and perform software upgrade and backup.
3.     Specify the BIMS server IP address, port number, and shared key.
By default, no BIMS server information is specified.
Automatic configuration enables a device to automatically obtain a set of configuration settings at startup. The server-based automatic configuration requires the cooperation of the DHCP server and file server (TFTP or HTTP server). The device uses the obtained parameters to contact the file server to get the configuration file. For more information about automatic configuration, see Fundamentals Configuration Guide.
Specifying the configuration file on a TFTP file server
3.     Specify the IP address or the name of a TFTP server.
¡     Specify the IP address of the TFTP server.
By default, no TFTP server IP address is specified.
¡     Specify the name of the TFTP server.
By default, no TFTP server name is specified.
4.     Specify the configuration file name.
bootfile-name bootfile-name
By default, no configuration file name is specified.
Specifying the URL of the configuration file on an HTTP file server
3.     Specify the URL of the configuration file.
bootfile-name url
By default, no configuration file URL is specified.
Some DHCP clients need to obtain configuration information from a server, such as a TFTP server. You can specify the IP address of that server. The DHCP server sends the server's IP address to DHCP clients along with other configuration information.
3.     Specify the IP address of a server.
next-server ip-address
By default, no server is specified.
To assign calling parameters to DHCP clients with voice service, you must configure Option 184 on the DHCP server. For more information about Option 184, see "Option 184."
3.     Specify the IP address of the primary network calling processor.
voice-config ncp-ip ip-address
By default, no primary network calling processor is specified.
After you configure this command, the other Option 184 parameters take effect.
4.     (Optional.) Specify the IP address of the backup server.
voice-config as-ip ip-address
By default, no backup network calling processor is specified.
5.     (Optional.) Configure the voice VLAN.
voice-config voice-vlan vlan-id { disable | enable }
By default, no voice VLAN is configured.
6.     (Optional.) Specify the failover IP address and dialer string.
voice-config fail-over ip-address dialer-string
By default, no failover IP address or dialer string is specified.
DHCP option customization applications
You can customize DHCP options for the following purposes:
·     Add newly released options.
·     Add options for which the vendor defines the contents, for example, Option 43.
·     Add options for which the CLI does not provide a dedicated configuration command. For example, you can use the option 4 ip-address 1.1.1.1 command to define the time server address 1.1.1.1 for DHCP clients.
·     Add all option values if the actual requirement exceeds the limit for a dedicated option configuration command. For example, the dns-list command can specify up to eight DNS servers. To specify more than eight DNS servers, you must use the option 6 command to define all DNS servers.
Common DHCP options
Table 1 lists common DHCP options and their parameters.
Table 1 Common DHCP options
Option
Option name
Corresponding command
Recommended parameter in the option command
3
Router Option
gateway-list
ip-address
6
Domain Name Server Option
dns-list
ip-address
15
Domain Name
domain-name
ascii
44
NetBIOS over TCP/IP Name Server Option
nbns-list
ip-address
46
NetBIOS over TCP/IP Node Type Option
netbios-type
hex
66
TFTP server name
tftp-server
ascii
67
Boot file name
bootfile-name
ascii
43
Vendor Specific Information
N/A
hex
Use caution when customizing DHCP options because the configuration might affect DHCP operation.
You can customize a DHCP option in a DHCP address pool
You can customize a DHCP option in a DHCP option group, and specify the option group for a user class in an address pool. A DHCP client in the user class will obtain the option configuration.
Customizing a DHCP option in a DHCP address pool
3.     Customize a DHCP option.
By default, no DHCP option is customized in a DHCP address pool.
DHCP options specified in DHCP option groups take precedence over those specified in DHCP address pools.
Customizing a DHCP option in a DHCP option group
2.     Create a DHCP option group and enter DHCP option group view.
By default, no DHCP option is customized in a DHCP option group.
If multiple DHCP option groups have the same option, the server selects the option in the DHCP option group first matching the user class.
4.     Return to system view.
5.     Enter DHCP address pool view.
6.     Specify the DHCP option group for the DHCP user class.
By default, no DHCP option group is specified for a DHCP user class.
If a DHCP address pool is applied to a VPN instance, the DHCP server assigns IP addresses in this address pool to clients in the VPN instance. Addresses in this address pool will not be assigned to clients on the public network.
The DHCP server can obtain the VPN instance to which a DHCP client belongs from the following information:
·     The client's VPN information stored in authentication modules.
·     The VPN information of the DHCP server's interface that receives DHCP packets from the client.
If both VPN instances can be obtained, the VPN information from authentication modules takes priority over the VPN information of the receiving interface.
An MCE acting as the DHCP server can assign IP addresses not only to clients on public networks, but also to clients on private networks. The IP address ranges of public and private networks or those of private networks on the DHCP server cannot overlap. For more information about MCE, see MPLS Configuration Guide.
3.     Apply the address pool to a VPN instance.
By default, the address pool is not applied to any VPN instance.
The DHCP user class whitelist allows the DHCP server to process requests only from clients on the DHCP user class whitelist.
The whitelist does not take effect on clients who request static IP addresses, and the server always processes their requests.
3.     Enable the DHCP user class whitelist.
verify class
By default, the DHCP user class whitelist is disabled.
4.     Add DHCP user classes to the DHCP user class whitelist.
valid class class-name&<1-8>
By default, no DHCP user class is on the DHCP user class whitelist.
The IP address reservation feature enables the DHCP server to reserve IP addresses for DHCP clients that are going offline. When a client goes offline, the DHCP server reserves the client IP as an expired lease. When the client comes online again, the DHCP server assigns the client the IP address in the reserved lease.
You can configure the reservation mode, reservation time and the maximum number of expired IP addresses reserved in a DHCP address pool to ensure the same IP address allocation.
A DHCP server can reserve IP addresses for DHCP clients in the following modes:
·     Reservation based on client IDs—The DHCP server records the IP-to-client ID bindings for online clients. When these clients come online again, the server assigns them the IP addresses in the bindings according to their client IDs.
·     Reservation based on client MAC addresses—The DHCP server records the IP-to-MAC bindings for online clients. When these clients come online again, the server assigns them the IP addresses in the bindings according to their MAC addresses.
Disable the IP address reservation feature if you want to the DHCP server to reclaim IP addresses immediately after clients go offline.
If multiple DHCP clients use the same client ID on your network, configure the DHCP server to reserve IP addresses based on client MAC addresses.
3.     Enable IP address reservation.
reserve expired-ip enable
By default, IP address reservation is enabled.
4.     Configure the IP address reservation mode.
reserve expired-ip mode { client-id | mac } [ limit limit-number | time time ] *
By default, with IP address reservation enabled, the DHCP server reserves IP addresses based on client IDs.
By default, the DHCP server tries to allocate the same IP address as the previous allocation to the same user.
With this feature enabled, the DHCP server will allocate a new IP address to a user every time the user acquires an IP address. This feature is applicable to the scenarios where a user must obtain a different IP address for each IP address acquisition.
This feature takes effect only after IP address reservation is enabled.
3.     Enable random IP address allocation.
allocate-new-ip enable
By default, random IP address allocation is disabled.
This feature enables the DHCP server to assign different gateway IP addresses to DHCP clients. In addition, the DHCP server uses the gateway IP addresses and the server's MAC address to reply to ARP requests from the clients.
As shown in Figure 9, the DHCP server is configured on the access device that provides access for clients of different service types, such as broadband, IPTV, and IP telephone. The clients of different types obtain IP addresses on different subnets. For the clients to access the network, the access interface typically has no IP address configured. You must bind the gateways to the DHCP server's MAC address when specifying gateways for the DHCP clients.
Figure 9 Network diagram
The gateway binding feature can take effect on an address pool that is applied to a VPN instance only when the VPN instance exists.
3.     Bind the gateways to the device's MAC address.
gateway-list ip-address&<1-64> export-route
By default, gateways are not bound to any MAC address.
This feature enables the route management module to advertise subnets assigned to DHCP clients. This feature achieves symmetric routing for traffic of the same host.
As shown in Figure 10, Router A and Router B act as both the DHCP server and the BRAS device. The BRAS devices send accounting packets to the RADIUS server. To enable the BRAS devices to collect correct accounting information for each RADIUS user, configure the DHCP server to advertise subnets assigned to clients. The upstream and downstream traffic of a RADIUS user will pass through the same BRAS device.
Figure 10 Network diagram
The subnet advertising feature can take effect on an address pool that is applied to a VPN instance only when the VPN instance exists.
3.     Advertise subnets assigned to DHCP clients.
network network-address [ mask-length | mask mask ] export-route [ preference preference | tag tag ] * [ secondary ]
By default, the subnets assigned to DHCP clients are not advertised.
Perform this task to apply a DHCP address pool to an interface.
Upon receiving a DHCP request from the interface, the DHCP server performs address allocation in the following ways:
·     If a static binding is found for the client, the server assigns the static IP address and configuration parameters from the address pool that contains the static binding.
·     If no static binding is found for the client, the server uses the address pool applied to the interface for address and configuration parameter allocation.
2.     Enter interface view.
3.     Apply an address pool to the interface.
By default, no address pool is applied to an interface.
If the applied address pool does not exist, the DHCP server fails to perform dynamic address allocation.
In a DHCP policy, each DHCP user class has a bound DHCP address pool. Clients matching different user classes obtain IP addresses and other parameters from different address pools. The DHCP policy must be applied to the interface that acts as the DHCP server. When receiving a DHCP request, the DHCP server compares the packet against the user classes in the order that they are configured.
·     If a matching user class is found and the bound address pool has assignable IP addresses, the server assigns an IP address and other parameters from the address pool. If the address pool does not have assignable IP addresses, the address assignment fails.
·     If no match is found, the server assigns an IP address and other parameters from the default DHCP address pool. If no default address pool is specified or the default address pool does not have assignable IP addresses, the address assignment fails.
For successful address assignment, make sure the applied DHCP policy and the bound address pools exist.
A DHCP policy take effect only after it is applied to an interface.
2.     Create a DHCP policy and enter DHCP policy view.
dhcp policy policy-name
3.     Specify a DHCP address pool for a DHCP user class.
By default, no address pool is specified for a user class.
4.     Specify the default DHCP address pool.
default ip-pool pool-name
By default, no default address pool is specified.
5.     Return to system view.
6.     Enter interface view.
7.     Apply the DHCP policy to the interface.
dhcp apply-policy policy-name
By default, no DHCP policy is applied to an interface.
Traditionally, the DHCP server identifies DHCP clients based on their MAC addresses. Each MAC address can be bound to only one IP address. However, DHCP clients that have the same MAC address exist in the network, and each client requires an IP address. You can enable this feature to allocate different IP addresses to such clients.
This feature enables the DHCP server to use the following methods to identify the DHCP clients that have the same MAC address:
·     If a DHCP snooping device or a DHCP relay agent exists, you must enable the DHCP snooping device or the DHCP relay agent to support Option 82. The DHCP server identifies a DHCP client by the MAC address of the client and the Option 82 in the DHCP request.
·     If no DHCP snooping device or DHCP relay agent is on the network, the DHCP server identifies a DHCP client by the combination of the following information:
¡     The MAC address of the client.
¡     The interface name in the DHCP request.
¡     The VLAN information of the receiving interface.
The feature does not take effect in a PPPoE network.
2.     Enable allocation of different IP addresses to DHCP clients with the same MAC address.
dhcp server multi-ip per-mac enable
By default, allocation of different IP addresses to DHCP clients with the same MAC address is disabled.
Enabling DHCP
You must enable DHCP to make other DHCP configurations take effect.
2.     Enable DHCP.
dhcp enable
By default, DHCP is disabled.
Perform this task to enable the DHCP server on an interface. Upon receiving a DHCP request on the interface, the DHCP server assigns the client an IP address and other configuration parameters from a DHCP address pool.
3.     Enable the DHCP server on the interface.
dhcp select server
By default, the DHCP server is enabled on the interface.
Before assigning an IP address, the DHCP server pings that IP address.
·     If the server receives a response within the specified period, it selects and pings another IP address.
·     If it receives no response, the server continues to ping the IP address until the maximum number of ping packets are sent. If still no response is received, the server assigns the IP address to the requesting client. The DHCP client uses gratuitous ARP to perform IP address conflict detection.
2.     (Optional.) Set the maximum number of ping packets to be sent for conflict detection.
The default setting is one.
To disable IP address conflict detection, set the value to 0.
3.     (Optional.) Set the ping timeout time.
The default setting is 500 ms.
Perform this task to enable the DHCP server to handle Option 82. Upon receiving a DHCP request that contains Option 82, the DHCP server adds Option 82 into the DHCP response.
If you disable the DHCP to handle Option 82, it does not add Option 82 into the response message.
You must enable handling of Option 82 on both the DHCP server and the DHCP relay agent to ensure correct processing for Option 82. For information about enabling handling of Option 82 on the DHCP relay agent, see "Configuring DHCP relay agent support for Option 82."
2.     Enable the server to handle Option 82.
dhcp server relay information enable
By default, handling of Option 82 is enabled.
Perform this task to enable the DHCP server to support DHCP clients that are incompliant with RFC.
By default, the DHCP server broadcasts a response only when the broadcast flag in the DHCP request is set to 1. You can configure the DHCP server to ignore the broadcast flag and always broadcast a response. This feature is useful when some clients set the broadcast flag to 0 but do not accept unicast responses.
The DHCP server always unicasts a response in the following situations, regardless of whether this feature is configured or not:
·     The DHCP request is from a DHCP client that has an IP address (the ciaddr field is not 0).
·     The DHCP request is forwarded by a DHCP relay agent from a DHCP client (the giaddr field is not 0).
2.     Enable the DHCP server to always broadcast all responses.
dhcp server always-broadcast
By default, the DHCP server reads the broadcast flag to decide whether to broadcast or unicast a response.
If one or more DHCP clients cannot resolve Option 60, disable the DHCP server from encapsulating Option 60 in DHCP replies. If you do not disable the capability, the DHCP server encapsulates Option 60 in a DHCP reply in the following situations:
·     The received DHCP packet contains Option 60.
·     Option 60 is configured for the address pool.
2.     Disable the DHCP server from encapsulating Option 60 in DHCP replies.
dhcp server reply-exclude-option60
By default, the DHCP server can encapsulate Option 60 in DHCP replies.
A DHCP client can send a DHCP-REQUEST message directly or upon receiving a DHCP-OFFER message. Upon receiving the request, the DHCP server will check if the client notion of its IP address is correct. If the requested IP address is different from the allocated one or has no matching lease record, the DHCP server remains silent by default. After the allocated IP address lease for the client expires, the DHCP server will make response to request from the client.
This feature enables the DHCP server to return DHCP-NAK messages if the client notions of their IP addresses are incorrect. After receiving the DHCP-NAK message, the DHCP client will request an IP address again.
2.     Enable the DHCP server to return a DHCP-NAK message if the client notions of their IP addresses are incorrect.
dhcp server request-ip-address check
The DHCP server does not return a DHCP-NAK message if the client notions of their IP addresses are incorrect.
The lease duration of the IP addresses obtained by the BOOTP clients is unlimited. For some scenarios that do not allow unlimited leases, you can configure the DHCP server to ignore BOOTP requests.
2.     Configure the DHCP server to ignore BOOTP requests.
dhcp server bootp ignore
By default, the DHCP server processes BOOTP requests.
Not all BOOTP clients can send requests that are compatible with RFC 1048. By default, the DHCP server does not process the Vend field of RFC 1048-incompliant requests but copies the Vend field into responses.
This feature enables the DHCP server to fill the Vend field in RFC 1048-compliant format in DHCP responses to RFC 1048-incompliant requests sent by BOOTP clients.
2.     Enable the DHCP server to send BOOTP responses in RFC 1048 format to the RFC 1048-incompliant BOOTP requests.
dhcp server bootp reply-rfc-1048
By default, the DHCP server directly copies the Vend field of such requests into the responses.
The DSCP value of a packet specifies the priority level of the packet and affects the transmission priority of the packet.
2.     Set the DSCP value for DHCP packets sent by the DHCP server.
dhcp dscp dscp-value
By default, the DSCP value in DHCP packets sent by the DHCP server is 56.
The auto backup feature saves bindings to a backup file and allows the DHCP server to download the bindings from the backup file at the server reboot. The bindings include the lease bindings and conflicted IP addresses. They cannot survive a reboot on the DHCP server.
The DHCP server does not provide services during the download process. If a connection error occurs during the process and cannot be repaired in a short amount of time, you can terminate the download operation. Manual interruption allows the DHCP server to provide services without waiting for the connection to be repaired.
2.     Configure the DHCP server to back up the bindings to a file.
By default, the DHCP server does not back up the DHCP bindings.
With this command executed, the DHCP server backs up its bindings immediately and runs auto backup.
3.     (Optional.) Manually save the DHCP bindings to the backup file.
dhcp server database update now
4.     (Optional.) Set the waiting time after a DHCP binding change for the DHCP server to update the backup file.
By default, the DHCP server waits 300 seconds to update the backup file after a DHCP binding change. If no DHCP binding changes, the backup file is not updated.
5.     (Optional.) Terminate the download of DHCP bindings from the backup file.
dhcp server database update stop
This command only triggers one termination.
The client offline detection feature reclaims an assigned IP address and deletes the binding entry when the ARP entry for the IP address ages out.
The feature does not function if an ARP entry is manually deleted.
3.     Enable client offline detection.
dhcp client-detect
By default, client offline detection is disabled on the DHCP server.
Perform this task to configure the DHCP module to send SNMP notifications to report the following DHCP server events:
·     Exhaustion or recovery of a DHCP address pool.
·     Usage threshold violation in a DHCP address pool.
·     IP address allocation success rate threshold violation.
The SNMP notifications are sent to the SNMP module. For the SNMP notifications to be sent correctly, you must also configure SNMP. For more information about SNMP configuration, see Network Management and Monitoring Configuration Guide.
For a DHCP address pool usage threshold violation, the DHCP module also sends a log message to the information center. For log messages to be sent correctly, you must also configure the information center. For information about the information center configuration, see System Management Configuration Guide.
2.     Enable SNMP notifications for the DHCP server.
snmp-agent trap enable dhcp server [ address-exhaust | allocated-ip | ip-in-use ]
By default, SNMP notifications are enabled for the DHCP server.
3.     (Optional.) Set the IP address allocation success rate threshold.
dhcp server allocated-ip threshold threshold-value
By default, no SNMP notification is sent for an IP address allocation success rate threshold violation.
4.     Enter DHCP address pool view.
5.     (Optional.) Set the DHCP address pool usage threshold.
The default threshold is 100%.
The DHCP logging feature enables the DHCP server to generate DHCP logs and send them to the information center. For information about the log destination and output rule configuration in the information center, see System Management Configuration Guide.
As a best practice, disable this feature if the log generation affects the device performance or reduces the address allocation efficiency. For example, this situation might occur when a large number of clients frequently come online or go offline.
2.     Enable DHCP logging.
dhcp log enable
By default, DHCP logging is disabled.
Verifying and maintaining DHCP server
Verifying DHCP server configuration
·     Display information about DHCP address pools.
display dhcp server pool [ pool-name | vpn-instance vpn-instance-name ] [ subnet-alloc ]
·     Display information about DHCP binding auto backup.
display dhcp server database
Displaying IP address allocation information on the DHCP server
·     Display information about assigned IP addresses.
display dhcp server ip-in-use [ [ dp-address ip-address | ip ip-address | subnet network-address mask-length | vxlan vxlan-id ] [ vpn-instance vpn-instance-name ] | pool pool-name ]
·     Display information about assignable IP addresses.
·     Display information about lease-expired IP addresses.
display dhcp server expired dp-address ip-address | ip ip-address | mac mac-address | vxlan vxlan-id  | pool pool-name ] [ verbose ]
·     Display information about IP address conflicts.
display dhcp server conflict [ dp-address ip-address | ip ip-address | vxlan vxlan-id ] [ vpn-instance vpn-instance-name ]
Clearing IP address allocation information on the DHCP server
A restart of the DHCP server or execution of the reset dhcp server ip-in-use command deletes all lease information. The DHCP server denies any DHCP request for lease extension, and the client must request an IP address again.
Perform clear tasks in user view.
·     Clear information about assigned IP addresses.
·     Clear information about lease-expired IP addresses.
reset dhcp server expired [ [ ip ip-address ] [ vpn-instance vpn-instance-name ]| pool pool-name ]
·     Clear information about IP address conflicts.
Displaying and clearing DHCP server statistics
To display DHCP server statistics, execute the following command in any view:
To clear DHCP server statistics, execute the following command in user view:
DHCP server configuration examples
Example: Configuring static IP address assignment
As shown in Figure 11, Router A (DHCP server) assigns a static IP address, a DNS server address, and a gateway address to Router B (DHCP client) and Router C (BOOTP client).
The client ID of the interface GigabitEthernet 0/0/1 on Router B is 0030-3030-662e-6532-3030-2e30-3030-322d-4574-6865-726e-6574.
The MAC address of the interface GigabitEthernet 0/0/1 on Router C is 000f-e200-01c0.
Figure 11 Network diagram
1.     Specify an IP address for GigabitEthernet 0/0/1 on Router A.
[RouterA] interface gigabitethernet 0/0/1
[RouterA-GigabitEthernet0/0/1] ip address 10.1.1.1 25
[RouterA-GigabitEthernet0/0/1] quit
2.     Configure the DHCP server:
# Create DHCP address pool 0.
[RouterA] dhcp server ip-pool 0
# Configure a static binding for Router B.
[RouterA-dhcp-pool-0] static-bind ip-address 10.1.1.5 25 client-identifier 0030-3030-662e-6532-3030-2e30-3030-322d-4574-6865-726e-6574
# Configure a static binding for Router C.
[RouterA-dhcp-pool-0] static-bind ip-address 10.1.1.6 25 hardware-address 000f-e200-01c0
# Specify the DNS server address and the gateway address.
[RouterA-dhcp-pool-0] dns-list 10.1.1.2
[RouterA-dhcp-pool-0] gateway-list 10.1.1.126
[RouterA-dhcp-pool-0] quit
[RouterA]
# Enable DHCP.
[RouterA] dhcp enable
# Enable the DHCP server on GigabitEthernet 0/0/1.
[RouterA-GigabitEthernet0/0/1] dhcp select server
# Verify that Router B can obtain IP address 10.1.1.5 and all other network parameters from Router A. (Details not shown.)
# Verify that Router C can obtain IP address 10.1.1.6 and all other network parameters from Router A. (Details not shown.)
# On the DHCP server, display the IP addresses assigned to the clients.
[RouterA] display dhcp server ip-in-use
IP address       Client identifier/    Lease expiration      Type
                 Hardware address
10.1.1.5         0030-3030-662e-6532-  Jan 21 14:27:27 2014  Static(C)
                 4574-6865-726e-6574
10.1.1.6         000f-e200-01c0        Unlimited             Static(C)
Example: Configuring dynamic IP address assignment
As shown in Figure 12, the DHCP server (Router A) assigns IP addresses to clients on subnet 10.1.1.0/24, which is subnetted into 10.1.1.0/25 and 10.1.1.128/25.
Configure DHCP server on Router A to implement the following assignment scheme.
Table 2 Assignment scheme
DHCP clients
IP address
Lease
Other configuration parameters
Clients connected to GigabitEthernet 0/0/1
IP addresses on subnet 10.1.1.0/25
10 days and 12 hours
·     Gateway: 10.1.1.126/25
·     DNS server: 10.1.1.2/25
·     Domain name: aabbcc.com
·     WINS server: 10.1.1.4/25
Clients connected to GigabitEthernet 0/0/2
IP addresses on subnet 10.1.1.128/25
Five days
·     Gateway: 10.1.1.254/25
Figure 12 Network diagram
1.     Specify IP addresses for interfaces. (Details not shown.)
# Exclude the IP addresses of the DNS server, WINS server, and gateways from dynamic allocation.
[RouterA] dhcp server forbidden-ip 10.1.1.2
[RouterA] dhcp server forbidden-ip 10.1.1.4
[RouterA] dhcp server forbidden-ip 10.1.1.126
[RouterA] dhcp server forbidden-ip 10.1.1.254
# Configure DHCP address pool 1 to assign IP addresses and other configuration parameters to clients on subnet 10.1.1.0/25.
[RouterA] dhcp server ip-pool 1
[RouterA-dhcp-pool-1] network 10.1.1.0 mask 255.255.255.128
[RouterA-dhcp-pool-1] expired day 10 hour 12
[RouterA-dhcp-pool-1] domain-name aabbcc.com
[RouterA-dhcp-pool-1] dns-list 10.1.1.2
[RouterA-dhcp-pool-1] gateway-list 10.1.1.126
[RouterA-dhcp-pool-1] nbns-list 10.1.1.4
[RouterA-dhcp-pool-1] quit
# Configure DHCP address pool 2 to assign IP addresses and other configuration parameters to clients on subnet 10.1.1.128/25.
[RouterA] dhcp server ip-pool 2
[RouterA-dhcp-pool-2] network 10.1.1.128 mask 255.255.255.128
[RouterA-dhcp-pool-2] expired day 5
[RouterA-dhcp-pool-2] domain-name aabbcc.com
[RouterA-dhcp-pool-2] dns-list 10.1.1.2
[RouterA-dhcp-pool-2] gateway-list 10.1.1.254
[RouterA-dhcp-pool-2] quit
# Enable DHCP.
# Enable the DHCP server on GigabitEthernet 0/0/1 and GigabitEthernet 0/0/2.
[RouterA] interface gigabitethernet 0/0/2
[RouterA-GigabitEthernet0/0/2] dhcp select server
[RouterA-GigabitEthernet0/0/2] quit
# Verify that clients on subnets 10.1.1.0/25 and 10.1.1.128/25 can obtain correct IP addresses and all other network parameters from Router A. (Details not shown.)
                 Hardware address
10.1.1.3         0031-3865-392e-6262-  Jan 14 22:25:03 2015  Auto(C)
                 3363-2e30-3230-352d-
                 4745-302f-30
10.1.1.5         0031-fe65-4203-7e02-  Jan 14 22:25:03 2015  Auto(C)
                 3063-5b30-3230-4702-
                 620e-712f-5e
10.1.1.130       3030-3030-2e30-3030-  Jan 9 10:45:11 2015   Auto(C)
                 662e-3030-3033-2d45-
                 7568-6572-1e
10.1.1.131       3030-0020-fe02-3020-  Jan 9 10:45:11 2015   Auto(C)
                 7052-0201-2013-1e02
                 0201-9068-23
10.1.1.132       2020-1220-1102-3021-  Jan 9 10:45:11 2015   Auto(C)
                 7e52-0211-2025-3402
                 0201-9068-9a
10.1.1.133       2021-d012-0202-4221-  Jan 9 10:45:11 2015   Auto(C)
                 8852-0203-2022-55e0
                 3921-0104-31
Example: Configuring DHCP user class
As shown in Figure 13, the DHCP relay agent (Router A) forwards DHCP packets between DHCP clients and the DHCP server (Router B). Enable Router A to handle Option 82 so that it can add Option 82 in DHCP requests and then forward them to the DHCP server.
Configure the address allocation scheme as follows:
Assign IP addresses
To clients
10.10.1.2 to 10.10.1.10
The DHCP request contains Option 82.
10.10.1.11 to 10.10.1.26
The hardware address in the request is six bytes long and begins with aabb-aabb-aab.
Router B assigns the DNS server address 10.10.1.20/24 and the gateway address 10.10.1.254/24 to clients on subnet 10.10.1.0/24.
Figure 13 Network diagram
1.     Specify IP addresses for the interfaces on the DHCP server. (Details not shown.)
2.     Configure DHCP:
# Create DHCP user class tt and configure a match rule to match DHCP requests that contain Option 82.
<RouterB> system-view
[RouterB] dhcp class tt
[RouterB-dhcp-class-tt] if-match rule 1 option 82
[RouterB-dhcp-class-tt] quit
# Create DHCP user class ss and configure a match rule to match DHCP requests in which the hardware address is six bytes long and begins with aabb-aabb-aab.
[RouterB] dhcp class ss
[RouterB-dhcp-class-ss] if-match rule 1 hardware-address aabb-aabb-aab0 mask ffff-ffff-fff0
[RouterB-dhcp-class-ss] quit
# Create DHCP address pool aa.
[RouterB] dhcp server ip-pool aa
# Specify the subnet for dynamic allocation.
[RouterB-dhcp-pool-aa] network 10.10.1.0 mask 255.255.255.0
# Specify the address range for dynamic allocation.
[RouterB-dhcp-pool-aa] address range 10.10.1.2 10.10.1.100
# Specify the address range for user class tt.
[RouterB-dhcp-pool-aa] class tt range 10.10.1.2 10.10.1.10
# Specify the address range for user class ss.
[RouterB-dhcp-pool-aa] class ss range 10.10.1.11 10.10.1.26
# Specify the gateway address and the DNS server address.
[RouterB-dhcp-pool-aa] gateway-list 10.10.1.254
[RouterB-dhcp-pool-aa] dns-list 10.10.1.20
[RouterB-dhcp-pool-aa] quit
# Enable DHCP and configure the DHCP server to handle Option 82.
[RouterB] dhcp enable
[RouterB] dhcp server relay information enable
# Enable the DHCP server on the interface GigabitEthernet0/0/1.
[RouterB] interface gigabitethernet 0/0/1
[RouterB-GigabitEthernet0/0/1] dhcp select server
[RouterB-GigabitEthernet0/0/1] quit
# Verify that clients matching the DHCP user classes can obtain IP addresses in the specified ranges and all other configuration parameters from the DHCP server. (Details not shown.)
[RouterB] display dhcp server ip-in-use
                 Hardware address
10.10.1.2        0031-3865-392e-6262-  Jan 14 22:25:03 2015  Auto(C)
                 4745-302f-30
10.10.1.11       aabb-aabb-aab1        Jan 14 22:25:03 2015  Auto(C)
Example: Configuring DHCP user class whitelist
As shown in Figure 14, configure the DHCP user class whitelist to allow the DHCP server to assign IP addresses to clients whose hardware addresses are six bytes long and begin with aabb-aabb.
Figure 14 Network diagram
2.     Configure DHCP:
# Create DHCP user class ss and configure a match rule to match DHCP requests in which the hardware address is six bytes long and begins with aabb-aabb.
[RouterB-dhcp-class-ss] if-match rule 1 hardware-address aabb-aabb-0000 mask ffff-ffff-0000
[RouterB-dhcp-pool-aa] network 10.1.1.0 mask 255.255.255.0
# Enable the DHCP user class whitelist.
[RouterB-dhcp-pool-aa] verify class
# Add DHCP user class ss to the DHCP user class whitelist.
[RouterB-dhcp-pool-aa] valid class ss
# Enable DHCP.
# Verify that clients matching the DHCP user class can obtain IP addresses on subnet 10.1.1.0/24 from the DHCP server. (Details not shown.)
                 Hardware address
10.1.1.2         aabb-aabb-ab01        Jan 14 22:25:03 2015  Auto(C)
Example: Configuring primary and secondary subnets
As shown in Figure 15, the DHCP server (Router A) assigns IP addresses to DHCP clients in the LAN.
Configure two subnets in the address pool on the DHCP server: 10.1.1.0/24 as the primary subnet and 10.1.2.0/24 as the secondary subnet. The DHCP server selects an IP address from the secondary subnet when the primary subnet has no assignable addresses.
Router A assigns the following parameters:
·     The default gateway 10.1.1.254/24 to clients on subnet 10.1.1.0/24.
·     The default gateway 10.1.2.254/24 to clients on subnet 10.1.2.0/24.
Figure 15 Network diagram
[RouterA] dhcp server ip-pool aa
# Specify the primary subnet and the gateway address for dynamic allocation.
[RouterA-dhcp-pool-aa] network 10.1.1.0 mask 255.255.255.0
[RouterA-dhcp-pool-aa] gateway-list 10.1.1.254
# Specify the secondary subnet and the gateway address for dynamic allocation.
[RouterA-dhcp-pool-aa] network 10.1.2.0 mask 255.255.255.0 secondary
[RouterA-dhcp-pool-aa-secondary] gateway-list 10.1.2.254
[RouterA-dhcp-pool-aa-secondary] quit
[RouterA-dhcp-pool-aa] quit
# Enable DHCP.
# Configure the primary and secondary IP addresses of GigabitEthernet0/0/1, and enable the DHCP server on GigabitEthernet 0/0/1.
[RouterA-GigabitEthernet0/0/1] ip address 10.1.1.1 24
[RouterA-GigabitEthernet0/0/1] ip address 10.1.2.1 24 sub
# Verify that the DHCP server assigns clients IP addresses and gateway address from the secondary subnet when no assignable address is available from the primary subnet. (Details not shown.)
# On the DHCP server, display IP addresses assigned to the clients. The following is part of the command output.
                 Hardware address
10.1.1.2         0031-3865-392e-6262-  Jan 14 22:25:03 2015  Auto(C)
                 4745-302f-30
10.1.2.2         3030-3030-2e30-3030-  Jan 14 22:25:03 2015  Auto(C)
                 7568-6572-1e
Example: Customizing DHCP option
As shown in Figure 16, DHCP clients obtain IP addresses and PXE server addresses from the DHCP server (Router A). The subnet for address allocation is 10.1.1.0/24.
Assign PXE addresses
To clients
2.3.4.5 and 3.3.3.3
The hardware address in the request is six bytes long and begins with aabb-aabb.
1.2.3.4 and 2.2.2.2.
Other clients.
The DHCP server assigns PXE server addresses to DHCP clients through Option 43, a custom option. The formats of Option 43 and PXE server address sub-option are shown in Figure 5 and Figure 7. For example, the value of Option 43 configured in the DHCP address pool is 80 0B 00 00 02 01 02 03 04 02 02 02 02.
·     The number 80 is the value of the sub-option type.
·     The number 0B is the value of the sub-option length.
·     The numbers 00 00 are the value of the PXE server type.
·     The number 02 indicates the number of servers.
·     The numbers 01 02 03 04 02 02 02 02 indicate that the PXE server addresses are 1.2.3.4 and 2.2.2.2.
Figure 16 Network diagram
1.     Specify an IP address for GigabitEthernet 0/0/1. (Details not shown.)
[RouterA] dhcp class ss
[RouterA-dhcp-class-ss] if-match rule 1 hardware-address aabb-aabb-0000 mask ffff-ffff-0000
[RouterA-dhcp-class-ss] quit
# Create DHCP option group 1 and customize Option 43.
[RouterA] dhcp option-group 1
[RouterA-dhcp-option-group-1] option 43 hex 800B0000020203040503030303
# Specify the subnet for dynamic address allocation.
[RouterA-dhcp-pool-0] network 10.1.1.0 mask 255.255.255.0
# Customize Option 43.
[RouterA-dhcp-pool-0] option 43 hex 800B0000020102030402020202
# Associate DHCP user class ss with option group 1.
[RouterA-dhcp-pool-0] class ss option-group 1
# Enable DHCP.
# Verify that Router B can obtain an IP address on subnet 10.1.1.0/24 and the corresponding PXE server addresses from Router A. (Details not shown.)
                 Hardware address
Troubleshooting DHCP server configuration
Failure to obtain a non-conflicting IP address
Symptom
A client's IP address obtained from the DHCP server conflicts with an IP address of another host.
Solution
Another host on the subnet might have the same IP address.
To resolve the problem:
1.     Disable the client's network adapter or disconnect the client's network cable. Ping the IP address of the client from another host to check whether there is a host using the same IP address.
2.     If a ping response is received, the IP address has been manually configured on a host. Execute the dhcp server forbidden-ip command on the DHCP server to exclude the IP address from dynamic allocation.
3.     Enable the network adapter or connect the network cable, release the IP address, and obtain another one on the client. For example, to release the IP address and obtain another one on a Windows XP DHCP client:
a.     In Windows environment, execute the cmd command to enter the DOS environment.
b.     Enter ipconfig /release to relinquish the IP address.
c.     Enter ipconfig /renew to obtain another IP address.
Configuring the DHCP relay agent
About DHCP relay agent
The DHCP relay agent enables clients to get IP addresses and configuration parameters from a DHCP server on another subnet.
Figure 17 shows a typical application of the DHCP relay agent.
Figure 17 DHCP relay agent application
DHCP relay agent operation
The DHCP server and client interact with each other in the same way regardless of whether the relay agent exists. For the interaction details, see "IP address allocation process." The following only describes steps related to the DHCP relay agent:
1.     After receiving a DHCP-DISCOVER or DHCP-REQUEST broadcast message from a DHCP client, the DHCP relay agent processes the message as follows:
a.     Fills the giaddr field of the message with its IP address.
b.     Unicasts the message to the designated DHCP server.
2.     Based on the giaddr field, the DHCP server returns an IP address and other configuration parameters in a response.
3.     The relay agent conveys the response to the client.
Figure 18 DHCP relay agent operation
Option 82 records the location information about the DHCP client. It enables the administrator to perform the following tasks:
·     Locate the DHCP client for security and accounting purposes.
·     Assign IP addresses in a specific range to clients.
For more information about Option 82, see "Relay agent option (Option 82)."
If the DHCP relay agent supports Option 82, it handles DHCP requests by following the strategies described in Table 3.
If a response returned by the DHCP server contains Option 82, the DHCP relay agent removes the Option 82 before forwarding the response to the client.
Table 3 Handling strategies of the DHCP relay agent
If a DHCP request has…
Handling strategy
The DHCP relay agent…
Option 82
Drop
Drops the message.
Keep
Forwards the message without changing Option 82.
Replace
Forwards the message after replacing the original Option 82 with the Option 82 padded according to the configured padding format, padding content, and code type.
No Option 82
N/A
Forwards the message after adding Option 82 padded according to the configured padding format, padding content, and code type.
DHCP relay agent support for MCE
An MCE device acting as the DHCP relay agent can forward DHCP packets between a DHCP server and clients on either a public network or a private network. For more information about MCE, see MPLS Configuration Guide.
DHCP relay agent tasks at a glance
To configure a DHCP relay agent, perform the following tasks:
1.     Enabling DHCP
2.     Enabling the DHCP relay agent on an interface
3.     Specifying DHCP servers
4.     (Optional.) Configuring the DHCP relay agent security features
5.     (Optional.) Configuring the DHCP relay agent to release an IP address
6.     (Optional.) Configuring DHCP relay agent support for Option 82
7.     (Optional.) Setting the DSCP value for DHCP packets sent by the DHCP relay agent
8.     (Optional.) Specifying the DHCP relay agent address for the giaddr field
9.     (Optional.) Specifying the source IP address for relayed DHCP requests
10.     (Optional.) Discarding DHCP requests received from SRv6 tunnels
11.     (Optional.) Configuring support for forwarding DHCP replies based on MAC address table
12.     (Optional.) Configuring the DHCP relay agent to always unicast relayed DHCP responses
13.     (Optional.) Configuring forwarding DHCP replies based on Option 82
Enabling DHCP
You must enable DHCP to make other DHCP relay agent settings take effect.
2.     Enable DHCP.
dhcp enable
With the DHCP relay agent enabled, an interface forwards incoming DHCP requests to a DHCP server.
An IP address pool that contains the IP address of the DHCP relay interface must be configured on the DHCP server. Otherwise, the DHCP clients connected to the relay agent cannot obtain correct IP addresses.
3.     Enable the DHCP relay agent.
dhcp select relay
By default, when DHCP is enabled, an interface operates in the DHCP server mode.
Specifying DHCP servers on a relay agent
To improve availability, you can specify several DHCP servers on the DHCP relay agent. When the interface receives request messages from clients, the relay agent forwards them to all DHCP servers.
The IP address of any specified DHCP server must not reside on the same subnet as the IP address of the relay interface. Otherwise, the clients might fail to obtain IP addresses.
3.     Specify a DHCP server address on the relay agent.
dhcp relay server-address ip-address
By default, no DHCP server address is specified on the relay agent.
To specify multiple DHCP server addresses, repeat this step. You can specify a maximum of eight DHCP servers.
Configuring a DHCP address pool on a DHCP relay agent
This feature allows DHCP clients of the same type to obtain IP addresses and other configuration parameters from the DHCP servers specified in the matching DHCP address pool.
It applies to scenarios where the DHCP relay agent connects to clients of the same access type but classified into different types by their locations. In this case, the relay interface typically has no IP address configured. You can use the gateway-list command to specify gateway addresses for clients matching the same DHCP address pool and bind the gateway addresses to the device's MAC address.
Upon receiving a DHCP DISCOVER or REQUEST from a client that matches a DHCP address pool, the relay agent processes the packet as follows:
·     Fills the giaddr field of the packet with a specified gateway address.
·     Forwards the packet to all DHCP servers in the matching DHCP address pool.
The DHCP servers select a DHCP address pool according to the gateway address.
If PPPoE users are in the network, follow these restrictions and guidelines when you configure the DHCP address pool:
·     Enable the DHCP relay agent to record DHCP relay entries by using the dhcp relay client-information record command. When a PPPoE user goes offline, the DHCP relay agent can find a matching relay entry and send a DHCP-RELEASE message to the DHCP server. This mechanism ensures the DHCP server is aware of the releasing of the IP address in a timely manner.
·     The remote-server command also configures the device as a DHCP relay agent. You do not need to enable the DHCP relay agent by using the dhcp select relay command.
3.     DHCP address pool.
gateway-list ip-address&<1-64> [ export-route ]
By default, no gateway address is specified.
4.     Specify DHCP servers for the DHCP address pool.
remote-server ip-address&<1-8>
By default, no DHCP server is specified for the DHCP address pool.
You can specify a maximum of eight DHCP servers for one DHCP address pool for high availability.
Specifying the DHCP server selecting algorithm
The DHCP relay agent supports the polling and master-backup DHCP server selecting algorithms.
By default, the DHCP relay agent uses the polling algorithm. It forwards DHCP requests to all DHCP servers. The DHCP clients select the DHCP server from which the first received DHCP reply comes.
If the DHCP relay agent uses the master-backup algorithm, it forwards DHCP requests to the master DHCP server first. If the master DHCP server is not available, the relay agent forwards the subsequent DHCP requests to a backup DHCP server. If the backup DHCP server is not available, the relay agent selects the next backup DHCP server, and so on. If no backup DHCP server is available, it repeats the process starting from the master DHCP server.
The master DHCP server is determined in one of the following ways:
·     In a common network where multiple DHCP server addresses are specified on the DHCP relay interface, the first specified DHCP server is the master. The other DHCP servers are backup.
·     In a network where DHCP address pools are configured on the DHCP relay agent, the first specified DHCP server in a DHCP address pool is the master. The other DHCP servers in the DHCP address pool are backup.
DHCP server selection supports the following functions:
·     DHCP server response timeout time—The DHCP relay agent determines that a DHCP server is not available if it does not receive any response from the server within the DHCP server response timeout time. The DHCP server response timeout time is configurable and the default is 30 seconds.
·     DHCP server switchback—If the DHCP relay agent selects a backup DHCP server, it does not switch back to the master DHCP server by default. You can configure the DHCP relay agent to switch back to the master DHCP server after a delay. If the master DHCP server is available, the DHCP relay agent forwards DHCP requests to the master DHCP server. If the master DHCP server is not available, the DHCP relay agent still uses the backup DHCP server.
Specifying the DHCP server selecting algorithm in interface view
3.     Specify the DHCP server selecting algorithm.
dhcp relay server-address algorithm { master-backup | polling }
By default, the polling algorithm is used. The DHCP relay agent forwards DHCP requests to all DHCP servers.
4.     (Optional.) Set the DHCP server response timeout time for DHCP server switchover.
dhcp relay dhcp-server timeout time
By default, the DHCP server response timeout time is 30 seconds.
5.     (Optional.) Enable the switchback to the master DHCP server and set the delay time.
dhcp relay master-server switch-delay delay-time
By default, the DHCP relay agent does not switch back to the master DHCP server.
Specifying the DHCP server selecting algorithm in DHCP address pool view
Enabling the DHCP relay agent to record relay entries
Perform this task to enable the DHCP relay agent to automatically record clients' IP-to-MAC bindings (relay entries) after they obtain IP addresses through DHCP.
Some security features use the relay entries to check incoming packets and block packets that do not match any entry. In this way, illegal hosts are not able to access external networks through the relay agent. Examples of the security features are ARP address check, authorized ARP, and IP source guard.
2.     Enable the relay agent to record relay entries.
By default, the relay agent does not record relay entries.
Enabling periodic refresh of dynamic relay entries
A DHCP client unicasts a DHCP-RELEASE message to the DHCP server to release its IP address. The DHCP relay agent conveys the message to the DHCP server and does not remove the IP-to-MAC entry of the client.
With this feature, the DHCP relay agent uses the following information to periodically send a DHCP-REQUEST message to the DHCP server:
·     The IP address of a relay entry.
·     The MAC address of the DHCP relay interface.
The relay agent maintains the relay entries depending on what it receives from the DHCP server:
·     If the server returns a DHCP-ACK message or does not return any message within an interval, the DHCP relay agent removes the relay entry. In addition, upon receiving the DHCP-ACK message, the relay agent sends a DHCP-RELEASE message to release the IP address.
·     If the server returns a DHCP-NAK message, the relay agent keeps the relay entry.
2.     Enable periodic refresh of dynamic relay entries.
dhcp relay client-information refresh enable
By default, periodic refresh of dynamic relay entries is enabled.
3.     (Optional.) Set the refresh interval.
dhcp relay client-information refresh [ auto | interval interval ]
By default, the refresh interval is auto, which is calculated based on the number of total relay entries.
Enabling DHCP starvation attack protection
A DHCP starvation attack occurs when an attacker constantly sends forged DHCP requests using different MAC addresses in the chaddr field to a DHCP server. This exhausts the IP address resources of the DHCP server so legitimate DHCP clients cannot obtain IP addresses. The DHCP server might also fail to work because of exhaustion of system resources. The following methods are available to relieve or prevent such attacks.
·     To relieve a DHCP starvation attack that uses DHCP packets encapsulated with different source MAC addresses, you can use one of the following methods:
¡     Limit the number of ARP entries that a Layer 3 interface can learn.
¡     Set the MAC learning limit for a Layer 2 port, and disable unknown frame forwarding when the MAC learning limit is reached.
·     To prevent a DHCP starvation attack that uses DHCP requests encapsulated with the same source MAC address, you can enable MAC address check on the DHCP relay agent. The DHCP relay agent compares the chaddr field of a received DHCP request with the source MAC address in the frame header. If they are the same, the DHCP relay agent forwards the request to the DHCP server. If not, the relay agent discards the request.
Enable MAC address check only on the DHCP relay agent directly connected to the DHCP clients. A DHCP relay agent changes the source MAC address of DHCP packets before sending them.
A MAC address check entry has an aging time. When the aging time expires, both of the following occur:
·     The entry ages out.
·     The DHCP relay agent rechecks the validity of DHCP requests sent from the MAC address in the entry.
2.     Set the aging time for MAC address check entries.
The default aging time is 30 seconds.
This command takes effect only after you execute the dhcp relay check mac-address command.
3.     Enter the interface view.
4.     Enable MAC address check.
By default, MAC address check is disabled.
Enabling DHCP server proxy on the DHCP relay agent
The DHCP server proxy feature isolates DHCP servers from DHCP clients and protects DHCP servers against attacks.
Upon receiving a response from the server, the DHCP server proxy modifies the server's IP address as the relay interface's IP address before sending out the response. The DHCP client takes the DHCP relay agent as the DHCP server.
3.     Enable DHCP relay agent and DHCP server proxy on the interface.
dhcp select relay proxy
By default, the interface operates in DHCP server mode after DHCP is enabled.
Enabling client offline detection on the DHCP relay agent
The client offline detection on the DHCP relay agent detects the user online status based on the ARP entry aging. When an ARP entry ages out, the DHCP client offline detection feature deletes the relay entry for the IP address and sends a RELEASE message to the DHCP server.
Without relay entries, client offline detection cannot function correctly.
3.     Enter interface view.
4.     Enable the DHCP relay agent.
dhcp select relay
5.     Enable client offline detection.
dhcp client-detect
By default, client offline detection is disabled on the DHCP relay agent.
Configure the relay agent to release the IP address for a relay entry. The relay agent sends a DHCP-RELEASE message to the server and meanwhile deletes the relay entry. Upon receiving the DHCP-RELEASE message, the DHCP server releases the IP address.
This command can release only the IP addresses in the recorded relay entries.
2.     Configure the DHCP relay agent to release an IP address.
To support Option 82, you must perform related configuration on both the DHCP server and relay agent. For DHCP server Option 82 configuration, see "Enabling handling of Option 82."
3.     Enable the relay agent to handle Option 82.
dhcp relay information enable
By default, handling of Option 82 is disabled.
4.     (Optional.) Configure the strategy for handling DHCP requests that contain Option 82.
By default, the handling strategy is replace.
If the handling strategy is replace, configure a padding mode and a padding format for Option 82. If the handling strategy is keep or drop, you do not need to configure a padding mode or padding format for Option 82.
5.     (Optional.) Configure the padding mode and padding format for the Circuit ID sub-option.
dhcp relay information circuit-id { bas [ sub-interface-vlan ] [ with-vxlan ] | srv6-opcode | string circuit-id | { normal | verbose [ node-identifier { mac | sysname | user-defined node-identifier } ] [ sub-interface-vlan ] [ interface ] } [ format { ascii | hex } ] }
By default, the padding mode for Circuit ID sub-option is normal, and the padding format is hex.
The device name (sysname) must not include spaces if it is configured as the padding content for sub-option 1. Otherwise, the DHCP relay agent will fail to add or replace Option 82.
6.     (Optional.) Configure the padding mode and padding format for the Remote ID sub-option.
By default, the padding mode for the Remote ID sub-option is normal, and the padding format is hex.
2.     Set the DSCP value for DHCP packets sent by the DHCP relay agent.
By default, the DSCP value in DHCP packets sent by the DHCP relay agent is 56.
Manually specifying the DHCP relay agent address for the giaddr field
This task allows you to specify the IP addresses to be encapsulated to the giaddr field of the DHCP requests. If you do not specify any DHCP relay agent address, the primary IP address of the DHCP relay interface is encapsulated to the giaddr field of DHCP requests.
3.     Specify the DHCP relay agent address to be encapsulated in relayed DHCP requests.
dhcp relay gateway ip-address
By default, the primary IP address of the DHCP relay interface is encapsulated in the relayed DHCP requests.
Configuring smart relay to specify the DHCP relay agent address for the giaddr field
By default, the relay agent only encapsulates the primary IP address to the giaddr field of all requests before relaying them to the DHCP server. The DHCP server then selects an IP address on the same subnet as the address in the giaddr filed. If no assignable addresses on the subnet are available, the DHCP server does not assign any IP address. The DHCP smart relay feature is introduced to allow the DHCP relay agent to encapsulate secondary IP addresses when the DHCP server does not send back a DHCP-OFFER message.
The relay agent initially encapsulates its primary IP address to the giaddr field before forwarding a request to the DHCP server. If no DHCP-OFFER is received, the relay agent allows the client to send a maximum of two requests to the DHCP server by using the primary IP address. If no DHCP-OFFER is returned after two retries, the relay agent switches to a secondary IP address. If the DHCP server still does not respond, the next secondary IP address is used. After the secondary IP addresses are all tried and the DHCP server does not respond, the relay agent repeats the process by starting from the primary IP address.
2.     Enable the DHCP smart relay feature.
dhcp smart-relay enable
By default, the DHCP smart relay feature is disabled.
This task is required if multiple relay interfaces share the same IP address or if a relay interface does not have routes to DHCP servers. You can perform this task to specify an IP address or the IP address of another interface on the DHCP relay agent as the source IP address for relayed DHCP requests.
If you specify the ip-address argument, the relay agent changes not only the source IP address but also the giaddr field of a DHCP request. The DHCP server assigns the client an IP address on the same subnet as the specified IP address in the giaddr field. As a result, the client might not be on the same subnet as the DHCP relay interface (the gateway). To avoid this problem, you must configure Option 82 on the relay interface before specifying the ip-address argument. This configuration enables the DHCP relay agent to insert the primary IP address of the relay interface in Option 82. Based on this option, the DHCP server assigns an IP address on the same subnet as the IP address of the relay interface. The DHCP relay agent looks up the MAC address table for the output interface to forward the DHCP reply packets.
3.     Specify the source IP address for DHCP requests.
dhcp relay source-address { ip-address [ option { 60 [ option-text ] | code } ] | gateway | interface interface-type interface-number | relay-interface }
The relay agent chooses the default source IP address for relayed requests depending on whether its server-side interface and the DHCP server belong to the same VPN instance:
¡     If they belong to the same VPN instance, the relay agent uses the IP address of the output interface for relayed requests as the source IP address.
¡     If they belong to different VPN instances, the relay agent uses the lowest IP address that is in the same VPN instance as the DHCP server as the source address.
Keyword
If a DHCP request carries the specified option, the relay agent changes the source IP address and the giaddr field of the DHCP request to the specified IP address.
gateway
The relay agent uses the IP address in the giaddr field as the source IP address. If the giaddr field is empty, the relay agent follows the default rule to specify the source IP address for DHCP requests.
interface
The relay agent uses the IP address of an interface as the source IP address. If the specified interface has no IP addresses, the relay agent follows the default rule to specify the source IP address for DHCP requests.
relay-interface
The relay agent uses the primary IP address of the relay interface as the source IP address. If this interface does not have an IP address, the relay agent follows the default rule to specify the source IP address for DHCP requests.
On an SRv6 network, the DHCP relay agent feature can be configured on the VSI interface of a PE.
When the DHCP relay agent receives a DHCP request from an access unit mapped to the VSI interface, the relay agent forwards this request to the DHCP servers and broadcasts this request to other PEs. If those PEs also function as DHCP relay agents, each will forward the DHCP request to the DHCP servers they are connecting to. To prevent a DHCP server from receiving the same DHCP request from different PEs, you can configure this command on the VSI interface of each PE that is not directly connecting to DHCP clients.
2.     Enter VSI interface view.
interface vsi-interface vsi-number
3.     Configure the DHCP relay agent to discard the DHCP requests received from SRv6 tunnels.
dhcp relay request-from-tunnel discard
By default, the DHCP relay agent forwards the DHCP requests received from SRv6 tunnels.
If you configure this command on a device that acts as both the distributed and centralized SRv6 IP gateways, make sure the gateways do not use the same VSI interface to provide gateway services.
On a distributed EVPN gateway network, VSI interfaces of all distributed EVPN gateways have the same IP address, and the DHCP relay agent is enabled on EVPN gateways. When a DHCP client sends a request to its connected EVPN gateway, the gateway records request forwarding information for the client before relaying the request to the DHCP server. The request forwarding information contains the MAC address of the DHCP client and output interface of the request packet. If the reply for this request is received by another EVPN gateway, the reply is discarded by default because it does not have matching request forwarding information on the gateway. As a result, the client cannot obtain the IP address.
To resolve this issue, configure the support for forwarding replies based on MAC address table on the relay agent that is connected to the DHCP server. The relay agent will look up the MAC address table for the output interface to forward the replies that do not have request forwarding information. This feature ensures that DHCP clients can receive DHCP reply packets.
If the broadcast keyword is specified, the DHCP relay agent broadcasts the DHCP reply out of the interface in the matching MAC address entry. When the DHCP relay agent connecting to the requesting DHCP client receives the reply, it sends the reply to its CPU before broadcasting the reply. If relay entry recording is enabled on this relay agent, a relay entry is generated for the DHCP client.
If the broadcast keyword is not specified, the DHCP relay agent connecting to the requesting client will directly forward the reply based on the MAC address instead of delivering it up to the CPU. In this case, the DHCP relay agent cannot be aware that the packet is a DHCP reply, thus no relay entry is generated for the client even if relay entry recording is enabled.
2.     Enable MAC address table lookup for DHCP replies that do not have request forwarding information.
dhcp relay mac-forward enable [ broadcast ]
By default, the DHCP relay agent discards a DHCP reply if the relay agent does not have request forwarding information for the reply.
This feature enables the DHCP relay agent to ignore the broadcast flag and always unicast relayed responses. This feature is useful in some LANs, such as a WLAN network, where broadcast communication is not recommended.
2.     Enable the DHCP relay agent to always unicast relayed DHCP responses.
dhcp relay always-unicast
By default, the DHCP relay agent reads the broadcast flag to decide whether to broadcast or unicast a response.
Configure this feature if the DHCP relay agent is required to forward DHCP replies to DHCP clients based on Option 82. For example, an IPRAN network has a primary gateway and a secondary gateway. An L3VE interface is configured as the relay interface on each of the gateways. Multiple L2VE subinterfaces are configured to receive packets. One L2VE subinterface corresponds to one PW. Only the primary gateway receives DHCP requests, but both the primary and secondary gateways might receive DHCP replies. The primary gateway can forward DHCP replies based on locally recorded user information, but the secondary gateway cannot. The secondary gateway can only forward DHCP replies to all PWs.
To enable the secondary gateway to forward a DHCP reply to only the intended PW, perform the following tasks:
·     Configure the dhcp relay information enable and dhcp relay information circuit-id (with sub-interface-vlan specified) commands on the primary gateway. Then, when the primary gateway receives a DHCP request, it adds Option 82 to the reply and record the VLAN ID of the L2VE subinterface.
·     Configure the dhcp relay information enable, dhcp relay information circuit-id (with sub-interface-vlan specified), and dhcp relay forward reply by-option82 commands on the secondary gateway. Then, when the secondary gateway receives a DHCP reply, it resolves Option 82, records the VLAN ID of the L2VE subinterface, and forwards the reply to the PW.
4.     Configure the padding mode and padding format for the Circuit ID sub-option.
dhcp relay information circuit-id { bas [ sub-interface-vlan ] [ with-vxlan ] | srv6-opcode | string circuit-id | { normal | verbose [ node-identifier { mac | sysname | user-defined node-identifier } ] [ interface ] } [ sub-interface-vlan ] [ format { ascii | hex } ] }
By default, the padding mode for the Circuit ID sub-option is normal, and the padding format is hex.
The device name (set by using the sysname command) must not include spaces if it is configured as the padding content for sub-option 1. Otherwise, the DHCP relay agent will fail to add or replace Option 82.
You must set the padding mode to bas, normal, or verbose, and specify the sub-interface-vlan keyword for this command.
5.     Configure the DHCP relay agent to forward DHCP replies based on Option 82.
By default, the DHCP relay agent does not forward DHCP replies based on Option 82.
Verifying and maintaining DHCP relay agent
Verifying DHCP relay agent configuration
Perform all display tasks in in any view.
·     Display information about DHCP servers on an interface.
·     Display Option 82 configuration information on the DHCP relay agent.
Displaying and clearing DHCP relay entries
To display DHCP relay entries, execute the following command in any view:
To clear DHCP relay entries, execute the following command in user view:
Displaying MAC address check entries on the DHCP relay agent
To display MAC address check entries on the DHCP relay agent, execute the following command in any view:
display dhcp relay check mac-address
Displaying and clearing packet statistics on the DHCP relay agent
To display packet statistics on the DHCP relay agent, execute the following command in any view:
To clear packet statistics on the DHCP relay agent, execute the following command in user view:
DHCP relay agent configuration examples
Example: Configuring basic DHCP relay agent
As shown in Figure 19, configure the DHCP relay agent on Router A. The DHCP relay agent enables DHCP clients to obtain IP addresses and other configuration parameters from the DHCP server on another subnet.
Figure 19 Network diagram
The DHCP relay agent and server are on different subnets. Configure static or dynamic routing to make them reachable to each other.
Configure the DHCP server to guarantee the client-server communication through the DHCP relay agent. For more information about DHCP server configuration, see "DHCP server configuration examples."
# Specify IP addresses for the interfaces. (Details not shown.)
# Enable DHCP.
# Enable the DHCP relay agent on GigabitEthernet 0/0/1.
[RouterA-GigabitEthernet0/0/1] dhcp select relay
# Specify the IP address of the DHCP server on the relay agent.
[RouterA-GigabitEthernet0/0/1] dhcp relay server-address 10.1.1.1
# Verify that DHCP clients can obtain IP addresses and all other network parameters from the DHCP server through the DHCP relay agent. (Details not shown.)
# Display the statistics of DHCP packets forwarded by the DHCP relay agent.
[RouterA] display dhcp relay statistics
# Display relay entries if you have enabled relay entry recording on the DHCP relay agent.
[RouterA] display dhcp relay client-information
Example: Configuring Option 82
As shown in Figure 20, the DHCP relay agent (Router A) replaces Option 82 in DHCP requests before forwarding them to the DHCP server (Router B).
·     The Circuit ID sub-option is company001.
·     The Remote ID sub-option is device001.
Figure 20 Network diagram
To ensure correct processing of Option 82, enable the DHCP server to handle Option 82.
# Enable DHCP.
# Enable the DHCP relay agent to handle Option 82, and perform Option 82 related configuration.
[RouterA-GigabitEthernet0/0/1] dhcp relay information enable
[RouterA-GigabitEthernet0/0/1] dhcp relay information strategy replace
[RouterA-GigabitEthernet0/0/1] dhcp relay information circuit-id string company001
[RouterA-GigabitEthernet0/0/1] dhcp relay information remote-id string device001
Example: Configuring DHCP server selection
As shown in Figure 21, the DHCP client and the DHCP servers are in different subnets. DHCP server 1 and DHCP server 2 both have a DHCP address pool that contains IP addresses in subnet 22.22.22.0/24, but neither has DHCP enabled.
Configure the DHCP relay agent for the DHCP client to obtain an IP address in subnet 22.22.22.0/24 and other configuration parameters from a DHCP server. The DHCP relay agent is connected to the DHCP client through GigabitEthernet 0/0/1, to DHCP server 1 through GigabitEthernet 0/0/2, and to DHCP server 2 through GigabitEthernet 0/0/3.
Figure 21 Network diagram
1.     Assign IP addresses to interfaces on the routers. (Details not shown.)
2.     Configure Router B and Router C as DHCP servers. (Details not shown.)
3.     Configure the DHCP relay agent on Router A:
# Enable DHCP.
# Specify the IP addresses of the DHCP servers.
[RouterA-GigabitEthernet0/0/1] dhcp relay server-address 1.1.1.1
[RouterA-GigabitEthernet0/0/1] dhcp relay server-address 2.2.2.2
# Specify the DHCP server selecting algorithm as master-backup.
[RouterA-GigabitEthernet0/0/1] dhcp relay server-address algorithm master-backup
# Configure the DHCP relay agent to switch back to the master DHCP server 3 minutes after it switches to the backup DHCP server.
[RouterA-GigabitEthernet0/0/1] dhcp relay master-server switch-delay 3
# Verify that the DHCP client cannot obtain an IP address and that the following log is output in about 30 seconds.
DHCPR/3/DHCPR_SERVERCHANGE: -MDC=1;
 Switched to the server at 2.2.2.2 because the current server did not respond.
# Enable DHCP on the DHCP server at 1.1.1.1. (Details not shown.)
# Verify that the DHCP client cannot obtain an IP address and that the following log is output in about 3 minutes.
DHCPR/3/DHCPR_SWITCHMASTER: -MDC=1;
 Switched to the master DHCP server at 1.1.1.1.
# Verify that the DHCP client obtains an IP address. (Details not shown.)
Troubleshooting DHCP relay agent configuration
Failure of DHCP clients to obtain configuration parameters through the DHCP relay agent
Symptom
DHCP clients cannot obtain configuration parameters through the DHCP relay agent.
Solution
Some problems might occur with the DHCP relay agent or server configuration.
To locate the problem, enable debugging and execute the display command on the DHCP relay agent to view the debugging information and interface state information.
Check that:
·     DHCP is enabled on the DHCP server and relay agent.
·     The DHCP server has an address pool on the same subnet as the DHCP clients.
·     The DHCP server and DHCP relay agent can reach each other.
·     The DHCP server address specified on the DHCP relay interface connected to the DHCP clients is correct.
Configuring the DHCP client
About DHCP client
With DHCP client enabled, an interface uses DHCP to obtain configuration parameters from the DHCP server, for example, an IP address.
Restrictions and guidelines: DHCP client configuration
The DHCP client configuration is supported only on Layer 3 Ethernet interfaces (or subinterfaces), VLAN interfaces, and Layer 3 aggregate interfaces.
DHCP client tasks at a glance
To configure a DHCP client, perform the following tasks:
1.     Enabling the DHCP client on an interface
2.     Configuring a DHCP client ID for an interface
Perform this task if the DHCP client uses the client ID to obtain IP addresses.
3.     (Optional.) Enabling duplicated address detection
4.     (Optional.) Setting the DSCP value for DHCP packets sent by the DHCP client
·     If the number of IP address request failures reaches the system-defined amount, the DHCP client-enabled interface uses a default IP address.
·     An interface can be configured to acquire an IP address in multiple ways. The new configuration overwrites the old.
·     Secondary IP addresses cannot be configured on an interface that is enabled with the DHCP client.
·     If the interface obtains an IP address on the same segment as another interface on the device, the interface does not use the assigned address. Instead, it requests a new IP address from the DHCP server.
2.     Enter interface view.
3.     Configure an interface to use DHCP for IP address acquisition.
ip address dhcp-alloc
By default, an interface does not use DHCP for IP address acquisition.
A DHCP client ID is added to the DHCP option 61 to uniquely identify a DHCP client. A DHCP server can assign IP addresses to clients based on their DHCP client IDs.
DHCP client ID includes an ID type and a type value. Each ID type has a fixed type value. You can specify a DHCP client ID by using one of the following methods:
·     Use an ASCII string as the client ID. If an ASCII string is used, the type value is 00.
·     Use a hexadecimal number as the client ID. If a hexadecimal number is used, the type value is the first two characters in the number.
·     Use the MAC address of an interface to generate a client ID. If this method is used, the type value is 01.
The type value of a DHCP client ID can be displayed by the display dhcp server ip-in-use or display dhcp client command.
Make sure the ID for each DHCP client is unique.
3.     Configure a DHCP client ID for the interface.
By default, an interface generates the DHCP client ID based on its MAC address. If the interface has no MAC address, it uses the MAC address of the first Ethernet interface to generate its client ID.
DHCP client detects IP address conflict through ARP packets. An attacker can act as the IP address owner to send an ARP reply. The spoofing attack makes the client unable to use the IP address assigned by the server. As a best practice, disable duplicate address detection when ARP attacks exist on the network.
2.     Enable duplicate address detection.
dhcp client dad enable
By default, the duplicate address detection feature is enabled on an interface.
2.     Set the DSCP value for DHCP packets sent by the DHCP client.
dhcp client dscp dscp-value
By default, the DSCP value in DHCP packets sent by the DHCP client is 56.
Verifying and maintaining DHCP client
To display DHCP client information, execute the following command in any view:
DHCP client configuration examples
Example: Configuring DHCP client
As shown in Figure 23, Router B contacts the DHCP server through GigabitEthernet 0/0/1 to obtain an IP address, a DNS server address, and static route information. The DHCP client's IP address resides on subnet 10.1.1.0/24. The DNS server address is 20.1.1.1. The next hop of the static route to subnet 20.1.1.0/24 is 10.1.1.2.
The DHCP server uses Option 121 to assign static route information to DHCP clients. Figure 22 shows the Option 121 format. The destination descriptor field contains the following parts: subnet mask length and destination network address, both in hexadecimal notation. In this example, the destination descriptor is 18 14 01 01 (the subnet mask length is 24 and the network address is 20.1.1.0 in dotted decimal notation). The next hop address is 0A 01 01 02 (10.1.1.2 in dotted decimal notation).
Figure 22 Option 121 format
Figure 23 Network diagram
1.     Configure Router A:
# Specify an IP address for GigabitEthernet 0/0/1.
# Exclude an IP address from dynamic allocation.
# Configure DHCP address pool 0. Specify the subnet, lease duration, DNS server address, and a static route to subnet 20.1.1.0/24.
[RouterA-dhcp-pool-0] expired day 10
[RouterA-dhcp-pool-0] dns-list 20.1.1.1
[RouterA-dhcp-pool-0] option 121 hex 181401010A010102
# Enable DHCP.
2.     Configure Router B:
# Configure GigabitEthernet 0/0/1 to use DHCP for IP address acquisition.
[RouterB-GigabitEthernet0/0/1] ip address dhcp-alloc
# Display the IP address and other network parameters assigned to Router B.
[RouterB] display dhcp client verbose
GigabitEthernet0/0/1 DHCP client information:
 Current state: BOUND
 Allocated IP: 10.1.1.3 255.255.255.0
 Allocated lease: 864000 seconds, T1: 331858 seconds, T2: 756000 seconds
 DHCP server: 10.1.1.1
 Transaction ID: 0xcde72232
 Classless static routes:
   Destination: 20.1.1.0, Mask: 255.255.255.0, NextHop: 10.1.1.2
 DNS servers: 20.1.1.1
 Client ID value: 000c.29d3.8659-GE0/0/1
                            6433-2e38-3635-392d-
                            4574-6830-2f30-2f32
 T1 will timeout in 3 days 19 hours 48 minutes 43 seconds
# Display the route information on Router B. The output shows that a static route to subnet 20.1.1.0/24 is added to the routing table.
[RouterB] display ip routing-table
Destinations : 11        Routes : 11
10.1.1.0/24         Direct 0    0            10.1.1.3        GE0/0/1
10.1.1.3/32         Direct 0    0            127.0.0.1       InLoop0
20.1.1.0/24         Static 70   0            10.1.1.2        GE0/0/1
10.1.1.255/32       Direct 0    0            10.1.1.3        GE0/0/1
127.0.0.0/32        Direct 0    0            127.0.0.1       InLoop0
224.0.0.0/4         Direct 0    0            0.0.0.0         NULL0
224.0.0.0/24        Direct 0    0            0.0.0.0         NULL0
255.255.255.255/32  Direct 0    0            127.0.0.1       InLoop0
DHCP client configuration examples (on an AP)
As shown in Figure 24, the AP obtains an IP address, the AC address, a gateway address, and a DNS server address through DHCP.
Figure 24 Network diagram
The following is the configuration on the AP.
<AP> system-view
[AP] interface gigabitethernet 0/0/1
[AP-GigabitEthernet0/0/1] ip address dhcp-alloc
# Display the IP address and other network parameters assigned to the AP.
[AP] display dhcp client
Configuring the BOOTP client
About BOOTP client
BOOTP client application
An interface that acts as a BOOTP client can use BOOTP to obtain information (such as IP address) from the BOOTP server.
To use BOOTP, an administrator must configure a BOOTP parameter file for each BOOTP client on the BOOTP server. The parameter file contains information such as MAC address and IP address of a BOOTP client. When a BOOTP client sends a request to the BOOTP server, the BOOTP server searches for the BOOTP parameter file and returns the corresponding configuration information.
BOOTP is usually used in relatively stable environments. In network environments that change frequently, DHCP is more suitable.
Because a DHCP server can interact with a BOOTP client, you can use the DHCP server to assign an IP address to the BOOTP client instead of using a BOOTP server. The DHCP server will assign an IP address to the BOOTP client based on the IP address allocation sequence.
Obtaining an IP address dynamically
A BOOTP client dynamically obtains an IP address from a BOOTP server as follows:
1.     The BOOTP client broadcasts a BOOTP request, which contains its own MAC address.
2.     Upon receiving the request, the BOOTP server searches the configuration file for the IP address and other information according to the BOOTP client's MAC address.
3.     The BOOTP server returns a BOOTP response to the BOOTP client.
4.     The BOOTP client obtains the IP address from the received response.
A DHCP server can take the place of the BOOTP server in the following dynamic IP address acquisition.
Protocols and standards
·     RFC 951, Bootstrap Protocol (BOOTP)
·     RFC 2132, DHCP Options and BOOTP Vendor Extensions
·     RFC 1542, Clarifications and Extensions for the Bootstrap Protocol
Configuring an interface to use BOOTP for IP address acquisition
BOOTP client configuration applies only to Layer 3 Ethernet interfaces (including subinterfaces), Layer 3 aggregate interfaces, and VLAN interfaces.
3.     Configure an interface to use BOOTP for IP address acquisition.
ip address bootp-alloc
By default, an interface does not use BOOTP for IP address acquisition.
Verifying and maintaining BOOTP client
To display BOOTP client information, execute the following command in any view:
BOOTP client configuration examples
Example: Configuring BOOTP client
As shown in Figure 25, GigabitEthernet 0/0/1 of Router B connects to the LAN to obtain an IP address from the DHCP server by using BOOTP.
Figure 25 Network diagram
Configure the DHCP server to assign an IP address to the BOOTP client. For more information, see "DHCP server configuration examples."
The following describes the configuration on Router B, which acts as a client.
# Configure GigabitEthernet 0/0/1 to use BOOTP to obtain an IP address.
[RouterB-GigabitEthernet0/0/1] ip address bootp-alloc
# Display the IP address assigned to the BOOTP client.
[RouterB] display bootp client