04-Track commands
Chapters Download (86.62 KB)
Use delay to set the period of time that the Track module must wait before notifying the application module of track entry state changes.
Use undo delay to remove the notification delay configuration.
delay { negative negative-time | positive positive-time } *
undo delay
The Track module notifies the application module immediately when the track entry state changes.
Track view
context-admin
negative negative-time: Specifies the delay for notifying the application module that the track entry state has changed to Negative. The negative-time argument represents the negative state notification delay in the range of 1 to 300 seconds.
positive positive-time: Specifies the delay for notifying the application module that the track entry state has changed to Positive. The positive-time argument represents the positive state notification delay in the range of 1 to 300 seconds.
If the Track module immediately notifies the application module of a track entry state change but the route convergence is not complete, a communication failure might occur. In such cases, you can set a notification delay to avoid immediate notification of track entry state changes.
The notification delay settings do not take effect if the track entry is not associated with an application module.
# Set the negative state notification delay to 50 seconds and the positive state notification delay to 30 seconds for Boolean OR tracked list 101.
[Sysname] track 101 list boolean or
[Sysname-track-101] delay negative 50 positive 30
track bfd
track interface
track interface physical
track interface protocol
track ip route reachability
track list boolean
track list threshold percentage
track list threshold weight
track nqa
Use display track to display track entry information.
display track { track-entry-number | all [ negative | positive ] } [ brief ]
context-admin
context-operator
track-entry-number: Specifies a track entry by its ID in the range of 1 to 1024.
all: Specifies all track entries.
negative: Displays information about track entries in Negative state.
positive: Displays information about track entries in Positive state.
brief: Displays brief information about track entries.
# Display information about all track entries.
<Sysname> display track all
Track ID: 1
State: Positive
Duration: 0 days 0 hours 0 minutes 7 seconds
Tracked object type: NQA
Notification delay: Positive 20, Negative 30 (in seconds)
Tracked object:
NQA entry: admin test
Reaction: 10
Remote IP/URL: 2.2.2.2
Local IP: 1.1.1.1
Interface: GigabitEthernet1/2/5/1
Tracked by:
Track-list 6
Track-list 7
Track ID: 2
State: NotReady
Tracked object type: BFD
Tracked object:
BFD session mode: Echo
Outgoing interface: GigabitEthernet1/2/5/1
VPN instance name: --
Remote IP: 192.168.40.1
Local IP: 192.168.40.2
Track ID: 3
State: Negative
Tracked object type: Interface
Tracked object:
Interface: GigabitEthernet1/2/5/2
Protocol: IPv4
Tracked by:
Track-list 6
Track-list 7
Track ID: 5
State: Positive
Tracked object type: Route
Tracked object:
IP route: 0.0.0.0/0 reachability
Protocol: BGP
Nexthop interface : GigabitEthernet1/2/5/3
Track ID: 6
State: Positive
Tracked object type: Percentage threshold list
Threshold: Positive 40, Negative 30
Percentage of positive objects: 50%
Tracked objects:
Object 1: Positive
Object 3: Negative
Track ID: 7
State: Positive
Tracked object type: Weight threshold list
Threshold: Positive 50, Negative 30
Positive weight/total weight: 50/80
Tracked objects:
Object 1: Positive, Weight: 50
Object 3: Negative, Weight: 30
Track ID: 8
State: Positive
Tracked object type: Boolean and list
Tracked objects:
Object 1: Positive
Object 3: Negative(not)
Object 10: NotReady(not)
# Display brief information about track entries in Negative state.
<Sysname> display track all negative brief
ID Status Type Remote IP/URL Local IP Interface
1 Negative Interface -- -- GE1/2/5/1
10 Negative Interface -- -- GE1/2/5/2
12 Negative List -- -- --
Track ID |
ID of a track entry. |
State |
States of a track entry: · Positive—The tracked object operates correctly. · NotReady—The tracked object is invalid. · Negative—The tracked object is abnormal. |
Duration |
Time period during which the track entry stays in the state. |
Type |
Tracked object type: · BFD. · Interface. · Route. · NQA. · List—Tracked list. This field is displayed only when the display track brief command is executed. |
Tracked object type |
Tracked object type: · BFD. · Interface. · Route. · NQA. · Boolean and list—Boolean AND list. · Boolean or list—Boolean OR list. · Percentage threshold list. · Weight threshold list. |
Notification delay: Positive 20, Negative 30 (in seconds) |
· The Track module notifies the application modules that the status of the track entry changes to Positive after a delay time of 20 seconds. · The Track module notifies the application modules that the status of the track entry changes to Negative after a delay time of 30 seconds. |
Threshold: Positive 40, Negative 30 |
Positive and negative state thresholds. This field is displayed only when the tracked object type is Percentage threshold list or Weight threshold list. |
Percentage of positive objects |
Percentage of Positive objects in the tracked list. This field is displayed only when the tracked object type is Percentage threshold list. |
Positive weight/total weight: 50/80 |
Weight of Positive objects to the total weight of all objects in the tracked list. This field is displayed only when the tracked object type is Weight threshold list. |
Tracked object |
Tracked object associated with the track entry. |
NQA entry |
NQA operation associated with the track entry. |
Reaction |
Reaction entry associated with the track entry. |
BFD session mode |
BFD session mode. Only echo mode is supported. |
Outgoing interface |
Outgoing interface of the packets. |
VPN instance name |
Name of the VPN instance to which the packets belong. If the packets belong to the public network, two consecutive hyphens (--) are displayed. |
Remote IP/URL |
Remote IP address or URL. If no remote IP address or URL exists, two consecutive hyphens (--) are displayed. |
Local IP |
Local IP address. If no local IP address exists, two consecutive hyphens (--) are displayed. |
Interface to be monitored. If no interface is to be monitored, two consecutive hyphens (--) are displayed. |
Protocol |
Link states or Layer 3 protocol states of the monitored interface: · None—Link status of the monitored interface. · IPv4—IPv4 protocol status of the monitored Layer 3 interface. · IPv6—IPv6 protocol status of the monitored Layer 3 interface. |
IP route |
Route associated with the track entry. |
Protocol |
Protocol type of the route. If the route does not exist, N/A is displayed. |
Nexthop interface |
Next hop of the route. If the route does not exist, N/A is displayed. |
Object 10 : Positive |
State of a tracked object: Positive, NotReady, or Negative. If the tracked object type is Weight threshold list, the weight of the object is also displayed. If the (not) attribute is displayed, the tracked list will negate the state of the object. |
Tracked by |
Track entries that are tracking the track entry (tracked object). |
Track-list 6 |
Tracked list that is tracking the track entry (tracked object). |
track bfd
track interface
track nqa
Use object to add a track entry as an object to a tracked list.
Use undo object to remove the object from a tracked list
object track-entry-number [ not ] [ weight weight ]
undo object track-entry-number
A tracked list does not contain any objects.
Track view
context-admin
not: Negates the state of the object. For example, the tracked list regards the object as Negative when the object is in Positive state. This keyword is supported only by a Boolean list.
weight weight: Assigns a weight in the range of 1 to 255 to the object. This keyword is supported only by a weight threshold list. The default weight is 10.
The track entry ID of the object cannot be the same as the ID of the tracked list to which the object is added.
You can add a maximum of 16 objects to a tracked list.
Loops between track entries are not allowed. For example, after you add track entry 1 (object 1) to tracked list 2 and track entry 2 (object 2) to tracked list 3, you cannot add track entry 3 (object 3) to tracked list 1 because a loop will be created.
# Create Boolean AND list 100 and add track entries 1 and 2 as tracked objects to the list.
[Sysname] track 100 list boolean and
[Sysname-track-100] object 1
[Sysname-track-100] object 2 not
Use threshold percentage to set the threshold values used to determine the state of a percentage threshold list.
Use undo threshold percentage to restore the default.
threshold percentage { negative negative-threshold | positive positive-threshold } *
The negative state threshold is 0% and the positive state threshold is 1%.
Track view
context-admin
negative negative-threshold: Specifies the negative state threshold in the range of 0 to 100. The percentage of Positive objects must be equal to or smaller than the configured negative state threshold for the tracked list to be set to the Negative state.
positive positive-threshold: Specifies the positive state threshold in the range of 0 to 100. The percentage of Positive objects must be equal to or greater than the configured positive state threshold for the tracked list to be set to the Positive state. The positive-threshold must be greater than the negative-threshold.
The state of a percentage threshold list remains unchanged if the percentage of Positive objects is below the positive state threshold and above the negative state threshold.
This command is supported only by a percentage threshold list.
# Set the negative state threshold to 30% and the positive state threshold to 50% for percentage threshold list 1.
[Sysname] track 1 list threshold percentage
[Sysname-track-1] threshold percentage negative 30 positive 50
Use threshold weight to set the threshold values used to determine the state of a weight threshold list.
Use undo threshold weight to restore the default.
threshold weight { negative negative-threshold | positive positive-threshold } *
The negative state threshold is 0 and the positive state threshold is 1.
Track view
context-admin
negative negative-threshold: Specifies the negative state threshold in the range of 0 to 255. The total weight of Positive objects must be equal to or smaller than the configured negative state threshold for the tracked list to be set to the Negative state.
positive positive-threshold: Specifies the positive state threshold in the range of 0 to 255. The total weight of Positive objects must be equal to or greater than the configured positive state threshold for the tracked list to be set to the Positive state. The positive-threshold must be greater than the negative-threshold.
The state of a weight threshold list remains unchanged if the total weight of Positive objects is below the positive state threshold and above the negative state threshold.
This command is supported only by a weight threshold list.
# Set the negative state threshold to 30 and the positive state threshold to 50 for weight threshold list 1.
[Sysname] track 1 list threshold weight
[Sysname-track-1] threshold weight negative 30 positive 50
Use track bfd to create a track entry associated with a BFD session and enter track entry view, or enter the view of an existing track entry.
Use undo track to remove the track entry and all configurations from its view.
track track-entry-number bfd echo interface interface-type interface-number remote ip remote-ip-address local ip local-ip-address
undo track track-entry-number
No track entries exist.
context-admin
track-entry-number: Specifies the track entry ID in the range of 1 to 1024.
interface interface-type interface-number: Specifies the outgoing interface by its type and number of the BFD echo packets.
remote ip remote-ip-address: Specifies the destination IP address of the BFD echo packets.
local ip local-ip-address: Specifies the source IP address of the BFD echo packets.
To create a track entry, you must specify the tracked object type, which is bfd in this command.
To enter the view of an existing track entry, use the track track-entry-number command. The tracked object type is not required.
To modify the settings of a track entry, execute the undo track command to remove the track entry, and then create the track entry again.
When you associate Track with BFD, the virtual IP address of a VRRP group cannot be the local or remote address of a BFD session.
# Associate track entry 1 with BFD to monitor the link between local IP address 192.168.40.2 and remote IP address 192.168.40.1 by sending BFD echo packets through GigabitEthernet 1/2/5/1.
[Sysname] track 1 bfd echo interface gigabitethernet 1/2/5/1 remote ip 192.168.40.1 local ip 192.168.40.2
[Sysname-track-1]
delay
display track
Use track interface to create a track entry associated with the link state of an interface and enter track entry view, or enter the view of an existing track entry.
track track-entry-number interface interface-type interface-number
context-admin
To create a track entry, you must specify the tracked object type, which is interface in this command.
When you associate Track with interface management to monitor the link status of an interface, the track entry state changes as follows:
· The track entry state is Positive if the link state of the interface is up.
· The track entry state is Negative if the link state of the interface is down.
To display the link state of an interface, use the display ip interface brief command.
# Create track entry 1 and associate it with the link state of interface GigabitEthernet 1/2/5/1.
[Sysname] track 1 interface gigabitethernet 1/2/5/1
[Sysname-track-1]
delay
display ip interface brief (Layer 3—IP Services Command Reference)
display track
Use track interface physical to create a track entry associated with the physical state of an interface and enter track entry view, or enter the view of an existing track entry.
track track-entry-number interface interface-type interface-number physical
context-admin
To create a track entry, you must specify the tracked object type, which is interface physical in this command.
# Create track entry 1 and associate it with the physical state of GigabitEthernet 1/2/5/1.
[Sysname] track 1 interface gigabitethernet 1/2/5/1 physical
[Sysname-track-1]
Use track interface protocol to create a track entry associated with the protocol state of an interface and enter track entry view, or enter the view of an existing track entry.
track track-entry-number interface interface-type interface-number protocol { ipv4 | ipv6 }
context-admin
ipv4: Monitors the IPv4 protocol state. When the IPv4 protocol state of an interface is up, the state of the track object is Positive. When the IPv4 protocol state of an interface is down, the state of the track object is Negative. To display the IPv4 protocol state of an interface, use the display ip interface brief command.
ipv6: Monitors the IPv6 protocol state. When the IPv6 protocol state of an interface is up, the state of the track object is Positive. When the IPv6 protocol state of an interface is down, the state of the track object is Negative. To display the IPv6 protocol state of an interface, use the display ipv6 interface brief command.
To create a track entry, you must specify the tracked object type, which is interface protocol in this command.
# Create track entry 1 and associate it with the IPv4 protocol state of interface GigabitEthernet 1/2/5/1.
[Sysname] track 1 interface gigabitethernet 1/2/5/1 protocol ipv4
[Sysname-track-1]
delay
display ipv6 interface brief (Layer 3—IP Services Command Reference)
display track
Use track ip route reachability to create a track entry associated with a route entry and enter track entry view, or enter the view of an existing track entry.
track track-entry-number ip route [ vpn-instance vpn-instance-name ] ip-address { mask-length | mask } reachability
context-admin
vpn-instance vpn-instance-name: Specifies an MPLS L3VPN instance by its name, a case-sensitive string of 1 to 31 characters. If you do not specify this option, this command creates the track entry for routes on the public network.
ip-address: Specifies the IP address of the route entry associated with the track entry in dotted decimal notation.
mask-length: Specifies the mask length in the range of 0 to 32.
mask: Specifies the mask of the IP address, in dotted decimal notation.
To create a track entry, you must specify the tracked object type, which is ip route reachability in this command.
Route management does not immediately notify the Track module of the route status changes when the following conditions are met:
· An active/standby device switchover or a RIB process switchover has occurred.
· The status of the monitored route entry is changed before the routing protocol completes the graceful restart.
You can resolve the problem by configuring the nonstop routing feature.
# Create track entry 1 to monitor the status of the route entry 10.1.1.0/24.
[Sysname] track 1 ip route 10.1.1.0 24 reachability
[Sysname-track-1]
delay
display ip route (Layer 3—IP Routing Command Reference)
display track
Use track list boolean to create a Boolean tracked list and enter its view, or enter the view of an existing tracked list.
Use undo track to remove the tracked list and all configurations from its view.
track track-entry-number list boolean { and | or }
No tracked lists exist.
context-admin
track-entry-number: Specifies an ID for the tracked list in the range of 1 to 1024.
and: Calculates the tracked list state by using the Boolean AND operation.
or: Calculates the tracked list state by using the Boolean OR operation.
The state of a Boolean list is determined by the tracked object states based on the Boolean AND or Boolean OR operation.
· Boolean AND list—The tracked list is set to the Positive state only when all objects are in Positive state. If one or more objects are in Negative state, the tracked list is set to the Negative state.
· Boolean OR list—The tracked list is set to the Positive state if any object is in Positive state. If all objects are in Negative state, the tracked list is set to the Negative state.
To create a track entry, you must specify the tracked object type, which is list boolean in this command.
# Create Boolean OR list 101 and enter its view.
[Sysname-track-101]
delay
object
Use track list threshold percentage to create a percentage threshold tracked list and enter its view, or enter the view of an existing tracked list.
track track-entry-number list threshold percentage
context-admin
The state of a percentage threshold list is determined by comparing the percentage of Positive objects in the list with the percentage thresholds configured for the list.
To configure the threshold values used to determine the state of a percentage threshold list, use the threshold percentage command.
To create a track entry, you must specify the tracked object type, which is list threshold percentage in this command.
# Create percentage threshold list 101 and enter its view.
[Sysname] track 101 list threshold percentage
[Sysname-track-101]
delay
object
Use track list threshold weight to create a weight threshold tracked list and enter its view, or enter the view of an existing tracked list.
track track-entry-number list threshold weight
context-admin
The state of a weight threshold list is determined by comparing the weight of Positive objects in the list with the weight thresholds configured for the list.
To configure the threshold values used to determine the state of a weight threshold list, use the threshold weight command.
To create a track entry, you must specify the tracked object type, which is list threshold weight in this command.
To modify the settings for a track entry, execute the undo track command to remove the track entry, and then execute the track list threshold weight command again.
# Create weight threshold tracked list 101 and enter its view.
[Sysname] track 101 list threshold weight
[Sysname-track-101]
delay
object
threshold weight
Use track nqa to create a track entry associated with the reaction entry of an NQA operation and enter track entry view, or enter the view of an existing track entry.
track track-entry-number nqa entry admin-name operation-tag reaction item-number
context-admin
entry admin-name operation-tag: Specifies the NQA operation to be associated with the track entry. The admin-name argument specifies the name of the NQA operation administrator who creates the NQA operation, and is a case-insensitive string of 1 to 32 characters. The operation-tag argument specifies the NQA operation tag, and is a case-insensitive string of 1 to 32 characters.
reaction item-number: Specifies the reaction entry to be associated with the track entry. The item-number argument is the reaction entry ID in the range of 1 to 10.
To create a track entry, you must specify the tracked object type, which is nqa in this command.
# Create track entry 1 and associate it with reaction entry 3 of NQA operation admin-test.
[Sysname] track 1 nqa entry admin test reaction 3
[Sysname-track-1]
delay
display track